-   -   Air Conditioning Question... (http://forums.pelicanparts.com/showthread.php?t=480870)
red-beard 06-18-2009 09:37 PM
The advantage of recycling the air is that you will remove the moisture in the air, dehumidifying as well as cooling. Constantly running "new" air will add moisture to the system, and if humid enough, may lead to freeze up of the coils.
You're pretty close to the water there (what? 2 miles?) so you may be getting more moisture than you think. A cheap bulk polymer humidity sensor would tell you for sure.
His hot air thing sounds like hot air to me. Cost shouldn't be any different. You are cooling office air, and running that into the shop. So you are pulling fresh air into the offices. I think with the recycle, you'll be more efficient, lower cost.
Cooling air is 1/3 the cost of removing moisture. The heat of vapoization of water is high! Look of the low pressure charts on the steam tables.
Eric Coffey 06-18-2009 09:40 PM
Certainly no expert, but I think a closed-loop system would be more efficient. Also, aren't most A/C systems designed to function best with certain warm/cold "split" temps? Maybe he's saying instead of having an exhause fan, that it should be a (filtered) air-return? I'd certainly get a second opinion.
Heel n Toe 06-18-2009 09:50 PM
Wayne, as you know, everything about the way these systems are set up with where the returns and the vents are and how big they are is critical to operating efficiency and performance.
Would it be possible to get a second opinion from another company, or are you on contract with this guy? Or would he be offended?
A second set of eyes might be your answer.
And if you think your guy might be offended if he knew you got another guy to look at it, just request that #2 guy come by after hours in an unmarked vehicle/his own car and do a walk through.
chapo 06-18-2009 10:00 PM
The only way it will freeze up is if it runs all the time, or for very long times. Compressors freeze up all the time in Lake Havasu at 110 degrees because they always run.
rick-l 06-18-2009 10:35 PM
So your AC guy is saying that continuously cooling the dry, 65 degree air allows the evaporator to drop below freezing?
Heel n Toe 06-18-2009 10:40 PM
Originally Posted by Wayne at Pelican Parts (Post 4730836)
It picks up the supply air on the other side of the building, cools it, and then deposits it into the server room. Then, the warm air is sucked out of the room using a ceiling exhaust fan. This air goes into the warehouse.
Originally Posted by Wayne at Pelican Parts (Post 4730890)
If the air in the warehouse (where the A/C unit is sucking in air) is very cool (say 60 degrees or so)
In the first paragraph above, you seem to be saying that the warm air in the server room is sent to the warehouse...
...then you seem to be saying that the return for the server room's A/C is also in the warehouse... but after having read everything you've said, it's from a cool area in the warehouse. The same warehouse, right?
At any rate, this is definitely beyond my abilities, but I know you need for the system to cause the humidity in that server room to be as low as possible... or perhaps within certain limits.
So, I recommend the second opinion approach. You're gonna want someone who is not only knowledgeable, but who doesn't mind answering all your questions. Get a recommendation from another businessman you know in the area who has a similar setup... at least an office area and a warehouse area in the same building... sounds like that's what you have.
fintstone 06-18-2009 10:50 PM
They will freeze up when they run constantly and if/when there is insufficient air flow based on the size of inlet or outlet (including a fouled or too restrictive filter). The really thick or dense filters will almost aways cause this...and changing to a less efficient one will often be enough to fix the problem.
Eric Coffey 06-18-2009 10:58 PM
Originally Posted by Wayne at Pelican Parts (Post 4730893)
I think that would be the case if there wasn't significant heat generation going on. I think that's what he thinks too, but the role of the servers (there are about 18 computers in there) change the whole equation. In his recommendation, I'd be pulling out 80-degree air. In my setup, we're pulling air that is about 65 degrees.
-Wayne
Yeah, I'm thinking closed-loop as in: the air in the room IS the air you are pulling back in and re-cooling (just have a filter somewhere in the loop). Just like the forced-air (closed-loop) system you would have in your house.
porsche4life 06-18-2009 11:35 PM
I would think the closed loop would be cleaner. Even with a good filter some dust could be getting by. Isn't dust the enemy for computers ?
island911 06-19-2009 12:05 AM
Originally Posted by fintstone (Post 4730960)
They will freeze up when they run constantly and if/when there is insufficient air flow based on the size of inlet or outlet (including a fouled or too restrictive filter). The really thick or dense filters will almost always cause this...and changing to a less efficient one will often be enough to fix the problem.
Yeah, I was going to suggest an array o' cool collar, but I suppose a K&N filter ought to do just as well. :cool:
Seriously, I've got to agree with finstone; increasing the airflow will transfer more heat to the coils. (stop the freeze)
island911 06-19-2009 12:17 AM
I'll just add that your guy is right, that feeding the cold side warmer air will help stop the freezing, but you are certainly right that there is a more efficient solution.
Hugh R 06-19-2009 12:25 AM
Wayne, certainly no expert here, but if your pulling already cooled air in, you compressor works less. Icing up is on the evaporator occurs from a less than 32 degree temp at the evaporator. Cooler air has less moisture than warm air. So less moisture from cooled air = less icing. One of the ways A/C works best is to recirculate already cooled air. The question is "Is the air from the server room warmer than the air outside?" Given where you are located, you should have a "smart" system that will pull makeup air from the coolest place. Winter outdoors, summer maybe from the server room.
island911 06-19-2009 12:46 AM
Originally Posted by Hugh R (Post 4731025)
. So less moisture from cooled air = less icing. ...
That part isn't quite right. (tho it may seem intuitive)
When air has more moisture it carries more heat-energy, and will take more energy to freeze. (Latent heat and all) Think of it this way; let's say there is ice already on the coils ... what will break the ice faster, room-temp super dry air, or room temp garden hose water?
So, with wet air, condensation may build faster but all that moisture imparts a lot of heat to the cold coils. That is, wet air will take longer to freeze than drier air. (...for a given air flow you'll have more mass flow & latent heat with additional water in the mix)
turbo6bar 06-19-2009 04:42 AM
Based on your last post describing a system that has worked well for several years, I'd say you may have an undercharged system or dirty evaporator coil reducing airflow. What type of filtration are you using? Are the filters changed regularly?
jurgen
javadog 06-19-2009 05:46 AM
I can't diagnose this system from across the country but I agree with turbo6bar, in that your current problem is most likely not due to the design.
However, depending upon where your thermostat is located, and given a higher than normal supply air temperature, it might be possible that the compressor may run a long time. I'd suggest having a mechanical engineer (as opposed to a contractor) take a look at how your system is installed, to see if there might be a better way to do it. I have installed a bunch of systems in server rooms and telephone switches and we never use outside air, primarily as we are also needing to control the humidity within a narrrow range.
JR
Radioactive 06-19-2009 06:02 AM
In my experience freezing up is caused by not enough air flow (ie:dirty filter, not enough incoming air flow) if it used to work, that is my guess. The air in and out to the warehouse I don't think it maters on the freezing . It is probably more efficient to run closed loop because you are trying to cool the already pre or cooled air, it would take less energy to cool the already cooled air plus you get the benefit of removing the humidity and not introducing more moisture.
dhoward 06-19-2009 08:13 AM
If it worked for several years before. It's not a design issue.
That's the lazy way out.
Low airflow or undercharge.
pete3799 06-19-2009 08:42 AM
No expert here but seems like your compresor would run less if you recuirculate the air inside the room (draw already cooled air) than drawing outside air.
turbo6bar 06-19-2009 09:37 AM
That would depend on the sensible and, to some extent, latent head loads. Without knowing the conditions of the server room AND warehouse space, it's pure wild-ass guessing. You could be entirely correct, though.
T77911S 06-19-2009 10:11 AM
if you are pulling air from another room, you are putting a vacuum on that room, i bet the doors dont need closers. so, you are putting a load on that system. it is trying to draw air into it, and it is providing air to another room.
the server room. this unit is icing because it has cool air going into the evap. the system is deigned to remove heat from the air, so if air going into the system is ALREADY cool, there is effectively no heat load on that system even though the room is getting warm. with the unit running and no heat load, it will/may ice up.
you may connsider just running another supply and return from where you are getting the cold air now to cool the server room and use the server unit as a backup. set the T stat to auto and about 5 degrees higher than what you want and as needed, itwill come on.
i dont know what type your big system is, but you could even put a damper controlled by a Tstat in the server room to keep it cool. keeping the server ac sys off would save the system and money.
Kaliv 06-19-2009 10:24 AM
It would seem that your setup is fine...your problem seems to lie with A/C technicians that work like doctors. They aren't sure what the problem is so the take a guess and fix one thing at a time until something works without really knowing what's causing the problem...being out there for the 3rd time when you haven't had issues in 5 years.
I've worked in server rooms for quite a few years, but I can't say that I've ever inquired about how the A/C system works. But I do know when working in the server room, it alway seemed windy. The main issue isn't really cooling the air, it's the transfer of air. Just as inside the computers themselves...they don't run cool air over the heat sinks, they just run plain air to move the hot air away. Ambient air will always be cooler than what the systems are generating. So you mainly just need a flow going to push the hot air out. Adding in cold air is just a bonus for extra cooling.
Case in point, I was working in a server room once when the fan to the A/C unit broke. We went from 68 degree to about 100 degrees in less than an hour. By the time we got a bunch of huge fans in the area to circulate the air, the temperature dropped to low 90s, high 80s...and that was without cooling and our crappy quick fix circulation.
Guess the point here is...seems like you have a working layout solution. Just keep the air circulation going.
Netspeed 06-19-2009 11:16 AM
Here's my take on the situation: There's gotta be a Pelicanite nearby in the HVAC biz that wouldn't mind taking a look and maybe trying a fix. It could be worth a nice swap...labor vs. Porsche parts! ;)
futuresoptions 06-19-2009 02:23 PM
Wayne, having 10yrs experience working on computer room a/c units (Phone company:)) I can tell you this. Cleanliness needs to be paramount... also redundancy needs to be built in to your system... What I mean is, you need a lead and a lag unit.... These units will change lead/lag weekly to insure equal run time on the compressors... also, The lead unit only cools, and the lag unit needs to have it's fan running continuously... what this does, is continually circulate air, but also prevents the lead unit from running after cooling has stopped, and redepositing the moisture that it has collected back into the air... If, you are utilizing cool dry air as return air, you run the risk of dropping your humidity too low, to the point that static electricity becomes an issue, and electronics can be knocked out due to these situations... also, if your main unit goes out, you have a back up... as far as the freezing up situation, it is possible that the evaporator is freezing up due to the cold air for one simple reason, usually you have a 10-20 degree split between supply air and discharge air... that being said, if your supply air is 60 degrees and you have a 20 degree split, that means your discharge air would be approximately 40 degrees, which would mean that you coil temperature has dropped below freezing... you may remedy the situation by overcharging it, but run the risk of damaging the valves in the compressor... If I were your a/c guy I would recommend only cooling the air in the room that needs to be conditioned... I would not import or export it... Computer rooms are considered critical for a reason and are generally taken better care of / more expense applied to than personnel occupied spaces....
futuresoptions 06-19-2009 02:26 PM
All he needs to do is send me a plane ticket and I would be more than willing to look at it for him....:D
javadog 06-19-2009 02:47 PM
I'd need a plane ticket, a nice hotel room and a big juicy steak..
JR
SherpaDog 06-19-2009 03:51 PM
Wayne,
What is the make and model of your server room unit? Thanks.
red-beard 06-19-2009 04:09 PM
JR
He might get you some fuel from the refinery across the street.
I guess El Segundo is a bit different than 10 years ago...
Zeke 06-19-2009 06:42 PM
The A/C guy is probably thinking of the balance of make up air, nothing too much more serious than that. A closed loop system keeps the intake and supply relatively balanced introducing a small amount of outside air, which is user adjustable on window units. Larger units are fairly well engineered with respect to exchange rates and make up air.
Wayne, your exhaust fan can't be more CFM than the A/C unit is pulling in or you will be pulling in dirty, unconditioned air. The A/C guy doesn't know what you have exactly, so he is playing it safe. You want a lightly positive system, certainly not negative.
billybek 06-19-2009 08:33 PM
Something has changed. If your tech has been servicing the unit for a while he should be able to pick that up.
+ 3 or 4 to airflow then charge. It is possible that the TX valve if equipped has lost pressure in its element simulating a full closed valve. Eventually this will cause a full freeze on the coil, but it takes a long time to do it. If charge is good and airflow is unchanged, look to the metering device. They can wear and develop glitches and allow full flood and coil starvation.
Has the system been topped up lately? Correct Refrigerant? Oil compatibility?