 Attn Sparky:  Need subpanel tips 
		
		
		I'm putting a 60amp sub in my garage and I've run the conduit and I'm about ready to pull 4 #6 leads.  2 hot, 1 neutral, 1 grounded to main. 
	Do I need to install a separate ground rod at the sub location or is gounding to the main enough? All leads are insulated. Should the ground be bare? There will be a hot water tank in the garage. Is there any reason why I cannot put the sub box near the H2O tank? - like within a foot or two. Any other suggestions on box location? Or things I should look out for? Thanks.  | 
		
 How far is the sub from the main? You shouldnt need a seperate grounding rod. Then again check your local codes also 
	 | 
		
 Sub is 40 feet from the main. 
	 | 
		
 When I built my garage, I had to run a ground wire X (I think 15) feet through the foundation, IIRC this is called "Ufer" (sp?) ground.  You will also need a grounding bar in the sub panel.  If the "ufer" ground isn't possible (ie existing structure) then I think you'd need to drive a rod.  An electrician gave me an explanation of why this was necessary, and it sounded good, but I can't recall it with enough detail to repeat it. 
	In this picture, the larger of the two grounds goes into the foundation, the other goes to the main panel. http://www.rennlight.com/shop/image/2100302.JPG  | 