rfuerst911sc 09-04-2021 02:10 PM

Paging Red Beard ........ generator question
 
I know Red Beard is a generator subject matter expert but anyone can chime in with knowledge of whole house generators. Local to me is a Honeywell 11 kw propane generator for sale with 714 hours on the hour meter . Owner says they bought it to have power while their house was being built . House now done and they decided to sell it.

It comes with a transfer switch and I have asked what paperwork might be included . They are asking $2,000.00 which sounds like a decent deal . Seller says in the ad it runs great but has a " slight oil leak " . I would have to look at it and see if it's a big deal or not regarding the oil leak . So Red Beard or anyone else does this sound like a good deal ? Are Honeywell generators good quality ? Thanks in advance 🙂

rfuerst911sc 09-04-2021 03:23 PM

Looks like an air cooled twin like most are . Off hand don't know the engine brand I will do some research . Seller says he has original owners manual and the oil leak is tiny ....... so small he says he can't find where it's coming from . It doesn't concern me it won't run that often . I did ask him why he's not keeping it for backup power , he said he would but needs the money .So I will try some negotiation .

rfuerst911sc 09-04-2021 03:58 PM

Ok so Generac makes Honeywell so they use Generac branded engines . And nearest I can tell this sold for 3500 - 4000 new in 2016 when it was purchased . That's all I know at the moment 😁

rfuerst911sc 09-04-2021 05:49 PM

Quote:

Originally Posted by Arizona_928 (Post 11448013)
If an air cooled twin that motor might be at end of life. Kohler 20 ish hp twins usually don't make it past 1500 hours.... the last one i ran using it for a hydraulic motor made it to 1100ish hours before it was completely worn out.


I would load test and make sure it's still good....

Any ideas on how to do that when the generator has been fully disconnected ? So it's basically just how you pull it out of the box when new . I would have to " rig " a BBQ propane tank is my guess .

Arizona_928 09-04-2021 06:10 PM

Quote:

Originally Posted by afterburn 549 (Post 11448016)
Whilst we are at it I am looking for a 3 cylinder turbo-charged Genset too! (Nothing from China please)
thanx

Kubota 1105 or Mitsubishi l3E. Both will get 15,000+ hours on 6kw 1800 rpm gen heads

rfuerst911sc 09-04-2021 06:12 PM

Did a few internet searches for " how many hours will a Generac engine last " and most sites say 3000 hours with proper maintenance . Proper maintenance looks like oil/filter change every 200 hours and valve adjustment every 400 hours . If that is accurate AND if the seller followed the schedule then it " should " have a lot of life left in it .

rfuerst911sc 09-06-2021 09:12 AM

Well another option has appeared but it's 160 miles away . An 11kw Kohler whole house style generator with 140 hours for $1900.00 but does not include the transfer switch . He has the transfer switch but wants extra $$$ for it . The engine is a 7000 series air cooled twin .

Compared to the first one there is a difference of aprox 600 hours , other than that I think the Honeywell and Kohler are similar in quality . Is the road trip worth the less hours ? Common sense says yes . What do you guys think ? I think an 11kw will run our 3 ton AC and well pump and a few other items using some common sense . I also will have to find a 250 or 500 gallon propane tank .

red-beard 09-06-2021 02:23 PM

Sorry, only just saw this.

#1. What size transfer Switch for each one? It has to be enough to allow power to your house under normal circumstances. If you have 125A service, you need a 150A or larger TS.

A 200A Transfer switch is about $1K new. You can order Generac TS through Home Depot.

The First deal sounds pretty good, but I would question the owner to the number of times the oil and filter were changed. It should be about every 100 hours. The other Generator with 140 hours, again ask about the maintenance.

You should stick with a transfer switch from the same company or manufacturer since some "talk" between the generator and the TS. We used to sell Briggs & Stratton. Each one "starts" the generator in a slightly different way.

That said, all of the generators are comparable. I like the Kohler for the way the generator starts. But we could accommodate any system with our Control System,

$2K for a 11kW Generator is a decent deal. The hours are OK if it were taken care of properly. $1.9K for a used 11kW with 140 without the TS seems a little bit high, but in the ball park..

rfuerst911sc 09-06-2021 03:46 PM

Red Beard here's what I know . My house has a 200 amp main service panel . The first generator is a Honeywell that includes a Generac # 6334 100 amp transfer switch . To me it looks like a manual switch . Can a 100 amp be used to feed a 200 amp panel ? I know that sounds silly but can't I control load via my home breaker box ? Turn off high amp breakers then add as needed .

Second generator is a Kohler and he is selling a Honeywell transfer switch for $300.00 . I can't see a model number but it is physically fairly large and the nomenclature on the decals sounds like it is a auto transfer switch . I do not see an amp rating .

CalPersFatCat 09-06-2021 04:33 PM

Quote:

Originally Posted by rfuerst911sc (Post 11449619)
Red Beard here's what I know . My house has a 200 amp main service panel . The first generator is a Honeywell that includes a Generac # 6334 100 amp transfer switch . To me it looks like a manual switch . Can a 100 amp be used to feed a 200 amp panel ? I know that sounds silly but can't I control load via my home breaker box ? Turn off high amp breakers then add as needed .

Second generator is a Kohler and he is selling a Honeywell transfer switch for $300.00 . I can't see a model number but it is physically fairly large and the nomenclature on the decals sounds like it is a auto transfer switch . I do not see an amp rating .

The 6334 is, as you stated, a manual transfer switch. I am a VERY minority partner in a Generac Premier Power Pro Dealer ($1.5m or more purchased from Generac annually, and a bunch of other service/technician related requirements). If you bought the generator from me, I would sell you that switch for $199. It is a current model. Lowes cost on it is probably $100. I'm not kidding.

You need a 200 amp automatic transfer switch. When you are out of town, you want the system to work as if you were in the next room. Again, Lowes is your best bet for that. Expect to pay $700 for it. The Honeywell costs $10 more than the Generac. If I had a Honeywell Gen then I would get a Honeywell Xfer Automatic Xfer Switch. When you sell your house it will present better.

Lowes is fantastic. We have the installation agreement for 15 Lowes Stores in a region in Florida and we do several installations for them each week. They will treat you right on that Auto Xfer Switch.

DL

rfuerst911sc 09-06-2021 05:23 PM

^^^ Appreciate the advice and now that I read what you said it makes perfect sense to have the 200 amp auto transfer switch .

red-beard 09-06-2021 08:02 PM

Yep, you have to have a TS switch at least equal to the size of the house service. I would agree that you want an Automatic TS.

rfuerst911sc 09-07-2021 04:17 AM

The transfer switch the Kohler generator guy has is a Honeywell OH7264E which is an auto switching but I think rated 100 amps . So either generator I am looking at I will have to purchase a 200 amp rated transfer switch .

rfuerst911sc 09-07-2021 06:24 AM

Hmmm I had asked the Honeywell seller how often has he changed the oil/filter in the 700+ hours . And have the valves been adjusted . He just replied .......... he has NEVER changed the oil/filter just topped it off as needed . And no valve adjustment ever done . I can live with the lack of valve adjustment but very concerned about the lack of oil and filter changes . Don't most air cooled generators come with break in oil that needs to be changed after 10 hours or so ? Then once yearly or every 100-200 hours ?

Not sure if I should make an offer of 1500 or not . No guarantee that he would accept and based on lack of maintenance I wouldn't pay any higher than that . What do you guys think ?

red-beard 09-07-2021 06:42 AM

That is a non maintained air cooled engine. This filters (air and oil), oil and spark plugs should be changed yearly or after 100 hours of operation.

These engines are basically 2 cylinder lawnmower engines, but with filters. I'd skip that one.

rfuerst911sc 09-07-2021 06:46 AM

Quote:

Originally Posted by red-beard (Post 11450052)
That is a non maintained air cooled engine. This filters (air and oil), oil and spark plugs should be changed yearly or after 100 hours of operation.

These engines are basically 2 cylinder lawnmower engines, but with filters. I'd skip that one.

Appreciate the honest feedback . And check your PM please 😁

rfuerst911sc 09-07-2021 09:07 AM

Quote:

Originally Posted by CalPersFatCat (Post 11449649)
The 6334 is, as you stated, a manual transfer switch. I am a VERY minority partner in a Generac Premier Power Pro Dealer ($1.5m or more purchased from Generac annually, and a bunch of other service/technician related requirements). If you bought the generator from me, I would sell you that switch for $199. It is a current model. Lowes cost on it is probably $100. I'm not kidding.

You need a 200 amp automatic transfer switch. When you are out of town, you want the system to work as if you were in the next room. Again, Lowes is your best bet for that. Expect to pay $700 for it. The Honeywell costs $10 more than the Generac. If I had a Honeywell Gen then I would get a Honeywell Xfer Automatic Xfer Switch. When you sell your house it will present better.

Lowes is fantastic. We have the installation agreement for 15 Lowes Stores in a region in Florida and we do several installations for them each week. They will treat you right on that Auto Xfer Switch.

DL

Sent you a PM .

rfuerst911sc 09-07-2021 04:17 PM

Any feedback on this Cummins ? Supposedly in stock and includes a 200 amp transfer switch . Not sure what shipping cost is .


https://themobilegrid.com/product/cummins-quiet-connect-20kw-air-cooled-home-standby-generator-rs20a/

red-beard 09-07-2021 09:06 PM

Looks good. Figure $750 for shipping.

David 09-08-2021 05:07 AM

What's involved for installation? What size gas line for a 20kw unit if running natural gas? How does the transfer switch get wired in?

My mom is looking at having one installed and it seems the going rate is over $10K installed. I don't see where the $5-6K of installation comes from. Looks like a days worth of work and a couple hundred dollars in material. Plus permits of course.

wdfifteen 09-08-2021 05:29 AM

My old house had a 19k Generac. The main panel was 200 amp and the automatic transfer switch was 100 amp with a load shedding switch on the AC. The transfer switch was sized based on the actual electrical load in the house. The circuit to our detached garage was bypassed. The one time we used it the AC ran the whole time the generator was running.

Our current set up is a 13k Generac 60 amp automatic transfer switch with a 16 slot breaker panel. Main panel is 200 amp. All critical circuits are fed off the panel on the transfer switch. That’s basically all fridges, both furnaces, the fan in the water heater, and lighting. When the power goes out we do without AC and power to the out buildings and a couple of lighting circuits.

I didn’t design either system. In both cases we had the Generac dealer look at our needs and make recommendations.

Just letting you know you don’t HAVE to have a 200 amp TS in a 200 amp house.

red-beard 09-08-2021 05:30 AM

The cost of the Generator plus TS is around $4500. $8k is $2500 for install and maybe $1k for profit.

About $1000 for the electrician, $750 for pipe, wire, conduits and gas regulator and the rest is labor for trenching and install.

Cables are 00, 100Amp breaker. Pipe size is 3/4" if you put the regulator at the generator. If the electrical box and gas meter are not close, install goes up. If you need city permits, price goes up. If you need licensed plumber for gas line and certified electricians for conduits, price goes up.

red-beard 09-08-2021 05:36 AM

Quote:

Originally Posted by wdfifteen (Post 11451252)
My old house had a 19k Generac. The main panel was 200 amp and the transfer switch was 100 amp with a load shedding switch on the AC. The transfer switch was sized based on the actual electrical load in the house. The circuit to our detached garage was bypassed.

Our current set up is a 13k Generac 60 amp transfer switch with a 16 slot breaker panel. Main panel is 200 amp. All critical circuits are fed off the panel on the transfer switch. That’s basically all fridges, both furnaces, the fan in the water heater, and lighting. When the power goes out we do without AC and power to the out buildings and a couple of lighting circuits.

Just letting you know you don’t HAVE to have a 200 amp TS in a 200 amp house.

If the TS directly feeds the main panel, yes you do! They must match.

If the TS feeds a sub-panel, it can be smaller.

wdfifteen 09-08-2021 05:39 AM

Quote:

Originally Posted by red-beard (Post 11451258)
If the TS directly feeds the main panel, yes you do! They must match.

If the TS feeds a sub-panel, it can be smaller.

Edit: On second thought, the TS includes a sub panel in my current house and fed a sub panel at my old place.


The TS basically is a sub panel in my current house, and I believe it was that way in the old place.

wdfifteen 09-08-2021 07:00 AM

rfuerst911sc, I suggest you consider whether you really want the house to "act like you are in the next room" when the power goes off or if you want to do without some items.
According to Tons Of Air Conditioning to Kilowatts | Kyle's Converter a 3 ton AC unit uses 10.5 kw of power. With an 11kw generator you don't have a lot of wiggle room for other things. At the very least you should consider a load shedder on the AC. You should do a whole house power assessment and see what you really are using.

We looked at the cost of an adequate generator to run the whole house and decided to downsize. We listed all the things we could do without in an emergency - AC, car charger, outbuildings, pool heater, dish washer, etc and conferred with our Generac dealer. He suggested a transfer switch with a sub panel than only powered the things we really needed in an emergency. The power goes out about 4 times a year out here and we have been happy to get along with partial power.

http://forums.pelicanparts.com/uploa...1631109285.jpg

The box on the left is the main panel. The center box is the old sub panel to the west part of the house. The box on the right is the transfer switch with all the essential circuits when the power goes out.


http://forums.pelicanparts.com/uploa...1631109285.jpg

The old sub panel still powers the AC, car charger, outside pool pumps, outbuildings, etc. as well as the 60 amp transfer switch sub panel (breaker on the lower right). When the power goes out, these circuits all go dead. It still has the old breakers in it, but they are disconnected.

http://forums.pelicanparts.com/uploa...1631109285.jpg

The transfer switch/sub panel powers the refrigerators, freezers, furnaces, water heater,
lighting, and other things we can't do without. When the power goes out, it starts the generator and provides power to all of these circuits.

Arizona_928 09-08-2021 09:16 AM

Not bad for a days work....

rfuerst911sc 09-08-2021 10:07 AM

I am slowly leaning towards a 20kw and be done . After studying manufacturers websites for size/price/fuel consumption there is not a lot of difference between 12kw and 20kw. Yes the 20 is more up front and a little hungrier with fuel consumption but it's not a huge difference . A 20kw will run my entire house .

But then I start thinking that in a " normal " year we lose the power two times . Some years more and some less. In that scenario I start thinking about what can we do without , can we get creative with load management via breakers and maybe a 12kw either whole house or portable is the way to go . If I would go portable I would still do a transfer switch and buy a duel fuel so it can run off a 250 or 500 gallon tank .

Currently we use our Honda 3000 watt inverter generator with the spaghetti mess of extension cords 😁 . I primarily only keep refrigerator and freezer going so food doesn't spoil and a few lamps. My point being we can go without certain amenities but I prefer not to.

Evans, Marv 09-08-2021 02:48 PM

Patrick's Kyle's Converter says I need 25 kW just to run my seven ton load for my HVAC. That's a lot more than I thought for that basic power need. I've been mulling over a whole house generator for a while & still haven't made up my mind to pull the trigger or just keep with my 10 kW that powers fridge, freezer, & some lights for the few times we're out of power. I was thinking maybe a 20/25 kW diesel, but it seems like I might need to go for 30/35, which is a pretty good sized system.

red-beard 09-08-2021 08:46 PM

Quote:

Originally Posted by wdfifteen (Post 11451357)
rfuerst911sc, I suggest you consider whether you really want the house to "act like you are in the next room" when the power goes off or if you want to do without some items.
According to Tons Of Air Conditioning to Kilowatts | Kyle's Converter a 3 ton AC unit uses 10.5 kw of power. With an 11kw generator you don't have a lot of wiggle room for other things. At the very least you should consider a load shedder on the AC. You should do a whole house power assessment and see what you really are using.

a 3 Ton Air Conditioner uses about 3-3.8kW of power. It may need up to 13 kW to START.

This is an older 13 SEER air conditioner, so some newer ones may not require so much current. Check the label on your Air Conditioner outdoor unit.

For Starting, use LRA (Locked Rotor Amps) multiplied by your 220-240 voltage. This is the starting power. With a Generator, the unit may allow up to a 30% voltage sag, which will reduce the starting power.

For running, use RLA (Rated Load Amps). You really should also add the FLA (Fan Load Amps) to the running current. And this data sheet does not show the evaporator and the blower which would be about another Amp or so.

But this will not add up to 10 kW of power.

http://forums.pelicanparts.com/uploa...1631158747.jpg

That "Kyle Converter" is straight up wrong.

Arizona_928 09-08-2021 08:59 PM

+1
One could go to soft start setups; vfd ect. But that adds cost.

I'm a firm believer in manual everything except for the semiautomatics... :rolleyes:

I would run a generator interlock for the breaker panel. This is a house, not a research lab, or server farm where if the temperatures rise **** goes boom/ruined.

As for the cheaper buy in price air cooled stuff; while they have a purpose for the average joe that won't run a bunch of hours over the water cooled diesel. If you plan to use the machine to full potential the 12k buy in on a diesel that will run 10k hours over the twin air cooled for a quarter of the price.

red-beard 09-08-2021 09:10 PM

Really Good Soft Starts are not expensive. $245.99

Hyper Engineering | Home

https://shop.gentekpower.com/collections/sure-start-ac-soft-start-ss1b08-16sn-ss1b16-32sn-hyper-engineering

SS1B08-16SN for up to 3 Tons
SS1B16-32SN for up to 6-7 Tons

They also make 120VAC units for RV units.

And 3 Phase units. They work for 50 or 60 Hertz

Arizona_928 09-08-2021 09:35 PM

Hmm those are a really good price!

Baz 09-08-2021 09:40 PM

Even though I'm in Florida and we get our share of hurricanes - and with some of those power outages....I have yet to justify in my mind one of those "house generators".

What I did do is get a portable with electric start that can run off gasoline or propane. It came with wheels and a handle so very easy to move around.

I bought it on Amazon just over a year ago for around $470 and don't believe the same model is available anymore. I moved it to my back patio where it is closer to my refrigerator and window AC - and whatever else I want electric for. And ran it just the other day after not running it for almost a year. The battery was still charged and she started right up with the flick of a switch. Runs pretty quiet too for a gas unit.

I don't mind a few extension cords. Worth the effort to have power to the fridge and AC!

http://forums.pelicanparts.com/uploa...1631162211.JPG

http://forums.pelicanparts.com/uploa...1631162211.JPG

GH85Carrera 09-09-2021 11:57 AM

Baz, I am right there with your way of thinking.

Every generator thread gets me wanting one. Then I realize how much the whole house units cost, and my interest shifts to a Honda inverter unit. Then I get to wondering where do I want to store it, and how much gasoline do I keep on hand and I get lazy and just forget abut it.

My back fence neighbor used to work for the local electric utility. He put in a 12 grand generator that automatically starts and tests itself regularly. He has had it for 9 years so far and he has used it for 18 minutes of backup power. That is some really expensive power.

We don't worry about hurricanes or tsunamis in Oklahoma. The biggest baddest tornadoes came through central Oklahoma. One F5 had 300+ MPH winds and leveled a few hundred feet wide paths of utter destruction. Another one was 2.5 miles wide and moving at nearly 100 MPH across the ground. Neither even made the light flicker in my part of town. The worst damaged areas were just a 1/4 of a mile from full civilization with hospitals and restaurants and gas stations everywhere. So nothing at all like the recent hurricanes and flooding where entire areas are in the dark.

If I happen upon a great deal for a Honda generator, I may buy one, but it is low on my list of to do.

red-beard 09-09-2021 12:45 PM

Since moving to Texas in 2004, we have had the following weather events

Hurricane Rita - 2005 (stronger than Katrina)
Hurricane Ike - 2008 - off for over 4 days
Hurricane Harvey - 2017 - Did not lose power
Great Texas Freeze 2021 - off for 30 hours

We have had numerous outages for random stuff. One of the power-lines feeding the south side of the neighborhood is much worse than the north side.

A few notes on power reliability

99% reliability means your power is off 3 days, 16 hours per year.
99.9% reliability means your power is 8 hours and 45 minutes per year
99.99% reliability means your power is off about 1 hour per year
99.999% reliability means your power is off about 5 minutes per year

The Average in Texas is about 2 hours per year. This is statewide.
The Average in Houston is about 8 hours per year. And this comes from being without power for days, every few years...

GH85Carrera 09-09-2021 01:20 PM

There is an retirement and assisted living center about a 1/2 mile north of our house. I really think they get priority service. In the big ice storm and sub zero freeze from this February we had about 2 minutes of power loss. All of our lines in the neighborhood have underground service.

OGE is our electricity provider. They are rated very highly by the industry and I sure love em.

Zeke 09-09-2021 02:10 PM

When you start figuring the cost of propane tanks you end up realizing you could have 10, 15, 20 twenty pound tanks for less than what a 200, 300 or 400 lb. tank would cost. The price of the fuel is the same.

I think you could figure on having 2-3 generators using the same reasoning. And if one takes a siht, you still have power. I only have a 120v 3000K unit to keep the beer cold. I could have 3 for $1500 and be at 9K potential. They also will pair up if you buy the right ones.

rfuerst911sc 09-09-2021 03:56 PM

Possible interesting twist , a Miller Pro 300 diesel welder/generator has popped up for sale . Have asked seller for details . It is a 2014 model year .

rfuerst911sc 09-10-2021 04:58 AM

Looks like the welder/generator might be a scam . Oh well .

rfuerst911sc 09-11-2021 04:22 AM

Interesting scam . I received an email from the seller last night with several pics of the generator ( or someone's generator ) . The seller provided her name and stated she is currently at Offutt AFB in Nebraska . Ok so far maybe it's legit ....... maybe.

She provides some details including the hours on the meter , then it gets weird/scammy . She asks me to provide my name and address ( red flag ) so eBay can start the process of DELIVERY to me !!!??? She states she made these arrangements prior to her leaving for the AFB . And as a final touch she states her husband passed away two months ago .

I can see how someone could fall for this , but it has warning written all over it to me . Could I be wrong ? Sure . But I am not willing to gamble . Be careful out there guys there are a lot of folks wanting to steal the contents of your wallet .