RNajarian 05-03-2022 01:42 PM
I’ve got an automatic fire suppression system in my garage. It was originally installed in 2003.
The pressure reducing valve (PRV) is required to be set at 100 minimum for this system.
Everything worked well from 2003 to 2011 when I noticed the system pressure was too high. I replaced the pressure reducing valve with the same unit, a Wilkins/Zurn 600XLHR. Designed to accommodate up to 300 inlet PSI, factory set at 85 PSI (adjustable from 75-125 PSI). It is important to note this PRV has a direct acting integral by-pass design prevents buildup of excessive system pressure caused by thermal expansion, typically from a water heater.
Recently I noticed the pressure had raised to 150 PSI and suspected the PRV had failed again after 12 years of service.
I replaced the PRV with the same model as the two before. Here is where the trouble began. After I installed the new PRV I adjusted the pressure to the recommended 100 PSI. The pressure held constant until the next day when it had risen to 150 PSI. I released the pressure in the system, then turned the water back on, adjusted the pressure down to 75 PSI and within a day (late afternoon) the pressure had risen to 150 PSI again.
I removed the newly installed PRV and exchanged it for a new unit (same model.) I reinstalled it but did not adjust the pressure, leaving it at the factory setting of 85 PSI.
Overnight the pressure held at 85 PSI. However, by 2:00 pm the next day the pressure had risen to 115 PSI.
I opened the main drain for 1 minute, purging the system. Once I closed the main drain the pressure stood at the factory setting of 85 PSI.
Does anyone have any idea what is going on? It is not particularly warm now, and I have not done anything to the system other than change out the PRVs.
Could the back flow preventer be the source of the problem? It is 19 years old. (Black Arrow in photo)
The system doesn’t have an expansion tank. Is there a PSI pressure that will activate the system?
http://forums.pelicanparts.com/uploa...1651613899.jpg
Factory set at 85 PSI
http://forums.pelicanparts.com/uploa...1651613985.jpg
john70t 05-03-2022 02:34 PM
Is that CO2 or another inert gas?
Over time there may be some chemical reaction in the system which might raise pressure. Just a guess.
There used to be haylon fire extinguishers, but they've been banned afaik.
RNajarian 05-03-2022 03:09 PM
No it is a water system. Sorry I used Pressurized/depressurized implying gas.
The sprinkler heads are called “frangible bulbs.”
At 155 degrees F the bulb bursts and allows water to flow. I’m wondering if there is an internal pressure that will break the bulb and set off the system in error.
http://forums.pelicanparts.com/uploa...1651619353.jpg
VINMAN 05-03-2022 05:06 PM
Is that system plumbed right into your regular house water? City water or well? The pressure is high. Even systems on a fire pump only run on the 70-80 range
I've never seen a sprinkler head activated from over pressurization. ( not saying it never happens,...) most
Just on a side note, you should change the heads every 5 yrs or so...
David 05-03-2022 05:14 PM
Our system at work shows the max city water pressure which goes over 100psi regularly.
RNajarian 05-03-2022 06:41 PM
I am hooked up to city water, pressure from the street is 150 PSI
The inspector wouldn’t sign off on the installation until we put this sign by the PRV
FIRE SPRINKLER PRV
Do Not Adjust
Must Be 100 PSI Min
I did some research and saw this model of sprinkler head is rated at 175 PSI, so I may be OK at 150. It bothers me that this system can’t maintain the set PSI of 85. MAYBE there is air in the line and that might be affecting the pressure.
I opened the main drain again for 45 seconds, let’s see what happens in the next day.
VINMAN 05-04-2022 04:18 AM
150psi from the street??
Holy crap that's impressive! I wouldn't even have to run my pumpers! We are lucky to get 80 out of our hydrants here in NJ.
RNajarian 05-04-2022 05:05 AM
Yea. . . I’ve got several Zurn 600XL pressure reducers (300 PSI max in/ 50-75 out). The one for the fire system is a 600XLHR (300 PSI max in/ 75-125 out).
I’ve got one outside faucet running the 150 PSI, works like a pressure washer.
GH85Carrera 05-04-2022 05:19 AM
FIRE SPRINKLER PRV
Do Not Adjust
Must Be 100 PSI Min
We are at the end of a water distribution line, and the area keeps building new homes and businesses. When we first moved in we were lucky to have 40 PSI at off peak times. In the mornings when lots of people were taking showers it got really bad. Finally the city put in new water mains and wee finally have respectable pressure, but nothing close to 100 PSI.
RNajarian 05-04-2022 05:29 AM
40 PSI !!??
Looks like I have a good problem.
RNajarian 05-04-2022 06:10 AM
UPDATE:
I sent an email to the company that makes the frangible bulbs. Here was their response. . .
The gem F680 is UL listed for a maximum pressure of 175psi. Not Maintaining your designed system pressure will affect your system operating correctly.
So at 150 PSI it would appear the system likely will not inadvertently go off.
Gives me a little breathing room to figure out the 150 PSI issue.
3rd_gear_Ted 05-04-2022 08:38 AM
Originally Posted by RNajarian (Post 11683251)
UPDATE:
Check MAX pressure on your toilet valves. That is a lot of water pressure.
wilnj 05-04-2022 09:19 AM
UPDATE:
A new install is typically tested to 200psi for 2 hours or 50psi over working pressure if the working pressure is in excess of 150psi.
I would worry about the heads, I’m sure there’s a safety factor built into that 175psi max.
Have you called zurn?
EDIT: Out of curiosity, I pulled up the specs and they recommend multiple PRV where the desired reduction is 4 to 1. That’s not your requirement but they also state that you’re not to bottom out the adjustment.
I wonder if a second PRV in series wouldn’t solve your issue.
RNajarian 05-04-2022 09:28 AM
A second PRV may be it.
I’ve noticed the pressure creeps up in the afternoon. I may put in a 125 PSI pressure relief valve on the system and see if that helps keep things in a more desired range.
Option 2 is see if I can put an expansion tank in the system.
I have not called Zurn . . . yet
RNajarian 05-04-2022 09:46 AM
I looked it up . . . here is the regulation of anyone is interested
Per NFPA 25 Sec : 5.3.1.1.1.3* Sprinklers manufactured using fast-response elements that have been installed for 20 years shall be replaced or representative samples shall be tested and then retested at 10-year intervals.
Tobra 05-04-2022 12:17 PM
We got a notice from the county they were going to come in and do a safety inspection, because the pressure we are getting from the water district is not high enough to assure the fire suppression sprinkler systems work correctly. They charged me $150, and told me I could not have a deadbolt on any of exterior doors in my office.
There are no sprinklers in this building. I am not comfortable have dead bolt free doors on my office. As a matter of fact, I am almost certain that medicare requires that I have deadbolts securing where I store medical records. Pretty much no matter what I do, I am guilty of a violation
carambola 05-04-2022 02:20 PM
Just thinking out loud,
you quoted the minimum when the maximum is your concern
confused me too, maybe it takes 100 just to operable?dunno
150 from the street has me wondering, how high does that water have to push upstream of you, awesome problem to have .
should you increase the size of the feeder pipe to increase flow while increasing pressure(did i do that backwards?)
I guess Jersey did Legalize weed, have a Great Day
RNajarian 05-04-2022 02:27 PM
Minimum pressure to be effective is 100 PSI
I’ve got that no problem.
The Frangible Bulbs will activate the system at 155 degrees F. They are designed for 175 PSI max with a room for error of an additional 50 PSI
Ideally I want to keep the pressure at 125.
I’m going to experiment with a pressure relief valve set at 125 PSI.
To be honest, the system may have been operating at 150 PSI for the last 20 years. . . I may not have noticed until now.
carambola 05-04-2022 03:27 PM
and that is cool
A930Rocket 05-04-2022 03:55 PM
I take it this was installed because of building codes?
Is it still required? Can you delete and cap it off?
RNajarian 05-04-2022 04:01 PM
Yes it would be very easy to cap it off. Literally shut the valve supplying the water.
I do like the idea of a sprinkler system protecting my two 911s
Tobra 05-04-2022 05:05 PM
How much water damage would it do if that went off?
RNajarian 05-04-2022 05:47 PM
The interior is dry walled, books, pinball machines etc . . . If the sprinklers went off there would be $15,000-$20,000 in damage easy.
. . . but my 911s are in there too. Combined those are worth more than $20,000. I’m thinking a soggy garage is better than baked 911s
Grandma and the boy in a pinball tournament
http://forums.pelicanparts.com/uploa...1651714087.jpg
Grandma and her Brother playing
http://forums.pelicanparts.com/uploa...1651714782.jpg
1975 911 3.0
http://forums.pelicanparts.com/uploa...1651714940.jpg
2000 996 2S
http://forums.pelicanparts.com/uploa...1651714988.jpg
RNajarian 05-04-2022 07:27 PM
Here is a pressure timeline. . .
May 4
8:00 am : System pressure 85 PSI. PRV Pressure at factory setting 85 PSI
3:00 pm : Recorded ambient outside temperature 81.5 deg F
5:00 pm : System pressure 146 PSI
8:20 pm : System pressure 106 PSI
May 5
3:00 am : Recorded outside ambient temperature 54.5 deg F
7:00 am : System pressure 85 PSI; Recorded outside ambient temperature 56 deg F
1:00 pm : System pressure 120 PSI; Recorded outside ambient temperature 77.5 deg F
3:45 pm : System pressure 140 PSI; Recorded outside ambient temperature 79 deg F
8:00 pm : System pressure 110 PSI; Recorded outside ambient temperature 71 deg F
9:00 pm : System pressure 100 PSI; Recorded outside ambient temperature 67 deg F
May 6
8:00 am : System pressure 85 PSI; Recorded outside ambient temperature 62 degrees F
Likely the heat of the garage attic where the pipes are caused the pressure increase.
The trick will be monitor temperature on a very hot day and on a very cold day.
Maybe I need an expansion tank after all. It is likely I never noticed the wide range of temperatures all these years. It makes sense the pressure rises with the heat of the garage attic during the day. I was thinking of putting an attic fan to keep the garage cool. That would keep the pipes in the ceiling 20 degrees cooler during the heat of the day.
RNajarian 05-08-2022 08:04 PM
UPDATE:
It is pretty obvious high attic temperatures would have an effect on pressure of the fire sprinkler pipes.
Likely the system has been cycling for the past 20 years high and low pressure depending on those attic temperatures.
I installed a thermostat controlled attic fan today and placed a wireless temperature sensor inside the attic. Hopefully the fan will keep the attic cooler and prevent the high 150 PSI I was seeing on the system.
Time will tell.
http://forums.pelicanparts.com/uploa...1652069077.jpg
Por_sha911 05-09-2022 02:43 PM
"Automatic Fire Suppression"
I thought you got yourself a machine gun with a silencer. ;)