Yet again, another generator thread.
We are in the third day of a unusual major ice storm. The leaves are still on the trees, and have not even started to turn colors much less turn loose. The ice is devastating to all the trees. We have several trees that will have to be removed. Power is out to thousands of people in large areas of Oklahoma.
We are very fortunate, and we have electricity, and the only power outrage was about 20 second long. However, my wife has now decided we need a backup generator. :cool: In the 20+ year we have lived here we have had two power outages that lasted more than an hour. Evey time we have a generator thread I get the fever, and then sticker shock sets in when I settle in on a generator. Pretty much the consensus seems to be the Honda 2200i inverter generator. That would run the furnace, fridge and a few lights and we would get by fine. If it was a summer event and we needed AC we can go to to a motel way cheaper than the cost of a whole house generator. So my question is: How do I get the power into the house? The generator will be on the back porch and the extension cord through a door or window seems really stupid. I know they make the connectors that hook to the power panel in the house, and let us walk around in the house and turn the lights in that room. That would feed the fridge and furnace and any device in the house, we just have to be smart and not turn on too much. And I know that then prevents back-feeding to the grid and keeps the linemen safe. Any suggestions on a type of connection, and what exactly it is called? I will hire a real electrician to install it. I just need to know what to ask him to install. Would an electrician prefer I have the gizmo here and ready for them to install or do I trust them to sell me a good one? If it was all up to me I would just live without the generator, but the wife says get one, so a generator it is. |
An electrician can add an "outlet" that will be used as an inlet next to the panel. It installs with a manual interlock that requires you to turn off the main before you can make the gen input functional.
|
You need a three-way switch, sized to the same size as your service.
https://www.homedepot.com/p/GE-200-Amp-240-Volt-Non-Fused-Emergency-Power-Transfer-Switch-TC10324R/100150463 Or you can setup a sub-panel for your "essential" circuits and go with a smaller three way switch https://www.homedepot.com/p/GE-100-Amp-240-Volt-Non-Fused-Emergency-Power-Transfer-Switch-TC10323R/100171587 You then connect a Receptacle to the generator side of the transfer switch and the main power to the "line" side. The center is connected to your loads. When the power goes out, plug in the cable to your generator, start it up, THEN move the transfer switch to generator. |
Sure - you can get a more elaborate system - but if you're only talking about the rare occasional outage....you can't beat the practicality running an extension cord through a window.
Not that big of a deal and best of all it's free. What you'll have to work out is how large the cord should be and how many more you'll need to plug in your designated appliances. |
I bought a transfer switch with six circuits that is hooked into my main panel. Each circuit has a switch for "line" (normal use), "off" isolates the circuit from the line, & "gen" for power coming from the generator. When I had it installed for my generator, the electrician said, "Wow! This is cool. I usually make these." So I'd imagine you could have an electician make one to run power to the things you want to use during outages.
|
Some of those premade units are pricey! The Generac units from HomeDepot are about $800 depending on options!
|
I got flamed last time I mentioned this... But here goes again.
A quick and nasty way to get power to the house is to turn the house mains off so you are not supplying the grid. Have the generator outside, an extension cord running under a door, and a suicide plug plugged into any outlet. http://forums.pelicanparts.com/uploa...1603954709.jpg |
As I am typing this we are getting pounded by rain/wind from Zeta and the lights have been flickering :( . I have a Honda EU3000 standing by ready to go . I have a overhead garage door in the basement so I just roll the generator outside and run an extension cord under the garage door . That cord then goes up the basement stairs and into the house . I want to keep the fridge cold and have some lights and be able to charge cellphones .
Yeah it's a redneck way of doing things but it works . Maybe sometime in the future I will do a proper switch setup . |
One thing to keep in mind with a portable generator is that if power goes out and it is raining, you need to be able to keep it dry without asphyxiating yourself, so you might want to built a small enclosure to set it under.
I thought about putting a box on the side of the house under an awning of sorts and then have a plug from the box to the generator and then wiring in a few outlets maybe orange color near sump pump and near the fridge and then I could move the plugs into those outlets when the power goes out- pretty simple and low cost. Still manual work, but no extension cords running fifty feet through a window or door. |
For years we ran extension cords to the things we wanted powered.
We got serious 15 years ago and had "plug" installed that leads to a transfer panel and fuse box, which are located right beside the main house fuse box connected to the grid. Flip a few switches, plug in gen, start gen, power those items you want via the fuse box. Since we have a basement (never again) and are on our own well, the important stuff are the sump and well pumps. The rest is really not that much of a draw on power. I do have a roll around a/c unit, 120v, just in case:D |
Quote:
That is not an overly dangerous solution if you stay alert. Turn your main off, do not feed power back to the grid. I would make a 220V version and feed the entire house. They are very common where I live. It's like bungee jumping. If it scares you, don't do it. |
As a start while waiting how many outages and duration we will be getting here I installed an inlet receptacle on the outside of my house connected to a duplex receptacle inside. I connect the Honda generator to the outlet receptacle. This is used to keep just the refrigerator going and charging cell phones, maybe have a light on at night. I was looking at going with a more elaborate system including a transfer switch but I'll try this for a few years and see how it goes. There is some interesting reading regarding how to setup a transfer switch - e.g. do you ground the generator and/or switch the neutrals? If someone wants to post a diagram of a way or ways to do it that meets code that might be helpful.
|
I recommend a gererator.
|
I gave a generator and transfer switch away that I purchased for my parents.
Grounding. If you use a transfer switch, the "house" provides it from what I understand. Do you guys running an extension cord(s), ground the generator? If I ever lose power more than three hours ..... I'm heading to Oklahoma .... mebbe Glen will let me crash at his place :D. Then again.... mebbe not ;). If I go AWOL later today .... Knock, knock.... |
Our house is in a neighborhood with all underground utilities. The only utility poles we have are for some street lights.
|
Quote:
|
Quote:
|
I went down that rabbit hole this summer. With three freezers full of food we can't afford a prolonged outage. The house was wired for a portable generator, there is a special plug on the outside wall to plug the generator into and had a manual transfer switch. I had it inspected and was told it was old but would probably work for our barest of needs.
Then I looked into generators. I would have to store it in a barn 100 yards from the house and go get it if there was an outage and we were home. If we were traveling it would just sit. I would have to start it up every few weeks to keep it limbered up and keep the fuel fresh. After adding up all the minuses of using a portable and the only minus to getting a dedicated generator ($$$) I went with a 13kw Generac running on natural gas and a 16 breaker automatic transfer switch. All in it cost $6000 but it is totally hands off and the entire system has a warranty. It still freaks me out at 2:00 PM every Wednesday when it fires itself up for 12 minutes of exercise. I get an email with a report on oil pressure, rpm, etc. I really like the fact that it is totally hands-off and will keep the furnaces and freezers running even if we are traveling. http://forums.pelicanparts.com/uploa...1603982888.jpg http://forums.pelicanparts.com/uploa...1603982888.jpg |
^^^ That is just where I kept ending up at. 6 large or more and so far in 20+ years of living here it would have been needed 12 to 20 hours total. So 6K for a day of power is just insane in my mind.
The longest outage we had was in the spring and the house got up to 80, and we were forced to eat ice cream for breakfast since it was melting. We don't have a deep freeze, and never store a lot of meat. My wife does have a fresh water Tropical fish aquarium. Those fish would be in a serious hurt if they want a day without electricity. The koi pond out in the back yard is deep enough it would likely be OK for a few days with no pump action. |
You can get smaller generators. I went with the smallest 2-cylinder because a Generac service guy once told me the single cylinder units are less reliable.
|
Quote:
every hard rain they go down good idea but hard to do right in low areas with a high water table esp if done on the cheap by land developers last bad hurricane the power was off then on then off for days as they fixed the system we had extension cords running across the street to send power from the working side or the guys with bigger generators sharing several homes with power |
Quote:
|
I keep thinking about replacing my Generac (10kW/12.5kW peak) with a 20kKW diesel because of the noise (could be worse, but I find it really irritating). But I'm in the same boat as others weighing getting a generator against the amount of use it would get. The amount of time we have to run it isn't all that much. If I went that route, I'd also upgrade the transfer switch to power more circuits and add in the well pump - so $$$$$.
|
Quote:
|
Quote:
|
Quote:
|
We actually went without power for three days last year. They were replacing a bunch of wood poles in the area with huge steel ones. It's being done to mitigate problems in case of fire & high winds. Some of the distribution poles are huge, and the others in between are much taller than the old wood poles. I'm going to wait to see if they reduce or eliminate outages - although like I said, outages haven't been a big problem. If it works out, I won't need to think about a generator.
|
Three days without power here and my Honeywell 5500 ran like a champ. I found it new on Craigslist for $300. Well worth it at twice the price. Next project will be a transfer box setup so I don’t have to run cords everywhere.
|
We had a small generator which allowed us to plug in fridge and freezer and maybe something else, but it was manual start. It was almost more than the wife could do to start it if I wasn't home.
Now there is an electric start unit in a repurposed shed (with forced air ventilation ) feeding a switchable panel in the house via an underground cable. Problem solved. Best Les |
Quote:
|
Quote:
Like that? |
Quote:
|
Zeta just blew through the ATL and here in Mariettta, GA we are going on 30 hours now sans power. After loading up 3 five gallon fuel cans, I found an open station and filled them all, then yanked my 3000 watt portable generator out and under our deck, strung all the extension cords I could find, and soon had the fridge, TV, laptops/chargers, etc. up and running. Our cable-based broadband came online overnight, so I can share this message with you.
Having recently retired from the generator part of American Honda, I can tell you from my many customer interactions that a basic 2000-3000 watt portable will do a great job for most homes. It will easily run the basics, as long as you thing of it as 'indoor camping' and understand not every single device is going to get power. Learn to 'load share', i.e., if you need to do laundry, unplug the fridge and plug in the washer. If you have gas heat, it's not too hard to wire up a special plug to run the 120v blower motor. On the other end of the thermometer, consider buying a small window AC unit for use in the bedroom; it will keep you cool enough to sleep at night, and many will easily run on a small generator. Best of all, a 2k-3k inverter-style generator (Honda and Yamaha make really high quality products), extension cords, fuel cans, etc. will run you $2,100~$3,500, far less than the five-figures it would cost for for a whole-house unit. Oh yeah, the cheaper portables are, well, portable. Nice if your house is doing okay, but a neighbor or nearby family member is dead in the water. New model Hondas even have an smartphone/Bluetooth App that can report output levels, fuel remaining, etc. Don't be an idiot and use the stupid f*cking suicide cord. If you are a single hermit, with no family, okay, fine. But if you have a wife, kids, etc. that have 'watched daddy hook up the generator' and now try and do it without you, you are asking for tragedy. I'll guess most of the people reading this understand the danger of Carbon Monoxide poisoning from engine exhaust, and will be sure to only place a running generator in an outdoor location. |
I just ordered a dual fuel (gas/propane) 8kw, electric start Champion gererator before I read about their notorious problem with XS oil consumption because Sandwicher can’t pull the cord anymore-which is a bad sign all the way around.
|
We lost our power yesterday at 6:00 in the morning and it's still out ☹️ . Two power poles snapped in half about 3/4 miles from my house. I expect to be without power for the weekend but maybe will get lucky 😁 .
My Honda E3000 generator is humming along powering a fridge , freezer , various lamps and cellphone chargers . Buying more gas today for the next two days . Fun times |
Quote:
five figures? You must have a BIG house. I paid $9000 all-in for a 20kw Generac and transfer switch with a load shedding switch for the AC. That was 3000 square foot house. |
Quote:
|
costco has some decent sized 5K-9K dual fuel generators at fair prices too.
|
Quote:
|
Timely thread for me. We are building a new home and want to plan for wiring (cut-over switch) now and perhaps add a generator later. It'll be connected to natural gas.
Appreciate input for our planning. Now is the time since we are in the design stages. |