Electrical question
I have a 70 amp sub panel in my garage. I need to run two new 20 amp circuits to the upstairs. My question is, if I run conduit straight up to the ceiling what wire do I use in the walls. I realize I can’t run Romex in the conduit but I can in the walls. Maybe just run BX cable throughout? Thanks
2.6 MB 168B3A2A-1 |
Recheck the codes. I believe Romex is now permitted so long as the conduit is not in a wet location.
|
Wow, thanks. Code allows for Romex to be run in a conduit. Solves that problem!
|