Pelican Parts
Parts Catalog Accessories Catalog How To Articles Tech Forums
Call Pelican Parts at 888-280-7799
Shopping Cart Cart | Project List | Order Status | Help



Go Back   Pelican Parts Forums > Miscellaneous and Off Topic Forums > Off Topic Discussions


Reply
 
LinkBack Thread Tools Rate Thread
Author
Thread Post New Thread    Reply
Registered
 
don911's Avatar
 
Join Date: May 2001
Location: SoCal
Posts: 2,884
Garage
Any home electicians? AL to Copper Q?

I'm doing a kitchen remodel and am hooking up some existing 220 to a cooktop and wall oven.
I have existing 10 gage copper wire and 6 gage AL wire. My cooktop needs 40 amps and my oven 30amps. According to my wiring book, my cooktop will need 8 gage wire and oven will need 10.

My plan is to use the existing 10 gage copper and run it to the oven. Should be fine.

For the cooktop, I plan to run new 8 gage copper from the cooktop up to a junction box and mate with the existing 6 gage AL. I've seen some scary pics of heat generated from bad AL/copper connections. I plan to use the proper AL/copper lugs for the connection but am wondering about the gage change from 8 to 6.
Any thoughts on possible issues going from 8 gage copper to 6 gage AL?

Also, I would have expected the oven to have higher amps than the cooktop. Seems odd that the oven can use smaller wiring. Normal?

__________________
Don
24 Cayman GTS - GT Silver
23 Cayman GTS - Arctic Grey - Sold
97 993 Coupe - Arctic/Black - Sold
13 991 Coupe - Platinum/Black - Sold, 87 911 Coupe - Venetian Blue
Old 02-18-2008, 11:41 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #1 (permalink)
Senior Member
 
Superman's Avatar
 
Join Date: Mar 2000
Location: Lacey, WA. USA
Posts: 25,309
I'm not an electrician, don't play one on TV and didn't sleep at a Holiday Inn Express last night but I will tell you what I think I know about Al wiring. I used to work with electrical inspectors. Their concern was that over time, the Al connections would loosen. Perhaps Al expands and contracts more than copper. At any rate, over the many years, the connections would become less tight, resulting in resistance, resulting in heat. Aside from that problem, I'm not sure Al is that bad. But.....loosening connections is plenty enough of a problem. I got the impression that if someone went in there every decade or so and retighened the connections, Al would be fine. But who wants to do that?
__________________
Man of Carbon Fiber (stronger than steel)

Mocha 1978 911SC. "Coco"
Old 02-18-2008, 12:10 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #2 (permalink)
Registered
 
don911's Avatar
 
Join Date: May 2001
Location: SoCal
Posts: 2,884
Garage
Yes, as far as I know, loose connections are the problem. I believe that's the problem if you put the wires together with those twist cap connectors. Over time, they can loosen up. There are AL to copper lugs that solve that issue. The lug hard fastens each wire separately.
__________________
Don
24 Cayman GTS - GT Silver
23 Cayman GTS - Arctic Grey - Sold
97 993 Coupe - Arctic/Black - Sold
13 991 Coupe - Platinum/Black - Sold, 87 911 Coupe - Venetian Blue
Old 02-18-2008, 12:16 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #3 (permalink)
Registered
Accepted connector: \





Here's another accepted connector: http://www.alcopstore.com/

__________________
Warren & Ron, may you rest in Peace.
Old 02-18-2008, 12:21 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #4 (permalink)
Parrothead member
 
VINMAN's Avatar
 
Join Date: Jul 2003
Location: Monmouth county, NJ USA
Posts: 13,853
25 yrs in the electrical field...
If it as all possible, I would replace the AL wiring. The 6ga AL and the 8 copper have the roughly the same ampacity, but you still have the expansion issue.
I went through my house and tore out all the old Al wiring. Almost every connection had an issue.
__________________
Vinny
Red '86 944, 05 Ford Super Duty Dually '02 Ram 3500 Diesel 4x4 Dually, '07Jeep Wrangler '62 Mercury Meteor '90 Harley 1200 XL
"Live your Life in such a way that the Westboro Baptist Church will want to picket your funeral."

Last edited by VINMAN; 02-18-2008 at 01:36 PM..
Old 02-18-2008, 12:43 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #5 (permalink)
Registered
 
Danny_Ocean's Avatar
 
Join Date: Aug 2006
Location: SoFLA
Posts: 5,536
1) Replace the AL wiring, sleep better at night.

2) Stepping-up a wire gauge is better than installing the minimum requirment.

3) An oven typically has two large, slow-heating elements (usually only one of which is used at a time (broil vs. bake). Cooktop has 4 (or more) rapid-heating elements, which could all potentially be in use simultaneously. I would suspect a cooktop draws more amps than an oven.
Old 02-18-2008, 01:13 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #6 (permalink)
 
Back in the saddle again
 
masraum's Avatar
 
Join Date: Oct 2001
Location: Central TX west of Houston
Posts: 56,335
Also, if you are really determined to use the Al wire, use lots of "no alox" I think it's called. It's a special goop that you put on the connection to reduce oxidation build up which is the big problem. I've got Al wiring in my house. I hate it. When we moved in every wall socket in the place was replaced with the correct co/alr recepticles. Even with that, I occasionally get one that stops working. I take it apart, clean the wires and put it back together tightly. I've seen sparks come out of a socket that has oxidized over time. It's exciting to say the least.
__________________
Steve
'08 Boxster RS60 Spyder #0099/1960
- never named a car before, but this is Charlotte.
'88 targa SOLD 2004 - gone but not forgotten
Old 02-18-2008, 01:17 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #7 (permalink)
Slumlord
 
Porsche_monkey's Avatar
 
Join Date: May 2001
Location: Canada
Posts: 4,983
I would dump the aluminum if possible. My entire house is wired with aluminum from the 70's. No issues, but I have treated every joint with no-alox.

If you keep the aluminum use no-alox and be sure not to knick the wire, they tend to crack and break off when this happens.
Old 02-18-2008, 03:33 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #8 (permalink)
Registered
 
don911's Avatar
 
Join Date: May 2001
Location: SoCal
Posts: 2,884
Garage
Thanks for the replys. I'd like to dump the AL wire but it would be quite a bit more work. I'm not sure why they used it for the one 220. Maybe it was added as an after thought.
I could run new wire under the house to the c/b panel. Might be the safer way to go.
__________________
Don
24 Cayman GTS - GT Silver
23 Cayman GTS - Arctic Grey - Sold
97 993 Coupe - Arctic/Black - Sold
13 991 Coupe - Platinum/Black - Sold, 87 911 Coupe - Venetian Blue
Old 02-18-2008, 04:58 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #9 (permalink)
Slackerous Maximus
 
HardDrive's Avatar
 
Join Date: Apr 2005
Location: Columbus, OH
Posts: 18,206
If you have access to the crawl space under the house, then I would do a fresh run.

Count your blessing friend. I have a mix of knob/tube + 60 years of someones drunk brother in law making 'updates' to my wiring. I've been here 5 years doing renovations, and come across stuff all the time that makes me say, "ARE YOU KIDDING?!?!?"

The electric heater that heats our tile floor in the master bathroom? It shares a ciruit....with the freaking garbage disposal in the kitchen! Sometimes I feel like tracking down the previous owners....and hurting them.
__________________
2022 Royal Enfield Interceptor.
2012 Harley Davidson Road King
2014 Triumph Bonneville T100.
2014 Cayman S, PDK.
Mercedes E350 family truckster.
Old 02-18-2008, 11:09 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #10 (permalink)
Registered
Quote:
Originally Posted by don911 View Post
I'm not sure why they used it for the one 220.
Aluminum is still used quite a bit in commercial settings. IIRC, the new home of the NJ Devils used it for all it's electrical infrastructure, which carries much more than 220v. Seems that aluminum is simply not conducive to residential type applications.
__________________
Warren & Ron, may you rest in Peace.
Old 02-19-2008, 06:19 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #11 (permalink)
Slumlord
 
Porsche_monkey's Avatar
 
Join Date: May 2001
Location: Canada
Posts: 4,983
I think aluminum is fine now. When it was first used there were quality issues and the wire was brittle. My home has zero problems, but my brother had a house that was slightly older, and I was over there once a month fixing outlets.

And aluminum may be good enough for the New Jersey Devils, but am sure that the mighty Toronto Maple Leafs are 100% copper. Okay maybe 75% sure.
Old 02-19-2008, 06:24 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #12 (permalink)
Registered
FWIU the arena save mucho bucks by switching the spec from copper to aluminum. Hasn't hurt their game either
__________________
Warren & Ron, may you rest in Peace.
Old 02-19-2008, 06:29 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #13 (permalink)
Evolved
 
Mo_Gearhead's Avatar
 
Join Date: Jan 2007
Posts: 3,338
If I were splicing AL to CU I would ALWAYS use a suitable 'crimp' connector.
Heat/expansion cycles are different in the two metals and bolted/screw connections can loosen/fail over time.
JMO

__________________
Don't fear the reaper.
Old 02-19-2008, 07:02 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #14 (permalink)
Reply


 


All times are GMT -8. The time now is 07:10 PM.


 
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2025, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2025 Pelican Parts, LLC - Posts may be archived for display on the Pelican Parts Website -    DMCA Registered Agent Contact Page
 

DTO Garage Plus vBulletin Plugins by Drive Thru Online, Inc.