I got a heater for garage. Runs ion 220 and says 20 amps. I installed and it works fine. Question, friend told me to use 30 amp breaker. That seem right?
Thanks.

Old 12-05-2024, 04:45 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #1 (permalink)
Platinum Member
 
dad911's Avatar
 
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 20,996
The breaker protects the wire not the heater. What size wire did you run?

12awg=20A, 10awg =30A
__________________
The truth is that while those on the left - particularly the far left - claim to be tolerant and welcoming of diversity, in reality many are quite intolerant of anyone not embracing their radical views. - Charlie Kirk
Old 12-05-2024, 04:48 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #2 (permalink)
Registered
 
Join Date: Apr 2015
Posts: 1,416
10 awg
Old 12-05-2024, 05:08 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #3 (permalink)
Registered
 
Join Date: May 2006
Posts: 210
Garage
While 12AWG is rated at 20A, you are only allowed to use 80% of that (16A). Your 10AWG is rated at 30A, 80% is 24A. Protecting the 10AWG wire with a 20A CB is allowed, you can always put in a 30A CB if it starts tripping.
Old 12-05-2024, 05:43 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #4 (permalink)
Registered
 
Join Date: Apr 2015
Posts: 1,416
Perfect thanks everyone. It will be nice to finally have heat at the hit of a switch.
Old 12-05-2024, 05:48 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #5 (permalink)
Registered
 
Join Date: Mar 2004
Location: La Crosse, WI
Posts: 1,346
Quote:
Originally Posted by schwarz633 View Post
While 12AWG is rated at 20A, you are only allowed to use 80% of that (16A). Your 10AWG is rated at 30A, 80% is 24A. Protecting the 10AWG wire with a 20A CB is allowed, you can always put in a 30A CB if it starts tripping.
Expanding on this a little. I found out from our electricians at work is you should only run the breaker at 80% as well. Running higher than that shortens the life of the breaker, worst case it won't trip when it needs to.

We had a 100a 3 phase running in the low 90's. Running a row of racks in a data center. We had to get creative and feed a couple of the racks from another source.

TL;DR, if you have 10g wire, and the heater does consistently draw 20a when running, use a 30a breaker. Just because it says 20a on the label doesn't mean it actually pulls 20a.
Old 12-05-2024, 06:20 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #6 (permalink)
 
Registered
 
Bill Douglas's Avatar
 
Join Date: Jun 2000
Location: bottom left corner of the world
Posts: 22,765
80%, that sounds like a good game plan.

There are breakers designed for things like compressors which require a big current for a moment when they fire up, then not much after that. These can be handy for situations where it trips too often. Electrician said I needed one for my compressor + plasma cutter but I said no thanks as it has never tripped.

but it could work in your situation if it's tripping often.

Old 12-05-2024, 06:39 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #7 (permalink)
Reply


 


All times are GMT -8. The time now is 10:21 AM.


 
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2025, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2025 Pelican Parts, LLC - Posts may be archived for display on the Pelican Parts Website -    DMCA Registered Agent Contact Page
 

DTO Garage Plus vBulletin Plugins by Drive Thru Online, Inc.