ELectrician...NEC...ground wire.

Anyone have a copy of the NEC handy or know off the top of their head if the EMT can be used as the ground or does a ground wire need to be pulled to the outlet/switch.


Last edited by MotoSook; 05-14-2006 at 09:02 PM..
Old 05-14-2006, 07:34 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #1 (permalink)
Registered
 
Join Date: Apr 2005
Location: outta here
Posts: 54,243
Pull a seperate ground wire and make sure you bond the electrical box to it also.

JR
__________________
"Masculine republics give way to feminine democracies, and feminine democracies give way to tyranny." *** Aristotle
Old 05-14-2006, 08:00 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #2 (permalink)
Somewhere in the Midwest
 
MotoSook's Avatar
 
Join Date: Oct 2001
Location: In the barn!
Posts: 12,499
JR, I would like to err on the safe side and just pull a separate wire, but technically, does the NEC allow the EMT to be used as the ground?
Old 05-14-2006, 08:06 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #3 (permalink)
Somewhere in the Midwest
 
MotoSook's Avatar
 
Join Date: Oct 2001
Location: In the barn!
Posts: 12,499
Just found out..NEC allows the EMT to be used as the ground, but most shops pull a separate ground in case one of the EMT connectors comes loose.
Old 05-14-2006, 08:23 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #4 (permalink)
Registered
 
Join Date: Mar 2005
Location: Jersey Shore
Posts: 1,084
Garage
250.118(4) lists EMT as suitable for equipment grounding means

358.60 Grounding. EMT shall be permitted as an equipment grounding conductor, (EGC).

hope that helps
Old 05-14-2006, 08:49 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #5 (permalink)
Somewhere in the Midwest
 
MotoSook's Avatar
 
Join Date: Oct 2001
Location: In the barn!
Posts: 12,499
Excellent! There are a couple of circuits that I will pull a ground wire to, but the others I'll use the EMT to ground. Thanks for looking it up!

Last edited by MotoSook; 05-14-2006 at 12:33 PM..
Old 05-14-2006, 10:22 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #6 (permalink)
 
Registered
 
Join Date: Aug 2004
Location: Wisconsin
Posts: 4,362


this is a test....

Last edited by SLO-BOB; 10-22-2006 at 01:21 PM..
Old 05-14-2006, 11:16 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #7 (permalink)
Parrothead member
 
VINMAN's Avatar
 
Join Date: Jul 2003
Location: Monmouth county, NJ USA
Posts: 13,884
Do yourself a favor and pull a separate ground. While NEC allows EMT to be used as a ground, you cant always trust your conduits mechanical connections to be secure, therefore compromising the conduits grounding capabilities.
__________________
Vinny
Red '86 944, 05 Ford Super Duty Dually '02 Ram 3500 Diesel 4x4 Dually, '07Jeep Wrangler '62 Mercury Meteor '90 Harley 1200 XL
"Live your Life in such a way that the Westboro Baptist Church will want to picket your funeral."
Old 05-14-2006, 11:35 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #8 (permalink)
Registered
 
elwood-914's Avatar
 
Join Date: Sep 2001
Location: Foothills, Ca
Posts: 699
Pull a ground. Locknuts do come loose, then there goes your bond. Some jobs like hospitals have it in their specs to pull grounds with everything. I piped my home and pulled a ground though everything. Not much more labor or materials for peace of mind. Code does allow for conduit to be used as ground though.
__________________
1973 green 1.7
1973 Orange 2.0
1989 Ford F-150
Old 05-14-2006, 11:57 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #9 (permalink)
Registered
 
Join Date: Apr 2005
Location: outta here
Posts: 54,243
Suok,

Been out doing Mother's day stuff, so couldn't respond to your question. I own a construction company. I have never seen an electrical contractor fail to pull a ground wire, anywhere, on one of my jobs.

There are a lot of reasons why you should pull a seperate ground wire but if you ever have voltage leave those pretty colored wires in the pipes and take up residence in your EMT, you will not soon forget it.

There are a million ways to do something half-ass, so I can't say some people don't get cheap with the electrical wiring. Pull a seperate wire.

JR
__________________
"Masculine republics give way to feminine democracies, and feminine democracies give way to tyranny." *** Aristotle
Old 05-14-2006, 01:17 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #10 (permalink)
Registered
 
Join Date: Aug 2004
Location: Wisconsin
Posts: 4,362


this is a test....

Last edited by SLO-BOB; 10-22-2006 at 01:21 PM..
Old 05-14-2006, 02:01 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #11 (permalink)
Parrothead member
 
VINMAN's Avatar
 
Join Date: Jul 2003
Location: Monmouth county, NJ USA
Posts: 13,884
Quote:
Originally posted by SLO-BOB
I always chuckle when someone other than an electrician tells people how to do electrical work. Architects and EEs are the worst-followed closely by all other contractors.
While I agree to a point, I have seen "Master electricians" seriously botch grounding. I have over 20 yrs as an electrician and an electrical engineer. While we dont alow EMT in our plants,( all threaded conduit and couplings) we require a separate ground be pulled with all circuits. This is due to an incident where a guy was seriously injured because of a bad mechanical connection on a conduit run.
__________________
Vinny
Red '86 944, 05 Ford Super Duty Dually '02 Ram 3500 Diesel 4x4 Dually, '07Jeep Wrangler '62 Mercury Meteor '90 Harley 1200 XL
"Live your Life in such a way that the Westboro Baptist Church will want to picket your funeral."
Old 05-14-2006, 05:04 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #12 (permalink)
 
Registered
 
elwood-914's Avatar
 
Join Date: Sep 2001
Location: Foothills, Ca
Posts: 699
Quote:
Originally posted by VINMAN
While I agree to a point, I have seen "Master electricians" seriously botch grounding. I have over 20 yrs as an electrician and an electrical engineer. While we dont alow EMT in our plants,( all threaded conduit and couplings) we require a separate ground be pulled with all circuits. This is due to an incident where a guy was seriously injured because of a bad mechanical connection on a conduit run.
I don't go touting myself as a "Master Electrician" but I did serve an apprenticeship also and have been an electrician for 30 years. I too have seen bad grounding but not always by the installer. I have caught sheetrockers backing out set screws, forklift drivers damaging conduits. Diecast fittings break easily...steel ETP fittings are the best for EMT, IMO. Pull an extra wire for the ground to be safe. Do it right the first time.
__________________
1973 green 1.7
1973 Orange 2.0
1989 Ford F-150
Old 05-14-2006, 05:34 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #13 (permalink)
Registered
 
Join Date: Aug 2004
Location: Wisconsin
Posts: 4,362


this is a test....

Last edited by SLO-BOB; 10-22-2006 at 01:22 PM..
Old 05-14-2006, 05:51 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #14 (permalink)
Registered
 
Join Date: Aug 2004
Location: Wisconsin
Posts: 4,362


this is a test....

Last edited by SLO-BOB; 10-22-2006 at 01:23 PM..
Old 05-14-2006, 06:01 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #15 (permalink)
Registered
 
Join Date: Mar 2005
Location: Jersey Shore
Posts: 1,084
Garage
if you're a homeowner doing the job yourself, pull the ground.
Old 05-14-2006, 06:14 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #16 (permalink)
Registered
 
elwood-914's Avatar
 
Join Date: Sep 2001
Location: Foothills, Ca
Posts: 699
Quote:
Originally posted by carambola
if you're a homeowner doing the job yourself, pull the ground.
Exactly. That was the original question.......not who knows more....pull a ground wire.
__________________
1973 green 1.7
1973 Orange 2.0
1989 Ford F-150
Old 05-14-2006, 06:18 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #17 (permalink)
Registered
 
Join Date: Aug 2004
Location: Wisconsin
Posts: 4,362


this is a test....

Last edited by SLO-BOB; 10-22-2006 at 01:23 PM..
Old 05-14-2006, 06:40 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #18 (permalink)
Somewhere in the Midwest
 
MotoSook's Avatar
 
Join Date: Oct 2001
Location: In the barn!
Posts: 12,499
Well guys, thanks for the posts. I pulled a ground to all of the outlets and switches. #12 hot and neutral and #14 ground, easy to push throught 1/2 inch EMT in the garage (I'm wiring the detached garage I built this past winter..finally!).

We pulled #6 hot and neutral and #8 ground from the house panel to the sub panel in the garage. I have a 50 amp GFI breaker in the house panel (for 120 and 240 power in the garage).

The screwy thing is that the sub panel I bought has no ground bus. So I guess I'll have to put a ground lug in the panel to connect the #8 ground (from the house) to the #14 grounds.

I called my girlfriend's uncle who is an electrician (I forgot about him and to call him before I posted). He mentioned that NEC technically requires a ground rod for a detached building, but most inspectors let you pass if you share ground with the house.

I had an electrician help, and I learned a few things...and although we still don't have lights in the garage, I think I'm OK to finish it all myself now....what a Mother's Day! I was running around all weekend and working in the rain and mud.

I think I'll have it all wired and done tomorrow or the next day...

Last edited by MotoSook; 05-14-2006 at 07:30 PM..
Old 05-14-2006, 06:40 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #19 (permalink)
Registered
 
Join Date: Aug 2004
Location: Wisconsin
Posts: 4,362


this is a test....


Last edited by SLO-BOB; 10-22-2006 at 01:24 PM..
Old 05-14-2006, 06:44 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #20 (permalink)
Reply


 


All times are GMT -8. The time now is 03:39 AM.


 
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2025, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2025 Pelican Parts, LLC - Posts may be archived for display on the Pelican Parts Website -    DMCA Registered Agent Contact Page
 

DTO Garage Plus vBulletin Plugins by Drive Thru Online, Inc.