I’m under the house right now. Check out this terrible design!http://forums.pelicanparts.com/uploa...1609466430.jpg
|
|
Quote:
https://www.pelicanparts.com/cgi-bin/ksearch/pel_search_2016.cgi?command=DWsearch&description=t achometer |
Was thinking what dad911 is thinking, feedback from motor control module not working correctly?
Can you just lock it on low heat for now? Noticed there is a switch for emergency heat (SW-4), not sure what sensors that bypasses, looks like it skips the blower calibration and just runs blower full speed. Are those pics part of the return? Looks like they were trying to get noise levels down and the flow at the same time. |
That was my next move - lock it down on low heat if this doesn’t work. Good thinking!
So I just rehooked it up - what a pain getting it around that beam in this tiny crawl space. I kept knocking my respirator off. I’m now standing in front of it watching it run for eight minutes. That is the amount of time they say you should see error codes. When I ran it in test mode it showed me a 41 error code with the shortened pipe - different than the 44 but certainly not a 11 code. I also knocked loose a bunch of dust and dirt thru this whole process and now that stuff is getting the filter dirty really quickly. So I’ll have to see if the hardware store up here is open tomorrow (not likely). Eight minutes now running full blast without any errors! Wayne |
|
Darn it. Code 44 again. And now the heater motor is making a different noise. Sounds a little louder or so. Maybe this a motor / controller issue after all.
Wayne |
Quote:
-Wayne |
Have you tried turning it off and turning back on? :cool:
Seriously, cut power at the breaker, give it a few minutes, turn back on. Might need a reset. Worth a try. |
Quote:
Quote:
BTW, there is another member here who is really well versed in this furnace. I don't recall his name but I remember him chiming in on another thread. I'll see if I can find his username. You might be able to PM him for advice. Update: I found him and sent a PM asking if he could chime in. |
Are you sure the squirrel cage is clean? Usually just a few screws and the whole motor/blower assembly slides out.
|
For the 44 code I noticed this in the troubleshooting guide
"You have excessive restriction in air delivery system. Check filter(s) and ductwork. If problem still persists, replace furnace control board. Make sure replacement board has a date code of 9506 or later. This new furnace control board will allow unit to run in high fire when necessary. See description of operation at start of Fault Code 44. If problem still persists, use Appendix E to evaluate." From Appendix E: "If furnace is on a call for heat or cooling and duct static is too high, ICM tries to overcome external static pressure. If duct static is excessive, ICM RPM will be out of range and a Fault Code 44 will flash on circuit board" |
Phew, what a long thread. My two cents from far away.
1. Lots of good advice on here. 2. Static is a function of both return and supply. Door off reduces static, but that doesn’t mean problem was with return. 3. Advice given earlier to check evaporator coil and clean if needed. Also check if internal insulation around coil or furnace is loose. I had one Job where the insulation blew onto the coil from the side of the cabinet when running, threw a code, and then returned to its normal position at rest. 4. Check insulation around blower motor for same problem. Door on could equal insulation sucking in and blocking 50% airflow. 5. Good advice for locking down in low speed, but see above. 6. Replace motor if all else fails, especially if it is original. I’ve seen over speed situations on ECM motors, though very rare. My $0.02. Bob |
Quote:
It sure looks to me like the previous owner increased the size of the house and added supply ducts (and probably upsized the furnace) and did not increase supply air to match. If that one return is all you have, it is likely just not enough. You would need to cut a hole in the return plenum and add another return...preferably from a different floor/part of the house (if possible). I could not really see your return air plenum in the photos (assume you have one). If not, you probably need to add one. If you can access it easily, depending on design (and the area it is located), you might be able to open it fairly easily and allow more air in to test if the additional air would solve your problem. Also, I would suggest that you update the grill on your existing return to one with larger spaces between the fins. Those with such narrow slots also restrict air flow. Of course, I assume that by not you have confirmed the ductwork you were examining is not collapsed or blocked. Good luck. |
Probably worth making up an incline manometer and check what is really going on in the ducts.
|
So, I shortened the duct - I still have the problem, although it seems "less" now. I think that there may be two problems - a poorly designed intake system, *and* a motor that may be getting old. When I shortened the intake, I rant the unit for a while with it disconnected - still gave the error code. Also did it when I removed the filter. Maybe there's a blockage on the pressure side, although it shouldn't work then when I open the blower compartment and bypass the intake.
I wish these machines had better error diagnosis codes... -Wayne |
Your duct system is a mess. My guess is that supply and return are sized wrong. This is why the code existed several years ago and why it likely never went away. I'd bet the system never worked properly but on low fire it was simply out of sight out of mind.
|
Prior to shooting darts at what needs to be replaced, should confirm what static pressure the fan is seeing, page 36 of the manual that fintstone provided. there is a possibility the furnace is working properly and the ducts are undersize. Pick up a 0-3" wc, water incline manometer.
Cabmando did ask this but what size unit is this? |
We've left the house. I've got an HVAC guy coming to look at it on Thursday. It's a house in the mountains, so my tools and equipment are not the same that I have here in Los Angeles. I basically have a large carry-around toolbox with some hardware-store Stanley tools. I do have a manometer here at home (used for diagnosing my pool heater problem - that's another story - six visits from the "techs" couldn't fix it - I had to do it myself), but I didn't have that there.
The fact that the heater still gave an error code with the intake disconnected from the convoluted intake duct, leads me to believe that either the motor is getting a bit old, or indeed, perhaps the system wasn't setup property from day one. |
Quote: