Shaun @ Tru6 10-21-2024 11:04 AM

Breaker box & breaker type help
 
New shop breaker box, what can you tell me about it?

30A breaker is too small for my compressor. Also why does the one outlined have the neutral going into the breaker? In my old building, neutral went to a buss bar.

Compressor is 7.5 hp motor so I would need a 60A.

Hoping to prevent a service call tomorrow.

http://forums.pelicanparts.com/uploa...1729537181.jpg


http://forums.pelicanparts.com/uploa...1729537181.jpg

masraum 10-21-2024 11:23 AM

I'll preface with "I'm not an electrician." Looks like a 3 phase breaker. If I had to guess, someone cut some corners when they wired it up. But before you do anything, wait for someone who stayed in a Holiday Inn Express last night to comment.

rockfan4 10-21-2024 11:23 AM

Well, that's a 3 phase box, so you're going to get about 208v going across a pair.

Why is there a white wire going into a breaker? Because it wasn't run by an electrician would be my answer. If you've got a regular single phase outlet on the other end of that run, you're in for a surprise when you plug something in.

masraum 10-21-2024 11:30 AM

Quote:

Originally Posted by rockfan4 (Post 12343489)
Well, that's a 3 phase box, so you're going to get about 208v going across a pair.

Why is there a white wire going into a breaker? Because it wasn't run by an electrician would be my answer. If you've got a regular single phase outlet on the other end of that run, you're in for a surprise when you plug something in.

LOL!
First thing that came to mind when I read your post.
https://www.memesmonkey.com/images/m...3bf3b524b.jpeg

The second thing that popped into my head.
http://forums.pelicanparts.com/uploa...1729539020.jpg

Shaun @ Tru6 10-21-2024 11:32 AM

Quote:

Originally Posted by rockfan4 (Post 12343489)
Well, that's a 3 phase box, so you're going to get about 208v going across a pair.

Why is there a white wire going into a breaker? Because it wasn't run by an electrician would be my answer. If you've got a regular single phase outlet on the other end of that run, you're in for a surprise when you plug something in.

The secondary box across the shop that this breaker goes to has an on/off lever, the white wire is not connected at the ON side which feeds an outlet for a single phase lift.

peppy 10-21-2024 12:34 PM

We have 3 phase square d panels like that, but there is a main disconnect in the box. We do not have neutrals on 3 phase equipment. Just 3 hots and a ground are what we have and that white wire is probably be the high leg of the 3 phase.

After looking at the panel you probably don't have a high leg, every third breaker slot would have the higher voltage.

Scott Douglas 10-21-2024 01:10 PM

The cost of a service call will soon be forgotten when you can use any plug without worry of electrocution.

Did I tell you guys the story of my cousin who was fishing in an aluminum boat on a private lake that had a bridge over it?
He reached up and touched the bridge and was electrocuted. Someone didn't wire the lights on the bridge correctly.
He was only 10 years old.
Part of the reason I don't mess with electrical stuff like this. It can and will kill ya if given the chance.

908/930 10-21-2024 01:22 PM

Will start with I'm not an electrician. But thinking somebody possibly ran out of #12 blue wire or they needed 3 phase power where that ends up and just reused the white. Pretty dangerous if somebody assumes that white is a neutral wire at the other end. At least put blue tape on it to identify it.

60A for 7.5hp? Sounds high, is that motor single phase?

greglepore 10-21-2024 02:04 PM

Quote:

Originally Posted by 908/930 (Post 12343552)
Will start with I'm not an electrician. But thinking somebody possibly ran out of #12 blue wire or they needed 3 phase power where that ends up and just reused the white. Pretty dangerous if somebody assumes that white is a neutral wire at the other end. At least put blue tape on it to identify it.

60A for 7.5hp? Sounds high, is that motor single phase?

This more or less. Someone didn't have correctly colored wire for 3 phase and used standard 12/3 intended for 2 phase use. Yeah, blue tape on it, both ends.

schwarz633 10-21-2024 02:39 PM

Probably used 10/3 romex, or some type of cable for that 30A 3-phase circuit. That being the case, you have to use the white wire for one of the 3 "hot" conductors. That's allowed, but the white wire should have been marked with tape or paint on both ends.

908/930 10-21-2024 06:21 PM

If your compressor motor is single phase you have a snag, unless you have a 3 phase to single phase transformer. But a 3 phase motor would be a better choice.

Bill Douglas 10-21-2024 07:05 PM

On a more positive note (http://forums.pelicanparts.com/support/smileys/wat3.gif) three phase is good. It's expensive to get put in so great that someone else paid for it. And it all looks very tidy too.

billybek 10-21-2024 07:12 PM

Quote:

Originally Posted by 908/930 (Post 12343552)
Will start with I'm not an electrician. But thinking somebody possibly ran out of #12 blue wire or they needed 3 phase power where that ends up and just reused the white. Pretty dangerous if somebody assumes that white is a neutral wire at the other end. At least put blue tape on it to identify it.

60A for 7.5hp? Sounds high, is that motor single phase?

This. Here it would pass inspection if both ends were taped to identify it as one of three phases.
60 amps isn't all that high to handle the inrush at startup on a single phase compressor.
If three phase is available, I would change the motor to three phase if it the original were to fail.
The wire size would need to be sized to the breaker. #6 for 60 amps I think.

Pazuzu 10-21-2024 08:22 PM

Quote:

Originally Posted by peppy (Post 12343523)
We have 3 phase square d panels like that, but there is a main disconnect in the box. We do not have neutrals on 3 phase equipment. Just 3 hots and a ground are what we have and that white wire is probably be the high leg of the 3 phase.

After looking at the panel you probably don't have a high leg, every third breaker slot would have the higher voltage.

It's a basic 5 wire 3-phase box. Allows for the standard 3-phase power, plus 120V single phase by combining one of the legs with a neutral and a ground. Let's you have 120V outlets without any extra transformers. Also allows 208/3 and 120/1 and 240/1 all in the same machine without a transformer.

jyl 10-22-2024 02:37 AM

Skinny wire for 30A, isn’t it?

Shaun @ Tru6 10-22-2024 03:37 AM

So much to digest here, thank you. I'll put together a more inclusive description of details a little later on.

I can say now the compressor is 1.5 years old, an Atlas Copco screw, single phase 230V that I have a buck boost transformer for. I can ask how much a 3 phase motor is. The compressor was 5 figures so I need to keep it.

I was told this place is single phase 208V.

schwarz633 10-22-2024 05:11 AM

208V would indicate a 3 phase service. 120V between each hot leg and neutral, 208V between the hot legs. If you take a voltmeter and measure 208V from A>B, A>C, and B>C, I would say you've got 3 phase. Is this the same service that you were jacking around with the loose connection outside?

MBAtarga 10-22-2024 06:46 AM

Quote:

Originally Posted by Shaun @ Tru6 (Post 12343850)
I was told this place is single phase 208V.

Someone either lied or was confused.

70SATMan 10-22-2024 07:10 AM

Shaun, where’s the main three phase disconnect for that box? Is it a blade lever box next to or is it disconnected only by a main breaker in a main panel elsewhere? You need to know the service limit feeding your box as well.

Shaun @ Tru6 10-22-2024 07:55 AM

Quote:

Originally Posted by MBAtarga (Post 12343939)
Someone either lied or was confused.

I'm going with confused. He was very nice, I don't think any malice or trickery was intended.