It probably ends up being closer to 24 feet now that I've measured everything.
Something like this?
https://www.menards.com/main/electrical/circuit-protection-distribution/main-lugs/square-d-trade-homeline-trade-100-amp-6-space-12-circuit-indoor-main-lug-load-center/hom612l100s/p-1444444042902-c-6438.htm
I can use a 50 amp breaker and 6 gauge wire to supply it?
I like that, but that puppy is 100 amp sub panel. You have a 200 amp main panel? If so, you must up your wire size going to the sub panel. #3 is required for 100 A