-   -   A/C tripping breaker - Think this was the problem? (http://forums.pelicanparts.com/off-topic-discussions/563950-c-tripping-breaker-think-problem.html)
LeeH 09-12-2010 11:32 AM
Our A/C compressor started tripping the breaker a couple of days ago. I hope this crispy contactor was the problem. Think this was enough to cause the breaker to trip?
http://forums.pelicanparts.com/uploa...1284316104.jpg
http://forums.pelicanparts.com/uploa...1284316119.jpg
MBAtarga 09-12-2010 12:25 PM
that would make sense
A930Rocket 09-12-2010 12:27 PM
Yep...
Green 912 09-12-2010 02:03 PM
Might just be a symptom of the real problem. Overload will fry the contacts. Check the start (inrush) and run amps of the compressor and condenser fan also check the capacitors on the condenser fan and compressor.
MarKoBrow 09-12-2010 02:13 PM
I would immediately check the capacitor first than the condition of the compressor and the charge make sure there is no blockage that contactor looks as though the compressor is working against a high side blockage. Replace the relay and the problem will only go away temporarily
LeeH 09-12-2010 02:47 PM
A little more info... the condensor fan (15 year old original) went out a month or so ago. It and its capacitor were replaced by an independent a/c guy who checked out everything when he was here. The compressor and run capacitor were replaced about 6-7 years ago. But again, both of those checked out a few weeks ago.
rick-l 09-12-2010 05:14 PM
Is that the relay in the condenser? If so I'd start saving for a new unit.
Icemaster 09-12-2010 05:38 PM
Ditto.
Overload usually means your compressor is about to die. Drawing more amperage than the breaker can handle on startup.
What does "checked out" mean? I don't think there's a check to see how much life is left in a compressor, more just checks to see if there's refrigerant in and how much amps it's drawing when running.
Check the power leads going to the compressor itself, especially the connections. If you see evidence of the same crispiness, bite the bullet and schedule the replacement.
futuresoptions 09-12-2010 06:17 PM
One of two things... the guy that came out does not know how to do a proper PM, or the compressor is starting to pull more amps recently maybe due to internal problems as a bad bearing... I would guess the first... A new contactor is the cheapest way to go at this point.. if the new contactor goes out pretty quick you know you got other problems... +1000 on checking your LRA (Locked rotor amperage (Startup) and your FLA (Running amperage) anything 10% above name plate shows possible internal problems... be careful when checking though..... also if you are starting a unit where the inside of the house is very hot it can give you higher than normal readings as well... hope this helps...
futuresoptions 09-12-2010 06:46 PM
Oh BTW, you know when a breaker trips under load that it looses approximately 10% of its effective rating right???? So when a 30amp breaker trips under load it comes close to being a 27amp breaker and so on....
Chocaholic 09-13-2010 07:44 AM
Had a breaker throw on ours when we bought the house. Seems coils were just caked with dirt and grime, apparently causing overheating. Once completely cleaned...system worked great for the rest of the summer without issue. Just a thought and easy to try.
javadog 09-13-2010 11:02 AM
Check your line voltage, too. We have sags from the power company from time to time and I've seen voltages as low as 200, or less. Ees Not so bueno, if you have low voltage when your system is trying to start up.
Also used to see contactors burn up early in systems that were really oversized and that cycled a lot.
Then, there's the new "parts from China" problem...
JR
LeeH 09-13-2010 03:31 PM
Being AZ, it definitely cycles a lot.
I'm going to take a wait and see approach to this. I've had two friends who had older but working systems replaced recently as they were sold on the idea that they'd save money on utilities. Both regretted it later when their power bills actually went up!
LeeH 09-25-2010 04:53 PM
I've done all I can do... new contactor, breaker, capacitor, and added a hard start kit. Still tripping in the heat of the afternoon. Had the independent A/C guy back out. Pressure's good. Draw while running is good. At this point I'm guessing it's time for a compressor.
Any other suggestions before we go down that road?
futuresoptions 09-25-2010 06:56 PM
Did you check your amps/pressures during the hot part of the day?
Does this thing have a high pressure cut out that does not have a manual reset?
Could your condensor fan be shutting off intermittently?
Can you check compressor temps with infrared thermometer during running?
There may be a short in your low voltage wiring that causes the unit to bump on and off... this will cause the unit to try and start against high head pressure... weedeaters and corrosion are two factors... t-stat failing could do the same thing...
If your pressures and temps are reading good, this is what I would look at before replacing the compressor....
LeeH 09-25-2010 07:27 PM
Condensor fan & relay were just replaced. It's not cutting out. Yes, the a/c guy was out at the hottest part of the day. He was a bit baffled as the pressure was good - he said he was assuming that he was going to find it overcharged. Comressor doesn't seem to be cycling in any unusual way. The unit sits right outside our kitchen window so it's easy to keep tabs on what it's doing. The only thing we hadn't tried was to hose down the coils, which we did today. Being AZ, they were pretty dusty, but not gunked up.
futuresoptions 09-25-2010 07:34 PM
Yeah, I have seen low voltage wiring where only the insulation was holding the wire up... it will cause the compressor to cut out and then will try to immediately restart it.. (shorting out) if your unit does not have a 5min time delay outside I would install one, tstat could be on the fritz too... hard to say without being there to look and see what you have...
turbo6bar 09-26-2010 02:11 PM
Your tech needs to measure amperage. Ohm out the compressor to get insight about condition.
Until you can isolate the problem to the condensing unit, I would not replace it.
What was the techs recommendation?
The suggestion to add an on-delay relay is good. This would eliminate issues with thermostat or low voltage wiring and isolate problems to the unit.
If the compressor does require a hard start cap, then your compressor could be going. Again, check start and run amperage, compressor terminals, and ohms.
This is just fishing.
good luck,
jurgen
turbo6bar 09-26-2010 02:13 PM
BTW, if your low voltage wiring was bad and caused the contactor to step in and out, your contacts would be burnt out in short time.
LeeH 06-04-2011 09:56 PM
Sigh... here we go again. My compressor is back to popping the breaker. Had another check via the power company and they also said the draw was low. I did end up installing the hard start capacitor last year and a new breaker. Not sure where else to turn.
I'm not familiar with the delay relay. Is that easy to find/install? We're just getting started with the hot months here. I need to get this thing sorted out.
billybek 06-05-2011 07:13 AM
You may have a weak breaker.
I was reading you put on a hard start kit. Was it one of the generic kits made to fit all compressors or the factory potential relay and capacitor? (some had current relays that do the same job)
For a residential application, you could install a delay on break timer.
This timer at the end of a call for cooling will not allow the compressor to restart for a settable amount of time.
What this does for you is allow the system pressures to equalize so that you do not start up against high head and draw more amperage.
Some new programmable T'stats have this feature built in.
Edit: Go to any HVAC supplier and they will have this type of timer. Very easy to install.
Edit again: Make sure that you check all the supply wiring to make sure the connections are tight. If there are pull boxes with wire nuts inside, check those too.
LeeH 06-05-2011 09:13 AM
I put in a new breaker last year when I was working on this.
The capacitor I added was a generic sort. There is a disconnect box next to the unit outside... I even replaced the disconnect as it showed some heat damage. It's cool to the touch now when the copressor is running.
My thermostat (Honeywell Chronotherm III) does have a built in delay, but I may replace it anyway as it's original to the house - about 15 years old.
The breaker doesn't necessarily trip on start up. Sometimes it's after the compressor has been running for a minute or so.
The only time my breaker trips is late in the afternoon when it's >102 outside. At that point, the sun is hitting the compressor, the disconnect, and the breaker box. Shouldn't think that would matter - especially since this only started happening last summer.
billybek 06-05-2011 01:16 PM
It is possible that you are in for a compressor replacement, but I would double check for voltage drop along the way.
If you are not comfortable with this, don't do it.
Check voltage at the panel. To do this you need to pull the panel cover off.
Check voltage with unit off. Check voltage with the unit on. Shouldn't be too much of a drop.
Check line to line and line to ground.
Do the same at the unit. Off, it should be the same as the panel. Running, you may experience a voltage drop. Again, line to line and line to ground.
If the voltage is good, it eliminates a supply problem.
It may be the start switch is not disengaging the start capacitor and you are pulling a little better than full load amps.
It is really hard to troubleshoot when you can't put your hands on it or hear it but it seems that it is doing hard starts for some reason.
LeeH 07-21-2011 11:59 AM
The compressor finally died Tuesday night at 9pm. Ya know... it's really hot this time of year in Phoenix without AC! I was lucky to find a guy who was able to get right on the replacement. The air handler has been a real pain, but we should have cool air shortly.
It's a tight squeeze to get the old condenser units in and out, so they prefer to do it by air.
http://forums.pelicanparts.com/uploa...1311274681.jpg
billybek 07-21-2011 06:34 PM
Cool! (trade pun)
What manufacturer did you go with?
Air handler was tight to get in or difficult to adapt to the existing ductwork?
LeeH 07-23-2011 09:05 AM
New unit is a Carrier, as was the old one. The ductwork was an exact match to the old air handler, so that was easy. Getting it in place was the issue.
It's located above the master bedroom closet and the scuttle is tiny. Enlarging it wasn't an option, either. We ended up hacking a hole next to the air intake and sliding it through that way. Even so it was a very tight fit. Getting the air handler up on the shelf in the photo was downright frightening. I was sure it and the two guys lifting it were coming down more than once.
http://forums.pelicanparts.com/uploa...1311437022.jpg