we have a small chiller system here at work. I have been to HVAC school but not chiller. its a YORK condenser system.
it has not been keeping up, oh its only a few years old. my question is about water flow. the controls are set to run the pumps at 40% "minimum" and that is where they stay no matter the heat load. Q: should the water flow increase with heat load? I had upped the one pump from 40% to 50% about 2 weeks ago and there did not seem to be an issue. then yesterday the tower cab (I work for the FAA) got up to 87. this morning I noticed the pumps switched and the pump it was on was at 40% so I just upped it to 58%. water flow went from about 45gpm to 65gpm. there is a "set point" for gpm of 75gpm but not sure if that is an alarm or just the max it can be. I am letting the water temps stabilize as the water supply temp out of the condenser was going up from 41deg to 44 last time I checked. BUT the return from the AHU was coming down, it was at 60deg. my thinking is if there is more water flow then the water will stay colder making the air supply colder. (it was about 58deg.) the room temp was already up to 74
__________________
86 930 94kmiles [_ ![]() 88 BMW 325is 200K+ SOLD 03 BMW 330CI 220K:: [_ ![]() 01 suburban 330K:: [_ ![]() RACE CAR:: sold |
||
![]() |
|
Banned
Join Date: May 2014
Posts: 15,053
|
The slower the flow, the more efficient the transfer of cold to the liquid you are trying to cool.
More contact /longer dwell time is better. It also reduces the friction of water through the pipes and friction adds heat. In many situations, the best thing to do is run the liquid just fast enough to prevent freezing. Last edited by Ziggythecat; 08-09-2019 at 06:29 AM.. |
||
![]() |
|
UnRegistered User
|
Could you get the Following info?
Chilled water temp entering and leaving evaporator Chilled water pressure in/out evap. Refrigerant r134a? Evap ref press Ref temp leaving evap Cond press. Ref temp leaving cond Keep in mind this could be an air handler problem. Could you check air temp drop across the cooling coil? |
||
![]() |
|
Registered
Join Date: Oct 2003
Location: Roseville, CA
Posts: 3,066
|
You say the pumps are running at 40% so I would assume everything is on VFD's? If so, I dont understand why they are set to a specific speed...usually they modulate based on an input (inlet temp, static pressure, etc), otherwise just get a single speed pump that runs at whatever GPM you're looking for?!
__________________
1992 968 Polar Silver 2010 Toyota Highlander SE 2006 Lexus LS430 ML |
||
![]() |
|
Registered
Join Date: Oct 2006
Location: MYR S.C.
Posts: 17,321
|
its a 410 unit, 2 comps
water temp WAS set at 45 pumps at 40%=45gmp cond unit supp-42 ret-52 evap supp-43.3 ret-58.5 air temp- 59 ret air 74 flow-8.8gpm energy-5.6btu when I upped the pump to 58%=66gmp it raised the supp temp out of cond a little. (only 1 comp running) I dropped the water at the cond to 40 degrees. temp in cab was already up to 76 and now its coming down,. cond unit supp- 36 ret- 47 70gpm evap supp-37 ret-55 air supp-56 ret air-74.7 evap says 8.6gpm energy -6.4btu when would the water supply rate need to be changed
__________________
86 930 94kmiles [_ ![]() 88 BMW 325is 200K+ SOLD 03 BMW 330CI 220K:: [_ ![]() 01 suburban 330K:: [_ ![]() RACE CAR:: sold |
||
![]() |
|
Registered
Join Date: Oct 2006
Location: MYR S.C.
Posts: 17,321
|
water pumps have a minimum setting of 40%, I have never seen them any higher.
that's my question, why or when would the flow rate need to go up and would that help with cooling. the cond unit was not maxed out, was just thinking if more water in through the evap faster that would drop the return temp which would drop the air temp. no?
__________________
86 930 94kmiles [_ ![]() 88 BMW 325is 200K+ SOLD 03 BMW 330CI 220K:: [_ ![]() 01 suburban 330K:: [_ ![]() RACE CAR:: sold |
||
![]() |
|
![]() |
canna change law physics
|
Quote:
The flow should be varying with the heat load. Temperature should be constant. Control can be set based on many conditions, room temp, outside temp, return temp and and combination. The entire system, HVAC and the chilled coolant flow, should ramp together. We use chillers on our gas dehydration skids.
__________________
James The pessimist complains about the wind; the optimist expects it to change; the engineer adjusts the sails.- William Arthur Ward (1921-1994) Red-beard for President, 2020 |
||
![]() |
|
Home of the Whopper
|
Chillers have a minimum flow requirement.
Chillers are also just one part of a system. What is the other part? Air handling units with 2 way valves or 3 way valves? Any bypass in the system? Primary / secondary system? Variable volume system? Constant volume system? yes you can have a CV system with VFDs.
__________________
1968 912 coupe 1971 911E Targa rustbucket 1972 914 1.7 1987 924S |
||
![]() |
|
UnRegistered User
|
Someone may have changed some settings recently.
One sure fallback is to find the IOM (installation operation and maintenance ) books for the unit and ahu. Maybe the pumps have been overridden to manual? Seems like you could get a bit more performance on the temp drop of air with more flow. Too much flow can make for problematic operation and poor heat transfer on the water side. On the off chance that it could be the ahu check damper positioning/operation. |
||
![]() |
|
Registered
Join Date: Nov 2003
Location: Seattle
Posts: 1,785
|
Far from understanding what a bunch of the numbers posted were, but we had a restaurant that we just could not keep cool no matter what we did. Turns out a big part of the problem was that the float that added water to the supply when it dipped too low was stuck and we were constantly adding new water to the system and dumping other water out the overflow. Didn't work real well like that.
__________________
Rob 1980 SC - 2011 Tiguan - 2018 Tesla M3P |
||
![]() |
|
Registered
Join Date: Oct 2006
Location: MYR S.C.
Posts: 17,321
|
room temp is down to 74 and its hotter out so maybe I wont get bothered over the weekend
supp air temp is down a little more to 54.7 I dropped the water supply down to 50% the colder water temp setting did it. before I don't even think the second compressor was coming on due to the load on the outside unit was not hi enough. no one else is going to mess with it. its scary but I am the most knowledgeable one here on it. still would like to know if the water supply should be increasing with heat load like a variable air handler might.
__________________
86 930 94kmiles [_ ![]() 88 BMW 325is 200K+ SOLD 03 BMW 330CI 220K:: [_ ![]() 01 suburban 330K:: [_ ![]() RACE CAR:: sold |
||
![]() |
|
Home of the Whopper
|
Chiller should modulate to maintain a constant supply water temperature.
Water flow modulates to maintain AHU discharge air temperature setpoint, down to the chiller minimum. edit: Water flow modulates to AHU to maintain discharge air temperature setpoint. If 2 way valves, this also increases/decreases water flow in the system as the AHU valve modulates. If 3 way valves, the overall system flow does not change. or should not change, if the 3 way bypass was balanced properly.
__________________
1968 912 coupe 1971 911E Targa rustbucket 1972 914 1.7 1987 924S Last edited by BK911; 08-09-2019 at 08:46 AM.. |
||
![]() |
|
![]() |
UnRegistered User
|
Another important point.
If it truly is chilled water and not glycol, make sure you don’t turn it into a slushy machine!😉 |
||
![]() |
|