Yeah, I was thinking the same thing!

__________________
Bill
1988 Carrera - 3.6 engine with ITBs, COPs, MS3X
2024 Macan S
Day job ... www.jesfab.com.au
Memories: '68 912, '72 911T, '80 911SC, '84 911, '85 930, '86 930, '87 911, '21 Macan S
Old 08-01-2012, 05:33 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #41 (permalink)
Registered
 
Join Date: Apr 2005
Location: outta here
Posts: 53,748
Quote:
Originally Posted by island911 View Post
The Q you really should be asking is; Why would any of these Home improvement stores exist? ....or; Why aren't home-improvement materials available only to licensed professionals?
Mainly because there are miilions of stupid people in this country that watch the inane home improvement shows on TV and think they can do anything to their house. After all, it looks so easy. Construction workers are really the bottom of the food chain, so how hard can it be?

Quote:
Originally Posted by DanielDudley View Post
I am also of the opinion that if you do this, you should break down and run a subpanel of at least 50 amps. If you are going to run a wire, and it is a pain, run something substantial, and never do it again.

FWIW, electricians who do this every day can frequently run a line that would be impossible for you run in less than an hour, and have subpanel hooked up and done in much less than a morning.
+1

I have a guy that works on my house electrical projects that could run this line in less time than it takes to wade through this thread.

The original poster needs to hire an electrician, in my opinion. If he can afford the lift, he can afford to wire it properly.

JR
Old 08-01-2012, 05:40 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #42 (permalink)
Registered
 
rnln's Avatar
 
Join Date: Nov 2005
Location: CA
Posts: 7,286
Alright guys. You guys scared me enough. I think I can make my decision now. I either hire someone to do a good 220v source, or get a 110v lift and just plug it in to have a good peace of mind.
Thanks.

BTW, reading someone mentioned about burning outlet. When I moved into this place, many outlets sparked. On a nice day, my dad (used to be an electrician in his young age) and I open up most of them and found that the wires connected to the outlet and switch without bending at the end and loose. And many of them were sticking in at the wrong direction (the screw turn direction). Many of them were old as the age of the house. We fixed them all, and fixed them tight and nice. Do you guys think all electricians do good job?
__________________
Fat butt 911, 1987
Old 08-03-2012, 01:15 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #43 (permalink)
Platinum Member
 
dad911's Avatar
 
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 21,128
Quote:
Originally Posted by sc_rufctr View Post
... Move to Australia
How does that help OP?

Do all garages have 220 in Australia?
Old 08-03-2012, 01:30 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #44 (permalink)
Almost Banned Once
 
sc_rufctr's Avatar
 
Join Date: Feb 2009
Location: Adelaide South Australia
Posts: 38,530
Send a message via MSN to sc_rufctr
Quote:
Originally Posted by dad911 View Post
How does that help OP?

Do all garages have 220 in Australia?
We have 240v everywhere and three phase if you need it.
__________________
- Peter
Old 08-03-2012, 02:29 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #45 (permalink)
Registered
 
Join Date: Apr 2005
Location: outta here
Posts: 53,748
Quote:
Originally Posted by rnln View Post
Do you guys think all electricians do good job?
Who said it was an electrician that put those in? Might have been a homeowner...

No electrican I've ever used would have screwed up something that simple. But then, I don't find my electricans on Craigslist, or waiting in the Home Depot parking lot...

JR
Old 08-03-2012, 04:46 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #46 (permalink)
 
Max Sluiter
 
Flieger's Avatar
 
Join Date: Mar 2006
Location: So Cal
Posts: 19,644
Garage
Quote:
Originally Posted by sc_rufctr View Post
We have 240v everywhere and three phase if you need it.
Mmmmmm... 3 phase.
__________________
1971 911S, 2.7RS spec MFI engine, suspension mods, lightened
Suspension by Rebel Racing, Serviced by TLG Auto, Brakes by PMB Performance
Old 08-03-2012, 11:56 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #47 (permalink)
Registered
 
Kraftwerk's Avatar
 
Join Date: Oct 2003
Location: Northside, Brooklyn
Posts: 2,358
The fridge should have a dedicated line! Not be shared with anything else.
Your 220 v should be dedicated as well use a#10 wire run from panel to destination.
__________________
jt
'83 SC
'96 M3
6 Bicycles

2 Sailboats
Old 08-04-2012, 08:11 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #48 (permalink)
Platinum Member
 
dad911's Avatar
 
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 21,128
Quote:
Originally Posted by sc_rufctr View Post
We have 240v everywhere and three phase if you need it.
Nice. Wish I had 3 phase available.
Old 08-04-2012, 08:15 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #49 (permalink)
Registered
 
beepbeep's Avatar
 
Join Date: Jun 2001
Location: Sweden
Posts: 5,911
I'm not electrician and live in 220V country but went trough all this fairly recently:


1. Run a separate line with separate fuse/breaker. If you want to save money, run a line yourself and pay electrician to connect it to the panel.

2. Use ground fault protection breaker. If you don't have any, get it. Ordinary fuse won't detect 30mA leak towards ground. Same current can kill you or start a fire.
__________________
Thank you for your time,
Old 08-05-2012, 12:46 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #50 (permalink)
Registered
 
Join Date: Mar 2004
Location: Los Angeles
Posts: 17,457
Have not read through all of the post. How aabout a long extension cord (correct gauge) from your 220 dryer outlet (20 amp, I assume?) to the lift? Install a plug from the motor or control and have a go at it. I know nothing about lifts, but I can't see it being a huge power draw, can it? Plus, it isn't used daily. Personally, I run the sub panel to the garage. Easy for my to say that, because I know how to do that kind of stuff.

Run a cord, no insurance and code issue to deal with.
Old 08-05-2012, 02:01 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #51 (permalink)
Registered
 
beepbeep's Avatar
 
Join Date: Jun 2001
Location: Sweden
Posts: 5,911
Can you US guys please explain this 110/220V thing to us in 220V-zone?

If I get it correctly, you have 110V 60Hz system and can get 220V for hi-power stuff trough twin 110V lines which are 180 deg out of phase, so you get 220V between them? Is this a 2-phase system?

For example, my house is fed by single 3-phase cable. Outlets are evenly spread by hooking on either of those three phases (thus delivering 220V in outlet). Selected few outlets are of 3-phase type and deliver 380V between phases. Phases themselves are 120-degrees from each other. There is also ground fault protection breaker which trips as soon as more than 30mA flows trough earth line, which shouldn't flow anything at all.
__________________
Thank you for your time,
Old 08-05-2012, 12:54 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #52 (permalink)
 
Max Sluiter
 
Flieger's Avatar
 
Join Date: Mar 2006
Location: So Cal
Posts: 19,644
Garage
Quote:
Originally Posted by beepbeep View Post
Can you US guys please explain this 110/220V thing to us in 220V-zone?

If I get it correctly, you have 110V 60Hz system and can get 220V for hi-power stuff trough twin 110V lines which are 180 deg out of phase, so you get 220V between them? Is this a 2-phase system?

For example, my house is fed by single 3-phase cable. Outlets are evenly spread by hooking on either of those three phases (thus delivering 220V in outlet). Selected few outlets are of 3-phase type and deliver 380V between phases. Phases themselves are 120-degrees from each other. There is also ground fault protection breaker which trips as soon as more than 30mA flows trough earth line, which shouldn't flow anything at all.
Yeah, that is basically it. 110 or 120 depending on who you ask. It is an rms value.

So you guys have readily available 3 phase, 380Vrms line-to-line voltage, Y connected? Nice. Makes the US look like we are in the stone age. Are you on 50 Hz?
__________________
1971 911S, 2.7RS spec MFI engine, suspension mods, lightened
Suspension by Rebel Racing, Serviced by TLG Auto, Brakes by PMB Performance
Old 08-05-2012, 01:02 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #53 (permalink)
Puny Bird
 
Mark Henry's Avatar
 
Join Date: Nov 2002
Location: Port Hope (near Toronto) On, Canada
Posts: 4,566
Quote:
Originally Posted by beepbeep View Post
Can you US guys please explain this 110/220V thing to us in 220V-zone?

If I get it correctly, you have 110V 60Hz system and can get 220V for hi-power stuff trough twin 110V lines which are 180 deg out of phase, so you get 220V between them? Is this a 2-phase system?

For example, my house is fed by single 3-phase cable. Outlets are evenly spread by hooking on either of those three phases (thus delivering 220V in outlet). Selected few outlets are of 3-phase type and deliver 380V between phases. Phases themselves are 120-degrees from each other. There is also ground fault protection breaker which trips as soon as more than 30mA flows trough earth line, which shouldn't flow anything at all.
No 220v is still single phase and is much like your outlets, it runs on two 110v (105-127v) legs. If you run a neutral with it you get 240V.
__________________
'74 Porsche 914, 3.0/6
'72 Porsche 914, 1.7, wife's summer DD
'67 Bug, 2600cc T4,'67 Bus, 2.0 T1
Not putting miles on your car is like not having sex with your girlfriend, so she'll be more desirable to her next boyfriend.
Old 08-05-2012, 09:13 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #54 (permalink)
Registered
 
DanielDudley's Avatar
 
Join Date: Jan 2007
Posts: 11,758
Quote:
Originally Posted by rnln View Post
Alright guys. You guys scared me enough. I think I can make my decision now. I either hire someone to do a good 220v source, or get a 110v lift and just plug it in to have a good peace of mind.
Thanks.

BTW, reading someone mentioned about burning outlet. When I moved into this place, many outlets sparked. On a nice day, my dad (used to be an electrician in his young age) and I open up most of them and found that the wires connected to the outlet and switch without bending at the end and loose. And many of them were sticking in at the wrong direction (the screw turn direction). Many of them were old as the age of the house. We fixed them all, and fixed them tight and nice. Do you guys think all electricians do good job?
I do most of my own wiring. I used to pay electricians, but no, they aren't all as careful as I am. I bought a book, read the book, and it is, for the most part simple stuff. I used to troubleshoot car wiring, so following a circuit is very simple for me.


Your dad was an electrician. When I was a kid, I hooked up lamps and outlets and switches for my dad. But I still bought the book. I already said it once. Most of what you need to know about electricity you can learn from a book in an hour.

If you read a book, and still don't want to snake the wire, or just feel uncomfortable, hire someone recommended by a trusted friend. Or anyone giving a strong endorsement. Any Lowes or HD will have a book. Get one with the big, simple color pictures. You know, like a comic book.
Old 08-06-2012, 02:31 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #55 (permalink)
Registered
 
beepbeep's Avatar
 
Join Date: Jun 2001
Location: Sweden
Posts: 5,911
Quote:
Originally Posted by Mark Henry View Post
No 220v is still single phase and is much like your outlets, it runs on two 110v (105-127v) legs. If you run a neutral with it you get 240V.
But how do you get 220V from two 110V legs? Are those two legs 180-degrees from each other?
__________________
Thank you for your time,
Old 08-06-2012, 11:50 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #56 (permalink)
Registered
 
Join Date: May 2002
Location: St Louis
Posts: 4,211
In the US most homes have a split phase 3 wire power system. It is a transformer with a center tap. Across both windings you get 240 across either one you get 120. The three phases (the way the power is generated) is split between neighborhoods with one phase high voltage powering these transformers on the pole.

This system dates back to Thomas Edison when he was trying to reduce distribution costs for DC lamps with carbon filaments that needed 100 volts DC. (P = V I so twice the voltage requires half the current for the same power) Westinghouse followed this design with AC.

Now the voltage level standards get complicated. This is how the system is designed.
  • nominal system voltage: what the voltage is at the transformer to the houses on that network 120 / 240
  • service voltage: what it is coming into your house. max 126/252 min 114/228
  • utilization voltage: What it is at the terminals of the equipment it is being used at. max 126/252 min 108/216

In the US if you want three phase you have to pay for the additional wires and transformer to be run to the house and suffer the industrial electrical rates provided. This gets very expensive.

Now in Sweden, I don't live there but I stayed at a Holiday Inn last night I think they have a 3 phase transformer on each pole and distribute one, two or three phases to each residence depending on the power required. It sounds like if you had a lathe with a three phase motor the hookup would be rather cheap.

Quote:
Originally Posted by beepbeep View Post
Can you US guys please explain this 110/220V thing to us in 220V-zone?

If I get it correctly, you have 110V 60Hz system and can get 220V for hi-power stuff trough twin 110V lines which are 180 deg out of phase, so you get 220V between them? Is this a 2-phase system?

For example, my house is fed by single 3-phase cable. Outlets are evenly spread by hooking on either of those three phases (thus delivering 220V in outlet). Selected few outlets are of 3-phase type and deliver 380V between phases. Phases themselves are 120-degrees from each other. There is also ground fault protection breaker which trips as soon as more than 30mA flows trough earth line, which shouldn't flow anything at all.
__________________
Rick
88 Cab
Old 08-06-2012, 11:55 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #57 (permalink)
Registered
 
beepbeep's Avatar
 
Join Date: Jun 2001
Location: Sweden
Posts: 5,911
Quote:
Originally Posted by Flieger View Post
Yeah, that is basically it. 110 or 120 depending on who you ask. It is an rms value.

So you guys have readily available 3 phase, 380Vrms line-to-line voltage, Y connected? Nice. Makes the US look like we are in the stone age. Are you on 50 Hz?
I live in Sweden, so it's usual EU standard.
Apartments/small households are usually fed by single-phase 220V (nowadays 230V) 50Hz. But houses are still fed by 3-phase cables. Few things that need lot's of power (heating, owens, my welder etc.) are connected on all three phases + neutral. But outlets are connected to only one phase (spread between all three phases to even-out the load). All outlets have phase, neutral and separate earth.

Line voltage between phase and neutral is 220V and 380V phase-to-phase. There is 120 degree gap between phases so in best case (resistive Y-load on all phases) the sum of power is constant.

Trefaseffekt

This is nice, although our outlet fuses are usually in 10A-16A range. My whole house is secured by three 25A-fuses. MY understanding is that US households have larger fuses?
__________________
Thank you for your time,
Old 08-06-2012, 12:09 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #58 (permalink)
Registered
 
Kraftwerk's Avatar
 
Join Date: Oct 2003
Location: Northside, Brooklyn
Posts: 2,358
I am happy to read this thread since I used to do a lot of electrical work.
From what I was told back in the day was that you can run something 220 v cheaper than the same type of thing at 110v. The same size, say, 10,000 btu Air conditioner will use MORE energy if it is designed for 110v than one that is built to run a 220v line. True?
Makes sense.
__________________
jt
'83 SC
'96 M3
6 Bicycles

2 Sailboats
Old 08-06-2012, 12:18 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #59 (permalink)
Registered
 
Join Date: Sep 2009
Location: North of You
Posts: 9,160
Quote:
Originally Posted by Kraftwerk View Post
I am happy to read this thread since I used to do a lot of electrical work.
From what I was told back in the day was that you can run something 220 v cheaper than the same type of thing at 110v. The same size, say, 10,000 btu Air conditioner will use MORE energy if it is designed for 110v than one that is built to run a 220v line. True?
Makes sense.
False. E=IR. You can double the voltage and cut the current in half. The power consumption is unchanged. There is no free lunch, aside from running the device on a smaller conductor at the higher voltage.

__________________
"A machine you build yourself is a vote for a different way of life. There are things you have to earn with your hands."
Old 08-06-2012, 12:27 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #60 (permalink)
Reply


 


All times are GMT -8. The time now is 05:54 AM.


 
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2025, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2025 Pelican Parts, LLC - Posts may be archived for display on the Pelican Parts Website -    DMCA Registered Agent Contact Page
 

DTO Garage Plus vBulletin Plugins by Drive Thru Online, Inc.