Bingo! At this point I'm somewhat happy to say the AC contractor now agrees something odd is happening. Now we can cut the bravo sierra and start diagnosing the issue.
__________________
Sold: 1989 3.2 coupe, 112k miles |
||
![]() |
|
Mighty Meatlocker Turbo
Join Date: Apr 2016
Location: North TexASS
Posts: 18,526
|
^^^
There is a good chance that they either did not get all of the air and moisture out of the system after all (possibly due to an unfound leak, as indicated by one of your vacuum charts), or did not add the proper amount of refrigerant (too much or too little), given the strange rise in evaporator temps even when the compressor is running. Mini-splits come with the compressor pre-loaded with refrigerant that is sufficient for whatever length of piping the install manual specifies (more must be added if that length is exceeded); with your complex system (multiple evaporators/head units), I'm betting the installers did not correctly calculate how much additional refrigerant to add. When set up correctly, those Mitsubishi's are capable of bone chilling cooling, way beyond what a normal person (me being abnormal! ![]() Last edited by Rawknees'Turbo; 10-12-2023 at 04:44 PM.. |
||
![]() |
|
Registered
Join Date: Mar 2005
Location: Northern CA
Posts: 4,703
|
Quote:
1 - They/we did many evacuation runs with the last couple under 500 (~420) microns. From all my reading under 500 is good. However 420 is certainly nothing to write home about. I think the system is dry enough to operate to spec. 2 - They were aware that a calculated amount of R410A needed to be added - two people checked the calculation. Of course they could have still put in not enough. 3- Your last point is the best - When properly installed and setup I should get "beer" cold air. He now admits something is off.
__________________
Sold: 1989 3.2 coupe, 112k miles |
||
![]() |
|
Registered
Join Date: Mar 2005
Location: Northern CA
Posts: 4,703
|
I think I'm finally getting somewhere on this. What do we know now:
1 - The one GL wall unit appears to be somewhat okay running by itself. The controls work and it tries to heat and cool. 2 - The GL unit doesn't, at this point, have the capacity to cool the big room enough. 3 - When two or more of the smaller bedroom units are turned on the "big" GL unit all but stops cooling. This brings to mind a question. When the GL (24,000 Btu) unit is running alone is it cooling near its capacity? How would we test this? Fortunately the CFM for the 5 different fan speeds are in the service manual. I should have thought of this before... it is easy to calculate the cooling provided (Btu/Hr.) using the very common equation Q=1.08*dtF*CFM. So I tested the unit while on full cooling (min. set point of 61F) at the 5 different fan speeds and this is what I got. What do you think now? ![]()
__________________
Sold: 1989 3.2 coupe, 112k miles |
||
![]() |
|
Registered
Join Date: Dec 2002
Location: Dahlonega , Georgia
Posts: 14,570
|
Just for a data point my man cave garage is 24x26x12 foot high ceiling . Has 2x6 walls with R19 fiberglass insulation . The ceiling is also R19 . Two garage doors are insulated . So overall a fairly tight building .
The Mitsubishi 24k mini split can get the interior to meat locker quickly . I have never timed it but my guess is less than an hour after turn on . Likewise in heat mode it heats quickly . Just a single head unit . Past experience with a 3 bay garage in my previous house again with a 24k Mitsubishi was similar . I guess in both cases my installer did a great job . When installed properly the performance is excellent in my opinion . |
||
![]() |
|
Registered
Join Date: Mar 2005
Location: Northern CA
Posts: 4,703
|
Quote:
The contractor is being a bit quiet right now. At some point I might need an independent evaluation and see if the system is capable or has an issue. If you have a way to measure air temperature and don't mind checking - maybe you can measure the coil input and exhaust temps for me to compare. I've seen a few measurements in the high 40sF but those don't last long. Probably will require a ladder to get to the top of the coil. The controls work by looking at the set point and air temp. going in the coil. That's what "people" are saying. Thanks in any case.
__________________
Sold: 1989 3.2 coupe, 112k miles |
||
![]() |
|
![]() |
Registered
Join Date: Mar 2005
Location: Northern CA
Posts: 4,703
|
@rfuerst, If you want to do some measurements I suggest.....
Fan speed 3, vanes down 3 "notches", setpoint 61F. I assume you have a GL24 unit but if different please send out the model #. Thanks.
__________________
Sold: 1989 3.2 coupe, 112k miles |
||
![]() |
|
Mighty Meatlocker Turbo
Join Date: Apr 2016
Location: North TexASS
Posts: 18,526
|
hcoles, those head units have three temperature sensors - one on the evaporator's in pipe, one on out pipe, and a room sensor that is beneath the cover, to the side of the LED display/sensor for remote control (there are a couple of small slits on the side of the cover and the room sensor is there - it basically looks like a short, thin black wire . . . can't see it without removing the cover/case however). I know this because I had to make mods to those when installing my aftermarket controller.
With my fan speed on the second from highest setting (not the "powerful" setting), and the remote control temp set at 61 (my aftermarket controller not operating at the time), the air exiting the evaporator is consistently in the 45-48 degree range (with aftermarket controller running the exit air temp gets much lower). My model is GL24 (a/c version only - no heat pump function). Based on what you've described above, it sure seems like there has been an error made in the amount of refrigerant added. Unfortunately, your best option at this point is probably going to be getting someone else to look at/test the system, as long as you can find a tech that you are confident he/she knows what they are doing (based on your remark about installer business going quiet). Last edited by Rawknees'Turbo; 10-15-2023 at 04:53 PM.. |
||
![]() |
|
Registered
Join Date: Mar 2005
Location: Northern CA
Posts: 4,703
|
Quote:
__________________
Sold: 1989 3.2 coupe, 112k miles |
||
![]() |
|
Registered
Join Date: Mar 2005
Location: Northern CA
Posts: 4,703
|
Okay people, the saga continues.
During hot days the large family room unit goes to a high (+65F) discharge temp. when it should keep supplying cold air. The contractor agrees something is not right. I've been watching them closely e.g. during the pressure and vacuum processes because I found the brazing "issue" and ground wires placed in the panel on the wrong bus. Then the vacuum process had poor performance due to worn out equipment/etc. Anyway - I'm watching them like a hawk. Now the GM and lead tech. wants to come and work on the system - AND - doesn't want me to be near where they are working. I suspect many reasons but of course not sure why he would all of a sudden change how we are working. My main concern is he will again not do a good job during the vacuum process and doesn't want me to see him do that. Am I being unreasonable to want to know exactly what they are doing?
__________________
Sold: 1989 3.2 coupe, 112k miles |
||
![]() |
|
Registered
|
Quote:
__________________
Rutager West 1977 911S Targa Chocolate Brown |
||
![]() |
|
Registered
|
A couple simple things to check with the contractor. Is the vacuum pump a minimum 3-5 CFM capacity? Is pump oil clean, should be changed after each use as contaminates, moisture are captured in the oil. Does pump pull below 500 microns when “blocked” off? Does the tech know triple sweep, double evacuation procedure? Did they purge the line set with nitrogen before brazing to prevent oxidation? Looks like they used foscopper brazing solder on the lines, not silver solder or silfos or stabrite. You should talk to the tech intelligently before he starts to work as rwest suggests, so he knows you’re pretty well versed as to what’s happening with the system. Good luck, hopefully the problem will be resolved.
|
||
![]() |
|
![]() |
Registered
Join Date: Mar 2005
Location: Northern CA
Posts: 4,703
|
Quote:
FYI - When the system was first installed they pressure tested with nitrogen and vacuumed the system. This is where we hit a snag. I read the Mitsubishi manual that describes the vacuum process and specs. Their equipment initially was not capable because it was worn out and needed maintenance. I figured all this out and they finally showed up with much better equipment and pulled an "okay" vacuum. So, I feel justified in being skeptical and wanting to watch closely to what they might do. I understand it is not comfortable to have someone watching over you when working. The bottom line is at this point - when someone makes a big change (very open to don't be near us) without explanation - it makes me feel they are untrustworthy.
__________________
Sold: 1989 3.2 coupe, 112k miles |
||
![]() |
|
Registered
Join Date: Jan 2002
Location: Long Beach CA, the sewer by the sea.
Posts: 37,639
|
I've always maintained that if you want to watch (not under all circumstances, depends on what tools are being used) go ahead because I know what I'm doing and it doesn't make any difference.
But stay quiet. |
||
![]() |
|
Registered
|
Like Zeke says, stay quiet but keep your eyes open. You’ve been armed with plenty of info from the board to have a pretty good idea of what’s going on. I wonder if the techs are NATE certified? Years ago, I had my techs attend Carrier and Trane tech schools to learn how their equipment should be serviced including understanding a psychometric chart to properly charge a system. At least the hvac owner is standing by his installation and hopefully the issues will be resolved. Best of luck….
|
||
![]() |
|
Registered
Join Date: Mar 2005
Location: Northern CA
Posts: 4,703
|
Quote:
Re. psychometric chart - as I understand mini-split systems don't "use" the chart in the same way as standard AC. E.g. there appears to be only one tap (on the pressure side). My contractor has one person and that person lives ~2000 miles away, TX vs CA.
__________________
Sold: 1989 3.2 coupe, 112k miles |
||
![]() |
|
Registered
Join Date: Mar 2005
Location: Northern CA
Posts: 4,703
|
Minor update. The head guy from the contractor called and we discussed why sometimes people don't like to be watched/etc. So I guess all is going okay - I can still watch what they are doing bit I guess be careful what I say. I don't know - positive progress I guess.
__________________
Sold: 1989 3.2 coupe, 112k miles |
||
![]() |
|
FUSHIGI
Join Date: Feb 2006
Location: somewhere between here and there
Posts: 10,732
|
Taking over 2 months to correct their usual and customary installation strongly suggests nobody has taken them to the mat on their crappy work before.
__________________
Cults require delusions. |
||
![]() |
|
Registered
Join Date: Mar 2005
Location: Northern CA
Posts: 4,703
|
I've been reading about mini-splits and watching YouTube, there is a lot of info. out there. What I'm getting is... Mini-splits are a different animal compared to what installers worked on 20-30 years ago. They are less forgiving of poor installation practices that worked okay in the past. One guy on the HVACtalk forum, said residential work doesn't pay enough for us to do good work. My feeling is that someone that knows what they are doing can do correct work without too much more time/materials being used. For me, I'm willing to pay the additional amount but many probably go for the lowest bid. The issue is you don't know all this until you have selected your contractor and watched what they do.
__________________
Sold: 1989 3.2 coupe, 112k miles |
||
![]() |
|
Registered
Join Date: Mar 2005
Location: Northern CA
Posts: 4,703
|
I think some of you here are HVAC technicians or very interested so here is an update.
Their best technician came Friday Nov 17 to find out what is going on. Most if not all of the LED flashing codes indicated a low refrigerant level. So they decided to pull the charge and weigh it. It weighed 3.5lbs instead of 9,8lbs. So they (tech. phoned manager) concluded there is a leak. Pressurized with nitrogen to 600psig in attempt to find the leak(s). Hooked up a digital pressure gauge set Testo 550s. The pressure was dropping. Found a leaking flare fitting right at the outside unit. Checked all the coils and flare fittings at the inside units, using a sonic sniffer, and didn't find any leaks. Closed the isolation valves and hooked one tap on the Testo on the "machine" side and the other on the "house" side. This was a way to isolate where a leak might be if there is one remaining. Initially the machine side was dropping but we were in the afternoon and things were getting colder so not sure what is happening. I'll attach graphs for comment. Thanks. ![]() ![]()