Pelican Parts
Parts Catalog Accessories Catalog How To Articles Tech Forums
Call Pelican Parts at 888-280-7799
Shopping Cart Cart | Project List | Order Status | Help



Go Back   Pelican Parts Forums > Miscellaneous and Off Topic Forums > Off Topic Discussions


Reply
 
LinkBack Thread Tools Rate Thread
Author
Thread Post New Thread    Reply
Student of the obvious
 
LeeH's Avatar
 
Join Date: May 2000
Location: Phoenix
Posts: 7,714
What triggers a heat pump's auxiliary heat to come on?

I've searched all over and can't seem to find the answer to a simple question. What causes my heat pump's aux heat to come on? Mine is seemingly not working. Temps here in Phoenix got in to the low 30s last night. My thermostat is set to 70, but the house is 65.

The outside unit is running, but I think the problem is that the auxiliary electric heat is just not coming on for some reason. Funny thing is that our ancient Honeywell Chronotherm III thermostat does not have an indicator for aux heat. Everything I can find online about these thermostats suggest there is a heat pump version (with LED for aux/emergency heat) and one for standard systems. Can't image we've lived in this house for 16 years with a thermostat that's not compatible with a heat pump.

Does the interior thermostat trigger aux heat or does the outside unit have its own thermostat that triggers it? I don't want to go buy a new thermostat if that's not what's causing the problem.

__________________
Lee
Old 12-15-2015, 06:36 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #1 (permalink)
Registered
 
VincentVega's Avatar
 
Join Date: Aug 2002
Location: MD
Posts: 5,733
Setting in the thermostat to initiate aux heat, usually configurable for desired temp.
Old 12-15-2015, 06:45 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #2 (permalink)
UnRegistered User
 
billybek's Avatar
 
Join Date: Dec 2007
Location: Calgary
Posts: 8,018
Garage
You have reached and exceeded the balance point for your heat pump.
That is the available heat from the pump diminishes with a drop in outdoor ambient temperature until the heat required for keeping the house comfortable is no longer available. The unit will run continuously after the balance point.
There should be a second stage on the thermostat that will bring on your auxiliary heat be it electric strip/element or nat gas or propane.
There may be other ways of doing this too depending on the unit and its age.
__________________
Bill K.
"I started out with nothin and I still got most of it left...."
83 911 SC Guards Red (now gone)
And I sold a bunch of parts I hadn't installed yet.
Old 12-15-2015, 06:47 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #3 (permalink)
Cogito Ergo Sum
 
Join Date: Jul 2007
Posts: 29,791
Garage
Brrr! 65 in the house? I wouldn't be able to function! I'm no good at diagnosing, but if you need help swapping parts, let me know!
Old 12-15-2015, 06:52 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #4 (permalink)
Student of the obvious
 
LeeH's Avatar
 
Join Date: May 2000
Location: Phoenix
Posts: 7,714
Quote:
Originally Posted by billybek View Post
You have reached and exceeded the balance point for your heat pump.
That is the available heat from the pump diminishes with a drop in outdoor ambient temperature until the heat required for keeping the house comfortable is no longer available. The unit will run continuously after the balance point.
There should be a second stage on the thermostat that will bring on your auxiliary heat be it electric strip/element or nat gas or propane.
There may be other ways of doing this too depending on the unit and its age.
The heat pump is only a couple of years old. The interior thermostat is from 1995.

What's odd to me is that the interior thermostat has no indicator for aux. heat. The documents I can dig up from Honeywell would suggest that there was a version of the Chronotherm III thermostat specifically for use with heat pumps. Mine's not that one. We've had cold weather in the past and this hasn't been an issue. What I can't remember is if we've had cold weather since the new heat pump was installed.
__________________
Lee
Old 12-15-2015, 06:59 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #5 (permalink)
Cogito Ergo Sum
 
Join Date: Jul 2007
Posts: 29,791
Garage
It was this cold last year right after christmas, if that helps...
Old 12-15-2015, 07:04 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #6 (permalink)
 
UnRegistered User
 
billybek's Avatar
 
Join Date: Dec 2007
Location: Calgary
Posts: 8,018
Garage
Was the entire system changed out at that time or just the condensing unit section?
__________________
Bill K.
"I started out with nothin and I still got most of it left...."
83 911 SC Guards Red (now gone)
And I sold a bunch of parts I hadn't installed yet.
Old 12-15-2015, 07:05 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #7 (permalink)
Student of the obvious
 
LeeH's Avatar
 
Join Date: May 2000
Location: Phoenix
Posts: 7,714
Quote:
Originally Posted by billybek View Post
Was the entire system changed out at that time or just the condensing unit section?
Both ends. Air handler is in the attic.
__________________
Lee
Old 12-15-2015, 07:08 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #8 (permalink)
Cogito Ergo Sum
 
Join Date: Jul 2007
Posts: 29,791
Garage
If you decide you need a pro, I've got a guy who is honest, and not ungodly overpriced.
Old 12-15-2015, 07:10 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #9 (permalink)
UnRegistered User
 
billybek's Avatar
 
Join Date: Dec 2007
Location: Calgary
Posts: 8,018
Garage
Ok the product nomenclature that you have given me indicates that there is no auxiliary heat installed on the air handler. Now that doesn't mean it isn't there and was added as a kit later on.
__________________
Bill K.
"I started out with nothin and I still got most of it left...."
83 911 SC Guards Red (now gone)
And I sold a bunch of parts I hadn't installed yet.
Old 12-15-2015, 07:18 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #10 (permalink)
Student of the obvious
 
LeeH's Avatar
 
Join Date: May 2000
Location: Phoenix
Posts: 7,714
Quote:
Originally Posted by porsche4life View Post
If you decide you need a pro, I've got a guy who is honest, and not ungodly overpriced.
It's probably going to come to that.

It's a Carrier that was installed in 2011. The compressor was replaced exactly one year ago under warranty. "Under warranty" is amusing as diagnostics, labor, freon aren't part of an a/c warranty so I paid $800 out of pocket.

I'd like to upgrade the thermostat, but that's another issue. As I understand it, the new thermostats require a dedicated power line. I have an unused wire, but am confused about the proper set up. The power wire is labelled "C". Well, the terminals on my thermostat have "C" as unused, but outside, "C" seems to be attached.
__________________
Lee
Old 12-15-2015, 07:19 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #11 (permalink)
UnRegistered User
 
billybek's Avatar
 
Join Date: Dec 2007
Location: Calgary
Posts: 8,018
Garage
If it is easy to access open the air handler/fan coil panel and look for the resistance heat strip. It should be quite large on the section towards the supply fan.
It could be a control issue but I would make sure that there is resistance heat there before you start chasing control problems.
It also looks like that you have a 5 ton air handler and a 3 ton condensing unit.
That is quite common in dry areas to oversize the evaporator for the A/C but it doesn't do much for the heat output.
I have an exam to run, will check back later to see how you are doing.
__________________
Bill K.
"I started out with nothin and I still got most of it left...."
83 911 SC Guards Red (now gone)
And I sold a bunch of parts I hadn't installed yet.
Old 12-15-2015, 07:41 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #12 (permalink)
Student of the obvious
 
LeeH's Avatar
 
Join Date: May 2000
Location: Phoenix
Posts: 7,714
Ok. So Bill, looks like you're correct. No aux heat installed per the guy who installed it in 2011.

He's going to come check it out shortly.
__________________
Lee
Old 12-15-2015, 08:20 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #13 (permalink)
Student of the obvious
 
LeeH's Avatar
 
Join Date: May 2000
Location: Phoenix
Posts: 7,714
Verdict is that it is low on freon due to a leak in the coil. Access to the air handler is through a scuttle that's too small for the coil so...




Really not happy with Carrier. $800 out of pocket for last year's compressor that was under warranty and now $1100 for the coil that is under warranty.
__________________
Lee
Old 12-15-2015, 01:46 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #14 (permalink)
Brew Master
 
cabmandone's Avatar
 
Join Date: Jul 2013
Location: Delphos OH
Posts: 32,094
Garage
Okay, but that doesn't explain why your secondary heat didn't kick in. Your chronotherm should have a red light that illuminates when stage 2 (emergency heat) activates. You should have a swich to go between Heat, Cool, Auto and E Heat. Set it to E heat and see if the electric resistance heat is working. I'm guessing it isn't because at 5 degrees below set point your auxiliary heat should have kicked in. I installed Carrier for several years and can do some research on the system but I'm thinking yours should have an Optimizer for dual fuel (heat pump and electric resistance) but I can't recall exactly anymore. It has been several years since I've installed a heat pump with and air handler and electric resistance heat.

Correction: I think the older chronotherm had a red light on the sub base that displayed when auxiliary heat is on. On yours it might say "aux" or "E heat" when the backup resistance heat is on. Question, did your A/C work okay throughout the summer?

From the manual for the stat
STATUS LIGHTS—Lights that show system operation
settings.
SYSTEM light (yellow)—This light glows whenever
the thermostat is calling for heating or cooling
(located on thermostat).
AUX HT light [T8631R only] (green)—This light
glows whenever the thermostat is calling for operation
of the backup heater. Backup (auxiliary) heat is
more expensive to operate than the heat pump and
typically is used only when the heat pump is unable
to handle the load (located on subbase).

Last edited by cabmandone; 12-15-2015 at 02:40 PM..
Old 12-15-2015, 02:28 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #15 (permalink)
Student of the obvious
 
LeeH's Avatar
 
Join Date: May 2000
Location: Phoenix
Posts: 7,714
There is no aux. heat installed on this unit. Seems lots of them get sold in AZ without them.
__________________
Lee
Old 12-15-2015, 07:44 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #16 (permalink)
Cogito Ergo Sum
 
Join Date: Jul 2007
Posts: 29,791
Garage
Come to think of it, I don't know that we have strip heat. I've never kicked it on if we do....
Old 12-15-2015, 07:51 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #17 (permalink)
Brew Master
 
cabmandone's Avatar
 
Join Date: Jul 2013
Location: Delphos OH
Posts: 32,094
Garage
Quote:
Originally Posted by LeeH View Post
There is no aux. heat installed on this unit. Seems lots of them get sold in AZ without them.
Seems odd to me but I suppose the climate is mild enough that a good working heat pump would be sufficient 90% or better of the time.

BTW, I suppose the system not having any backup heat would make it difficult for the system to stage it in

Also, I would ask them to show you exactly where the leak at the coil was. I have almost NEVER seen an indoor coil leak unless the coil was in a home with sulfur water. You mentioned the system was only 2 years old or so which makes me doubt the claim of a coil leak even more. My guess is, when they brazed the lines for the evaporator coil, they didn't wrap the metering device and most have a nut with a rubber O ring that will melt if you don't keep them protected while brazing.

Last edited by cabmandone; 12-16-2015 at 03:34 AM..
Old 12-16-2015, 03:28 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #18 (permalink)
 
Registered
 
Join Date: Jan 2005
Location: Dalton, Georgia
Posts: 250
Garage
Sounds like it was never properly installed, not Carrier's fault. If a good vacuum was not pulled and the lines not flushed out (if it was a replacement and still using the old refrigerant lines for the flushing part) the air left in the lines will mix with the refrigerant and form an acid. That acid will slowly eat away at the epoxy coatings on the compressor windings until it fails. It will also eat away at your coils. It will do this silently and slowly bring death to your HVAC equipment

A properly installed system, almost any brand, will last at least 10 years. The good ones, like Carrier, should go for 15-20 and sometimes well beyond. These numbers are generated for my part of the country after 20 years in the biz.

Just hope you have a good tech - it is usually the ONLY thing separating you from a good system versus a money pit.

My $0.02
__________________
I’m Porsche-less! 2010 AMG E63 - what an engine! BMW K1200R - Hang on! 1987 Porsche 928 S4 - SOLD. 1981 Porsche 928 Saved & SOLD. 1976 Porsche 911 S (V8 Race Car) - SOLD.
Yes I'm blue collar, all my white ones got dirty!
Old 12-16-2015, 04:15 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #19 (permalink)
Brew Master
 
cabmandone's Avatar
 
Join Date: Jul 2013
Location: Delphos OH
Posts: 32,094
Garage
Quote:
Originally Posted by Fischer_76_911S View Post
Sounds like it was never properly installed, not Carrier's fault. If a good vacuum was not pulled and the lines not flushed out (if it was a replacement and still using the old refrigerant lines for the flushing part) the air left in the lines will mix with the refrigerant and form an acid. That acid will slowly eat away at the epoxy coatings on the compressor windings until it fails. It will also eat away at your coils. It will do this silently and slowly bring death to your HVAC equipment

A properly installed system, almost any brand, will last at least 10 years. The good ones, like Carrier, should go for 15-20 and sometimes well beyond. These numbers are generated for my part of the country after 20 years in the biz.

Just hope you have a good tech - it is usually the ONLY thing separating you from a good system versus a money pit.

My $0.02
I've got a General heat pump. It was a generic made by Carrier with a brown outer color and a big white star on top. I installed the thing in 1996 and it's still chugging away today. I agree, this doesn't sound like Carrier is to blame here.

Old 12-16-2015, 04:49 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #20 (permalink)
Reply


 


All times are GMT -8. The time now is 09:20 AM.


 
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2025, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2025 Pelican Parts, LLC - Posts may be archived for display on the Pelican Parts Website -    DMCA Registered Agent Contact Page
 

DTO Garage Plus vBulletin Plugins by Drive Thru Online, Inc.