			Amana propane furnace, maybe 7 years old "air command 95" It was blowing cold air when I got home, so I assumed ignitor. Pulled the ignitor and it tested fine. So I double checked the tank, also fine (20%). Then I spoke with a tech and it was the over temp rollout switch and when I reset it she kicked on. He said to check the vent and I went outside it was blowing out fine. So, I get back inside and she's blowing cold again......you guessed it, the overtemp switch popped again. So I reset it and watched it trip again after 5 min. Everything looks ok, should I assume it's a bad switch and just jump it for tonight or what? Is there a diagnostic I can do on the switch? 
				__________________ Cornpoppin' Pony Soldier | ||
|  01-29-2007, 05:14 PM | 
 | 
| Registered | 
			Id be on my way to Meijer's to pick up a couple of space heaters cause its going to be a long night...
		 | ||
|  01-29-2007, 05:30 PM | 
 | 
| Bandwidth AbUser Join Date: Nov 2001 Location: SoCal 
					Posts: 29,522
				 | 
			It's B2's fault.    
				__________________ Jim R. | ||
|  01-29-2007, 06:07 PM | 
 | 
| Registered Join Date: May 2002 Location: St Louis 
					Posts: 4,211
				 | 
			I take it there is a fan and it is running? edit; the fan that blows air across the heat exchanger | ||
|  01-29-2007, 06:12 PM | 
 | 
| Dept store Quartermaster Join Date: Jul 2001 Location: I'm right here Tati 
					Posts: 19,858
				 | 
			I'm pretty sure I have a cracked/rusted heat exchanger.........again.  I bypassed the exchanger for now and am debating if I should do that for the night (carbon monoxide and all).  I have to CO alarms in the living area....but.
		 
				__________________ Cornpoppin' Pony Soldier | ||
|  01-29-2007, 06:12 PM | 
 | 
| Bandwidth AbUser Join Date: Nov 2001 Location: SoCal 
					Posts: 29,522
				 | 
			It sounds like the switch is bad.  I'm not sure about the diagnostics since I'm not sure what part of the furnace the overtemp switch is monitoring.  If it's the heated air coming out of the blower, maybe use an oven thermometer to measure air temp while measuring the voltage drop across the switch contacts (in circuit), or the resistance across the switch with the wires disconnect and jumped together.  I would consider jumping overnight it if I was absolutely convinced the thermostat was functioning properly and the outlet air temperature wasn't unreasonably hot.  If you do jump it, watch it for a while to gain some confidence that the thermostat is doing its job.  Then replace the overtemperature switch tomorrow. Disclaimer: Without actually seeing the furnace manual and schematics, I'm winging it and my advice may be sketchy. Still, I hope it (safely) helps you out. 
				__________________ Jim R. | ||
|  01-29-2007, 06:19 PM | 
 | 
|   | 
| Registered Join Date: Nov 2003 Location: Winchester, Va 
					Posts: 666
				 | 
			That sucks Len. I'd be looking into this asap AN INDUSTRY-LEADING WARRANTY ASSURES YOUR ULTIMATE COMFORT. With a warranty unsurpassed in the industry, the Air Command 95 IIQ has a limited lifetime furnace replacement warranty which states that if, for any reason, the heat exchanger or recuperative coil should fail, Amana will provide, to the original owner, a new furnace! With this exclusive warranty and a limited 5 year warrant on parts, the Air Command 95 IIQ offers unbeatable assurance and value which will keep you comfortable for years to come. For added security, consider Amana Asure protection. It extends your coverage for up to ten years, and offers additional protection. It's this kind of commitment to our customers and quality that makes the Amana-built Air Command 95 IIQ an outstanding value for your home heating needs. Savings and dependability you can trust, from the company that stands behind it. 
				__________________ Tim 82 SC 90 C2 Yasowatt | ||
|  01-29-2007, 06:20 PM | 
 | 
| Bandwidth AbUser Join Date: Nov 2001 Location: SoCal 
					Posts: 29,522
				 | 
			Oh, heat exchanger issues, too?  Any nice hotels / motels nearby? edit: Oh wait, you guys worry about freezing breaking pipes, don't you? Sheet! 
				__________________ Jim R. | ||
|  01-29-2007, 06:20 PM | 
 | 
| Dept store Quartermaster Join Date: Jul 2001 Location: I'm right here Tati 
					Posts: 19,858
				 | 
			Yea I think the IIQ is the newer version but I'll check.
		 
				__________________ Cornpoppin' Pony Soldier | ||
|  01-29-2007, 06:23 PM | 
 | 
| Dept store Quartermaster Join Date: Jul 2001 Location: I'm right here Tati 
					Posts: 19,858
				 | 
			Wife wants to take the kids to Grandmas, hmmmmm.
		 
				__________________ Cornpoppin' Pony Soldier | ||
|  01-29-2007, 06:25 PM | 
 | 
| Unconstitutional Patriot Join Date: Apr 2000 Location: volunteer state 
					Posts: 5,620
				 | 
			Can you check the temp at the rollout switch?  Is your filter fresh?   If the temp is not 180- 200, then I think you are fine to jump it. Does the switch trigger immediately after the system lights or after a few minutes? | ||
|  01-29-2007, 06:26 PM | 
 | 
| Dept store Quartermaster Join Date: Jul 2001 Location: I'm right here Tati 
					Posts: 19,858
				 | Quote: 
 It does not trigger immediately, it takes about five minutes. 
				__________________ Cornpoppin' Pony Soldier | ||
|  01-29-2007, 06:28 PM | 
 | 
|   | 
| Unconstitutional Patriot Join Date: Apr 2000 Location: volunteer state 
					Posts: 5,620
				 | 
			I'd make absolutely certain the temps don't get above 200, before jumping the terminals.  Some temp switches trigger at lower temps, though.  Proceed with caution.
		 | ||
|  01-29-2007, 06:30 PM | 
 | 
| Dept store Quartermaster Join Date: Jul 2001 Location: I'm right here Tati 
					Posts: 19,858
				 | Quote: 
   
				__________________ Cornpoppin' Pony Soldier | ||
|  01-29-2007, 06:30 PM | 
 | 
| Bandwidth AbUser Join Date: Nov 2001 Location: SoCal 
					Posts: 29,522
				 | 
			I imagine the thermal element (resistive, bi-metalic, solder-pot, ???) within the switch has probably has failed.
		 
				__________________ Jim R. | ||
|  01-29-2007, 06:32 PM | 
 | 
| Registered Join Date: May 2002 Location: St Louis 
					Posts: 4,211
				 | Quote: 
 could be either one I'd check for airflow first. | ||
|  01-29-2007, 06:35 PM | 
 | 
| Unconstitutional Patriot Join Date: Apr 2000 Location: volunteer state 
					Posts: 5,620
				 | 
			Eck, you're no fun.   If you're going to jump it over, stay by the furnace and make sure the plenum doesn't get freaky hot. Without some rudimentary troubleshooting, I recommend you babysit the monster through the night. Better safe than sorry. jurgen | ||
|  01-29-2007, 06:37 PM | 
 | 
| Dept store Quartermaster Join Date: Jul 2001 Location: I'm right here Tati 
					Posts: 19,858
				 | 
			FWIW I have the cover off and the flames do not lap at the switch or anything like that.  When it first sarts up they do for an instant but that's it. When the blower kicks on I can't say for sure that the flame moves or not (supposedly a clue that the exchnger is cracked). 
				__________________ Cornpoppin' Pony Soldier | ||
|  01-29-2007, 06:40 PM | 
 | 
| Banned Join Date: Jul 2001 Location: los angeles, CA. 
					Posts: 41,306
				 | 
			Christ, I wish I knew more about furnaces and could help. I don't envy you guys this time of year, that cold is no joke (as much as we joke about it) and it can be seriously dangerous. I almost froze to death one time in my life and to this day it is a big fear. probably one of the reasons I live here. | ||
|  01-29-2007, 06:50 PM | 
 | 
| Unconstitutional Patriot Join Date: Apr 2000 Location: volunteer state 
					Posts: 5,620
				 | 
			At the very least, if you're gonna use the system for the night, babysit for at least 2 or 3 cycles.
		 | ||