Clothes dryer
My clothes dryer keeps tripping the fuse. I bought a used machine and still tripping. Suggestions?
Thanks |
||
![]() |
|
?
Join Date: Apr 2002
Posts: 30,344
|
Hang 'em outside
![]() I assume you're talking breaker, not fuse.... mebbe it's bad? |
||
![]() |
|
Registered
Join Date: Jun 2000
Location: bottom left corner of the world
Posts: 22,690
|
Yeah, I'd swap the "fuse" with another fuse of the same rating. Or more to the point, the correct rating. Good luck, I'm sure it's nothing expensive.
|
||
![]() |
|
Back in the saddle again
Join Date: Oct 2001
Location: Central TX west of Houston
Posts: 55,761
|
Yep breakers do go bad and when they do one of the symptoms is tripping more than they should.
Usually not expensive at the hardware store and easy to replace. That would be my first course of business. |
||
![]() |
|
Registered
|
Sometimes a breaker needs to be replaced, other times the connections at the receptacle or breaker loosen with age and need to be secured better. Loose connections cause overheating and arcing. Hopefully your house was not built during the period when aluminum wire was used. I have had to replace quite a few outlets with loose connections, and pigtail copper on many an outlet that had aluminum.
If you replace the breaker, do not go to a higher amp. The existing wire will only handle a certain load before the risk of fire.
__________________
Ed 1973.5 T |
||
![]() |
|
Registered
Join Date: Apr 2015
Posts: 1,397
|
Thanks, yes circuit breaker. I’m an accountant not an electrician.
Is 10AIC000 the same as 10KA? 10AIC000 is the existing one. Only see the 10KA at hardware store. All other numbers matching. |
||
![]() |
|
![]() |
Registered
Join Date: Apr 2015
Posts: 1,397
|
Just noticed existing one is twice as wide. I’ll try Home Depot.
|
||
![]() |
|
?
Join Date: Apr 2002
Posts: 30,344
|
I was in IT .... wait for someone who really knows... but...
My 220V dryer takes up 2 slots in the panel with a 30A breaker .... I just checked, and a quick search seems to confirm that's normal. Don't trust how a panel is labeled .... it could be wrong. |
||
![]() |
|
Brew Master
|
Quote:
For reference: 2 pole 30 amp https://www.amazon.com/Q230-30-Amp-Double-Circuit-Breaker/dp/B00002N5HJ/ref=asc_df_B00002N5HJ/?tag=hyprod-20&linkCode=df0&hvadid=194019628201&hvpos=&hvnetw=g&hvrand=8577251018249599060&hvpone=&hvptwo=&hvqmt=&hvdev=c&hvdvcmdl=&hvlocint=&hvlocphy=9015981&hvtargid=pla-313052266780&psc=1 Single pole 30 amp: https://www.amazon.com/General-Electric-GE-THQL1130-Circuit/dp/B01D5L7I1O/ref=sr_1_2?dchild=1&keywords=Single+pole+30+amp+breaker&qid=1625946878&s=hi&sr=1-2
__________________
Nick Last edited by cabmandone; 07-10-2021 at 11:55 AM.. |
||
![]() |
|
Registered
Join Date: Apr 2015
Posts: 1,397
|
Now at Home Depot. I guess the width is because it’s a double post. Both mine and the HD one say 30 amp 10xxx 120/240v-.
The difference is the xxx part. The HD one says kA. Of course no one here to ask. Thanks |
||
![]() |
|
Registered
Join Date: Jun 2000
Location: bottom left corner of the world
Posts: 22,690
|
Have you got another one of the same on the panel. that's what I meant by swapping it then test it out.
|
||
![]() |
|
Platinum Member
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 20,887
|
You need to match the brand of breaker to the panel box. 30 Amp is the rating. Not all 30 amp breakers will fit, or are rated to work in the panel.
__________________
Politics is in the eye of the beholder - Rodney Dangerfield |
||
![]() |
|
![]() |
Registered
Join Date: Feb 2011
Posts: 555
|
Clean the vent, it may be building up heat. We had that problem with a new dryer.
|
||
![]() |
|
Registered
Join Date: Apr 2015
Posts: 1,397
|
I cleaned vent. Home Depot guy told me breaker would work. I’ll try tomorrow.
Thanks guys. |
||
![]() |
|
Registered
|
You are having the same problem with two different dryers?
Check the connections in the receptacle box, where the house wires are attached. Make sure they are tight and no heat discoloration. Tighten the connections in the breaker panel. Replace the breaker with an identical one. That's all I've got.
__________________
. |
||
![]() |
|
Brew Master
|
Have you considered cussing at it? I've never found it to do much good as far as making things work better, but it sure makes me feel better!
The only box I know of that needs the "exact" breaker is the Square D QO load center. Outside of that Square D has a "cheaper" line that called the HOM that can take GE, Siemens and several other brands.
__________________
Nick |
||
![]() |
|
Registered
Join Date: Jun 2000
Location: bottom left corner of the world
Posts: 22,690
|
|||
![]() |
|
Registered
Join Date: Jan 2002
Location: west michigan
Posts: 26,388
|
If you had the older 'screw in' type of fuses....you could just use a penny.
![]()
__________________
78 SC Targa Black....gone 84 Carrera Targa White 98 Honda Prelude 22 Honda Civic SI |
||
![]() |
|