Outdoor electrical ? - UF Romex in conduit?

Quick question for the Pelican electricians here. Is it ok to run 12/2 UF Romex in pvc conduit for a short length, say 5-6 feet, above grade, outdoors? I think I'm ok with UF? If so is 1/2" ok or do I need 3/4 conduit? I'm hooking up a radiant heater (240v/12.5amp) outside on our deck...

While were at it, can I staple the romex to the bottom of the joists in my basement (finished, drop ceiling) or do I need to drill through each one? For the record, the PO has romex all over the ceiling, just laying on the tiles...

Thanks!

__________________
1957 Speedster, 1965 356SC, 1965 356SC Outlaw, 1972 911T, 1998 993 C2S, 2018 Targa 4 GTS, 2014 Cayenne S, 2016 Boxster Spyder, 2019 Tacoma
Old 12-30-2008, 07:29 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #1 (permalink)
Registered
 
Join Date: Aug 2007
Location: SE Wisconsin
Posts: 730
Garage
You should be able to just staple the wire up with out issue. 1/2" should be fine if the wire fits and as for the PVC being exposed; that you should check local code but in my mind I would use metal as it will give you more protection against damage (code here states if the wire is under ground no pipe is needed until it pops out). While PVC is sturdy it's still plastic and gets brittle in the cold.
__________________
Rick
93 968 (My summer car),
05 Cayenne S (My winter car),
79 924 (Wife's summer car), 02 C230k (Wife's winter car),
Old 12-30-2008, 08:06 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #2 (permalink)
Registered abUser
 
TerryH's Avatar
 
Join Date: Jan 2004
Location: Whittier, CA
Posts: 3,470
Garage
I'm not a contractor, maybe Milt will intercede. I think bare Romex needs to be strung through the floor joists not lay exposed on top/bottom.
__________________
'81 911SC Coupe SOLD
Old 12-30-2008, 09:49 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #3 (permalink)
Parrothead member
 
VINMAN's Avatar
 
Join Date: Jul 2003
Location: Monmouth county, NJ USA
Posts: 13,846
Romex needs to be strung through the joist. Holes have to be at least 1 1/4 inch from the edge of the stud or joist.
__________________
Vinny
Red '86 944, 05 Ford Super Duty Dually '02 Ram 3500 Diesel 4x4 Dually, '07Jeep Wrangler '62 Mercury Meteor '90 Harley 1200 XL
"Live your Life in such a way that the Westboro Baptist Church will want to picket your funeral."
Old 12-30-2008, 10:01 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #4 (permalink)
Registered
 
Join Date: Mar 2005
Location: Jersey Shore
Posts: 1,084
Garage
use 12/2 uf. use ¾ pvc. if breaking the pipe is a concern use sched 80 pvc. sched 40 is just fine, though. do yourself a favor and put a 90° sweep on the end(underground). as far as stapling to the joints, is there no more room left on the sill plate? if not, install a runner outside of the wire to protect it from damage.
anything else?
__________________
Chris
the more i learn, the less i know
Old 12-30-2008, 02:01 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #5 (permalink)
Registered
 
Join Date: Jun 1999
Posts: 7,172
Thanks guys. For some reason I hadn't thought of running along the sill plate, I think I can do that and be in good shape. I guess someday I should go along and fix all the other ceiling wiring that is just laying right on the grid....the PO was famous for running wire into metal boxes with no connectors, jamming way too much into a box, etc. I'm fixing things as I see them...
__________________
1957 Speedster, 1965 356SC, 1965 356SC Outlaw, 1972 911T, 1998 993 C2S, 2018 Targa 4 GTS, 2014 Cayenne S, 2016 Boxster Spyder, 2019 Tacoma
Old 12-30-2008, 02:57 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #6 (permalink)
 
Registered
 
Zeke's Avatar
 
Join Date: Jan 2002
Location: Long Beach CA, the sewer by the sea.
Posts: 37,772
If you want to get technical, plastic is not allowable above grade. Any wires in conduit don't need the Romex style sheathing, but if it's coming out of a wall as Romex, no reason to strip it. It's just bulky and fills up a conduit and doesn't pull well. In dry locations you should be able to use EMT. If it has potential to get wet, you should use Seal-Tight connections.
Old 12-30-2008, 03:22 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #7 (permalink)
Registered
 
ruf-porsche's Avatar
 
Join Date: Feb 2000
Location: no where
Posts: 4,390
Garage
Quote:
Originally Posted by Paul T View Post
Quick question for the Pelican electricians here. Is it ok to run 12/2 UF Romex in pvc conduit for a short length, say 5-6 feet, above grade, outdoors? I think I'm ok with UF? If so is 1/2" ok or do I need 3/4 conduit? I'm hooking up a radiant heater (240v/12.5amp) outside on our deck...

While were at it, can I staple the romex to the bottom of the joists in my basement (finished, drop ceiling) or do I need to drill through each one? For the record, the PO has romex all over the ceiling, just laying on the tiles...

Thanks!
Check what's required from your local building code. Everyone use a different code, some use the International Building Code, some use the B.O.C.A. code and some make up their own code such as CHICAGO. You don't want to install it and have to redo it if you have a house inspection.

Last edited by ruf-porsche; 12-30-2008 at 08:14 PM..
Old 12-30-2008, 05:02 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #8 (permalink)
Registered
 
Laneco's Avatar
 
Join Date: Jan 2005
Location: Usa
Posts: 5,573
min standard

Minimum standard in the US is NEC (National electrical codes). Local authority can make it more restrictive but not less. If you use any type of metallic conduit you will be required to bond the conduit to ground. The use of PVC is ok when not exposed to physical damage and schedule 80 is used. Stapling to the bottom of the joist will be ok as long as you have a drop ceiling. Romex must be protected from physical damage (Sheetrock, plywood, acoustical ceiling). In general romex in less then six feet is overlooked.

Steve
IBEW 659
__________________
Hello

http://forums.pelicanparts.com/off-topic-discussions/1102514-we-lost-amazing-woman-yesterday.html

Last edited by Laneco; 12-30-2008 at 05:39 PM..
Old 12-30-2008, 05:34 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #9 (permalink)
Registered
 
elwood-914's Avatar
 
Join Date: Sep 2001
Location: Foothills, Ca
Posts: 699
N.E.C. codes says no romex inside conduit. I have seen it done but you know everyone is an electrician.
__________________
1973 green 1.7
1973 Orange 2.0
1989 Ford F-150
Old 12-30-2008, 05:35 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #10 (permalink)
Registered
 
Join Date: Mar 2005
Location: Jersey Shore
Posts: 1,084
Garage
what do you want to do?
__________________
Chris
the more i learn, the less i know
Old 12-30-2008, 05:52 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #11 (permalink)
Registered
 
KarlCarrera's Avatar
 
Join Date: Feb 2007
Location: Colorado Springs, Co.
Posts: 952
Are you talking a single circuit of 120v or 120/240v? You mention 12/2, this will give you a single 120v, a neutral and a ground. If your looking for 120/240v you might consider 12/3 w/ grd.
Maybe I missed something in the original post?
.02

Karl
88 Targa
Old 12-30-2008, 06:01 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #12 (permalink)
Registered
 
ruf-porsche's Avatar
 
Join Date: Feb 2000
Location: no where
Posts: 4,390
Garage
Quote:
Originally Posted by KarlCarrera View Post
Are you talking a single circuit of 120v or 120/240v? You mention 12/2, this will give you a single 120v, a neutral and a ground. If your looking for 120/240v you might consider 12/3 w/ grd.
Maybe I missed something in the original post?
.02

Karl
88 Targa

he needs a 250v 12.5 amp circuit for an electrical radiant heater.
Old 12-30-2008, 08:16 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #13 (permalink)
Registered
 
elwood-914's Avatar
 
Join Date: Sep 2001
Location: Foothills, Ca
Posts: 699
PVC pipe can be exposed but it has to be schedule 80.

12-2 w/g would work because you don't need a neutral. You just need 2 hots and a ground.
__________________
1973 green 1.7
1973 Orange 2.0
1989 Ford F-150
Old 12-30-2008, 08:37 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #14 (permalink)
Registered
 
Join Date: Jun 1999
Posts: 7,172
Quote:
Originally Posted by ruf-porsche View Post
Check what's required from your local building code. Everyone use a different code, some use the International Building Code, some use the B.O.C.A. code and some make up their own code such as CHICAGO. You don't want to install it and have to redo it if you have a house inspection.
Good point, we recently adopted B.O.C.A standards, I will check it out.
__________________
1957 Speedster, 1965 356SC, 1965 356SC Outlaw, 1972 911T, 1998 993 C2S, 2018 Targa 4 GTS, 2014 Cayenne S, 2016 Boxster Spyder, 2019 Tacoma
Old 12-31-2008, 04:38 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #15 (permalink)
Registered
 
Join Date: Jun 1999
Posts: 7,172
Quote:
Originally Posted by milt View Post
If you want to get technical, plastic is not allowable above grade. Any wires in conduit don't need the Romex style sheathing, but if it's coming out of a wall as Romex, no reason to strip it. It's just bulky and fills up a conduit and doesn't pull well. In dry locations you should be able to use EMT. If it has potential to get wet, you should use Seal-Tight connections.
Thanks Milt, good point on the seal tight connections. It's covered, but not 100% dry so think I should do that..

__________________
1957 Speedster, 1965 356SC, 1965 356SC Outlaw, 1972 911T, 1998 993 C2S, 2018 Targa 4 GTS, 2014 Cayenne S, 2016 Boxster Spyder, 2019 Tacoma
Old 12-31-2008, 04:41 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #16 (permalink)
Reply


 


All times are GMT -8. The time now is 06:39 AM.


 
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2025, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2025 Pelican Parts, LLC - Posts may be archived for display on the Pelican Parts Website -    DMCA Registered Agent Contact Page
 

DTO Garage Plus vBulletin Plugins by Drive Thru Online, Inc.