Electrical fun at home

A few days ago, my 65" Vizio started randomly powering off on it's own. Every time I restarted it...it would be fine for a couple hours at least.
Yesterday, during the Lions game, it did it and wouldn't restart. I then noticed that other room lights were off also.
Checked the breakers...none tripped.
Took the the cover off of the breaker box and immediately saw a white wire melted and hanging open. Before I started to strip it down and re-attach it to the ground bar, I decided to check voltages.
120 at the breakers...good
100 at the white wire....wtf?? Where does it go if it's a hot wire??

I gave up on going any further....I called my local electrician at 8am today and he was here at 8:30
He said he sees that often. He just shut all the breakers off, stripped the white wire back and attached it to the ground bar. Flipped the breakers back and everything works.
He then took his screwdriver and torqued all the connections (breakers and ground bar) down extremely tight. He said it is a good idea to do that maybe every other year because they will work slightly loose on their own. He was only here for about 45 minutes.


I said everything worked..meaning all that didn't die in the process of the low and high voltage.
I lost my Sony A/V receiver, various light bulbs, portable phone and two handsets and my ECO robot vacuum.
Amazingly, the Vizio tv survived.

It could have been a lot worse...meaning a fire.

__________________
78 SC Targa Black....gone
84 Carrera Targa White
98 Honda Prelude
22 Honda Civic SI

Last edited by stevej37; 09-18-2023 at 01:18 PM..
Old 09-18-2023, 01:15 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #1 (permalink)
Back in the saddle again
 
masraum's Avatar
 
Join Date: Oct 2001
Location: Central TX west of Houston
Posts: 56,320
Wow! Glad it wasn't worse, because yeah, it could have been a lot worse. And I can only assume that if/once there's fire in a breaker box, things rapidly get worse.
__________________
Steve
'08 Boxster RS60 Spyder #0099/1960
- never named a car before, but this is Charlotte.
'88 targa SOLD 2004 - gone but not forgotten
Old 09-18-2023, 01:37 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #2 (permalink)
Registered
 
Join Date: Jan 2002
Location: west michigan
Posts: 26,897
I should have added...he said it usually starts with a loose screw on the ground bar and then it sparks over and over until it eventually gets the wire hot enough to melt itself and sometimes other wires that it is contact with.

I am def no electrician...but I learned a lot today.
__________________
78 SC Targa Black....gone
84 Carrera Targa White
98 Honda Prelude
22 Honda Civic SI

Last edited by stevej37; 09-18-2023 at 03:17 PM..
Old 09-18-2023, 01:43 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #3 (permalink)
Non Compos Mentis
 
Join Date: May 2001
Location: Off the grid- Almost
Posts: 10,607
Though minor, the connections in the breaker panel experience heat/cool cycles.
Over time, the heat/cool turns into expansion/contraction ever so slightly. Eventually, tight connections loosen.
Old 09-18-2023, 02:34 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #4 (permalink)
Evil Genius
 
Rusty Heap's Avatar
 
Join Date: May 2006
Location: On top of my BBQ
Posts: 5,650
Garage
as that is your line neutral, you could of had a "floating ground" as it wasn't really refenced to anything. You can see 100 vac on a line but there's no "work" or watts behind it.
__________________
Life is a big ocean to swim in.

Wag more, bark less.
Old 09-18-2023, 02:38 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #5 (permalink)
Registered
 
Join Date: Jan 2002
Location: west michigan
Posts: 26,897
The weird part of the whole thing is when the tv went off and the lights went out, I was checking other lights. When I would turn them on...they would get about half bright and slowly dim to nothing.
It was like they were running on batteries and they slowly died.....strange.

I always figured the ac power always on or off....no in between.
__________________
78 SC Targa Black....gone
84 Carrera Targa White
98 Honda Prelude
22 Honda Civic SI
Old 09-18-2023, 02:47 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #6 (permalink)
Registered
 
p911dad's Avatar
 
Join Date: Dec 2004
Location: Charlotte, NC
Posts: 2,332
Garage
What's the safest way to check a box for tight wire connections - trip the main breaker, then screw down each wire? Or call an electrician? Interesting. I thought the heat cycle affected the old aluminum wires but not the copper.
Old 09-18-2023, 02:58 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #7 (permalink)
Registered
 
Join Date: Jan 2002
Location: west michigan
Posts: 26,897
^^^ If you are careful...no need to trip the breakers. Just use a screwdriver that fits the bolt head good and has a good insulated handle. Lean into it and reef on it.

All of mine were loose enough that he got up to a full turn on them.
__________________
78 SC Targa Black....gone
84 Carrera Targa White
98 Honda Prelude
22 Honda Civic SI
Old 09-18-2023, 03:06 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #8 (permalink)
Registered
 
Join Date: Jan 2002
Location: west michigan
Posts: 26,897
Quote:
Originally Posted by Rusty Heap View Post
as that is your line neutral, you could of had a "floating ground" as it wasn't really refenced to anything. You can see 100 vac on a line but there's no "work" or watts behind it.
It gives a good spark/arc when touching it to anything....I found that out.
__________________
78 SC Targa Black....gone
84 Carrera Targa White
98 Honda Prelude
22 Honda Civic SI
Old 09-18-2023, 03:08 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #9 (permalink)
Registered
 
p911dad's Avatar
 
Join Date: Dec 2004
Location: Charlotte, NC
Posts: 2,332
Garage
Quote:
Originally Posted by stevej37 View Post
^^^ If you are careful...no need to trip the breakers. Just use a screwdriver that fits the bolt head good and has a good insulated handle. Lean into it and reef on it.

All of mine were loose enough that he got up to a full turn on them.
Thanks! Can't be too careful with that stuff.
Old 09-18-2023, 03:13 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #10 (permalink)
I see you
 
flatbutt's Avatar
 
Join Date: Nov 2002
Location: NJ
Posts: 29,933
Quote:
Originally Posted by stevej37 View Post
It gives a good spark/arc when touching it to anything....I found that out.
Any laundry damage?
__________________
Si non potes inimicum tuum vincere, habeas eum amicum and ride a big blue trike.
"'Bipartisan' usually means that a larger-than-usual deception is being carried out."
Old 09-18-2023, 03:22 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #11 (permalink)
Registered
 
Join Date: Jan 2002
Location: west michigan
Posts: 26,897
^^^ Luckily no.

I'll admit that I'm scared of electricity....I just don't understand it enough.
__________________
78 SC Targa Black....gone
84 Carrera Targa White
98 Honda Prelude
22 Honda Civic SI
Old 09-18-2023, 03:29 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #12 (permalink)
Evil Genius
 
Rusty Heap's Avatar
 
Join Date: May 2006
Location: On top of my BBQ
Posts: 5,650
Garage
You def had a floating ground.............voltage needs to be referenced to earth ground or your line neutral.

I'm a EE engineer. shrug.


Most puzzling troubleshooting was at my moms 50 year old house. Lights would dim and or burn out, depending on what appliance was on that circuit. Turned out a tree branch had rubbed through and broke the main power line neutral into the house. So we had a "floating" 220 vac circuit with nothing to reference to.

learned something new that day.
__________________
Life is a big ocean to swim in.

Wag more, bark less.
Old 09-18-2023, 03:35 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #13 (permalink)
Registered
 
Join Date: Jan 2002
Location: west michigan
Posts: 26,897
^^^ That sounds more serious than my 110 wire inside the breaker box.
__________________
78 SC Targa Black....gone
84 Carrera Targa White
98 Honda Prelude
22 Honda Civic SI
Old 09-18-2023, 03:38 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #14 (permalink)
I see you
 
flatbutt's Avatar
 
Join Date: Nov 2002
Location: NJ
Posts: 29,933
Is a loose white wire responsible for lights that occasionally flicker?
__________________
Si non potes inimicum tuum vincere, habeas eum amicum and ride a big blue trike.
"'Bipartisan' usually means that a larger-than-usual deception is being carried out."
Old 09-18-2023, 03:47 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #15 (permalink)
Registered
 
Join Date: Jan 2002
Location: west michigan
Posts: 26,897
Quote:
Originally Posted by flatbutt View Post
Is a loose white wire responsible for lights that occasionally flicker?
I'm going to say yes it could be, because I recall that happening in the last week before the circuit went. I thought at the time that the bulb was going bad...nothing else.

Others (Rusty Heap) would know better for certain.
__________________
78 SC Targa Black....gone
84 Carrera Targa White
98 Honda Prelude
22 Honda Civic SI

Last edited by stevej37; 09-18-2023 at 03:55 PM..
Old 09-18-2023, 03:51 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #16 (permalink)
Evil Genius
 
Rusty Heap's Avatar
 
Join Date: May 2006
Location: On top of my BBQ
Posts: 5,650
Garage
when in doubt, get your Fluke meter out, easy peasy. Even upper end Harbor Freight models are your friend when troubleshooting.........


here you go, good explanation. Simple, short words in small sentences, even Steves Turtles could fix it, but they'd be slow..........


https://electricaliq.com/what-is-floating-neutral-effects-how-to-test-fix/#:~:text=Floating%20neutral%20is%20a%20condition%2 C%20in%20which%20the,neutral%20wire%20is%20permane ntly%20grounded%20to%20the%20earth.
__________________
Life is a big ocean to swim in.

Wag more, bark less.

Last edited by Rusty Heap; 09-18-2023 at 04:20 PM..
Old 09-18-2023, 04:17 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #17 (permalink)
Evil Genius
 
Rusty Heap's Avatar
 
Join Date: May 2006
Location: On top of my BBQ
Posts: 5,650
Garage
a Nice Fluke meter really isn't "that" expensive and it'll last you a life time...........I used to work at Fluke assembling these.......

https://www.ebay.com/sch/i.html?_from=R40&_trksid=p4432023.m570.l1313&_nkw=fluke+77&_sacat=0
__________________
Life is a big ocean to swim in.

Wag more, bark less.
Old 09-18-2023, 04:23 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #18 (permalink)
 
Registered
 
Bill Douglas's Avatar
 
Join Date: Jun 2000
Location: bottom left corner of the world
Posts: 22,805
The tenants in a rental talked about the electricity being "a bit weird". Lots of energy saver bulbs dying etc.

I checked it with the multimeter (240 volt supply around here) and it would go from 258 to about 100 volts, and anywhere in between. I called the electricity supply company and the guy said at the box out by the front gate where my house meets the underground, the wires were actually loose. Brown outs is the term I believe. Now it's fine and I still get between 240 and 258 which everything is OK with
Old 09-18-2023, 04:24 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #19 (permalink)
Registered
 
Join Date: Jan 2002
Location: west michigan
Posts: 26,897
Quote:
Originally Posted by Bill Douglas View Post
The tenants in a rental talked about the electricity being "a bit weird". Lots of energy saver bulbs dying etc.

I checked it with the multimeter (240 volt supply around here) and it would go from 258 to about 100 volts, and anywhere in between. I called the electricity supply company and the guy said at the box out by the front gate where my house meets the underground, the wires were actually loose. Brown outs is the term I believe. Now it's fine and I still get between 240 and 258 which everything is OK with



Sounds exactly like my case.
I'm surely going to make a habit of checking the wires every year or so.

__________________
78 SC Targa Black....gone
84 Carrera Targa White
98 Honda Prelude
22 Honda Civic SI
Old 09-18-2023, 04:30 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #20 (permalink)
Reply


 


All times are GMT -8. The time now is 02:40 PM.


 
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2025, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2025 Pelican Parts, LLC - Posts may be archived for display on the Pelican Parts Website -    DMCA Registered Agent Contact Page
 

DTO Garage Plus vBulletin Plugins by Drive Thru Online, Inc.