Pelican Parts
Parts Catalog Accessories Catalog How To Articles Tech Forums
Call Pelican Parts at 888-280-7799
Shopping Cart Cart | Project List | Order Status | Help



Go Back   Pelican Parts Forums > Miscellaneous and Off Topic Forums > Off Topic Discussions


Reply
 
LinkBack Thread Tools Rate Thread
Author
Thread Post New Thread    Reply
Detached Member
 
Hugh R's Avatar
 
Join Date: May 2003
Location: southern California
Posts: 26,964
Check my assumptions-CFL floodlights for the Backyard

I have a really big backyard and am thinking about CFL floodlights, 120 volt, not low voltage. Too much voltage drop for the distances I want to run for 12v. I want to uplight some oak trees and really see the lights from the house which could be several hundred feet away.

Currently, I have a dedicated 15 amp breaker going to ten lights around the pool with 60 watt incandescent bulbs which is 600 watts, or about 5 amps, excluding line losses. They are all in a loop meaning the wires go from one light to the next. . I want to tap into one existing light in the middle of the loop and run outdoor-rated flex out and branch out to about 8 CFL outdoor fixtures.

The CFL's that are equivalent to a regular 75 watt incandescent are 18 watts, so 8 x 18 = 144 watts, if I convert the existing ten 60 watt bulbs to CFL's as well then I'm looking at 140 watts (they're 14 watt CFLs), and thus about 284 watts total, or around 2-1/4 amps, plus voltage drop on about 300 feet of outdoor wiring. It looks like I'll be well under the load rating of the 15 amp breaker. Any thoughts? Are my assumptions correct?

__________________
Hugh
Old 01-01-2009, 03:11 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #1 (permalink)
Registered
 
Eric Coffey's Avatar
 
Join Date: Nov 2000
Location: AZ
Posts: 8,414
The only thing I would add is that some of the CFL-to-incandescent equivalency ratings seem to be a bit optimistic regarding lumens/output. In other words, those 14w CFL's are probably closer to 40w incandescent. To equal a 60w incandescent, you probably need a 20w+ CFL.
Old 01-01-2009, 05:12 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #2 (permalink)
Detached Member
 
Hugh R's Avatar
 
Join Date: May 2003
Location: southern California
Posts: 26,964
Thanks Eric, but even with that, I think I'm still well under the rating of the breaker. I never did this project because the wattage to get some decent lumens in the trees always seemed to dictate a bigger breaker, hence maybe a subpanel. But with the CFL's it looks like it's definitely doable.
__________________
Hugh
Old 01-01-2009, 06:45 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #3 (permalink)
Registered
 
Join Date: Mar 2005
Location: Jersey Shore
Posts: 1,084
Garage
dude, given the values you have stated your voltage drop should be 2.1 A and using a given of 120v we then apply ohms law.
248/117.9=2.1
2.1 is definately within the 80% allowed of 15

hope this helps
__________________
Chris
the more i learn, the less i know
Old 01-01-2009, 08:24 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #4 (permalink)
Used to be Singpilot...
 
Join Date: Oct 2006
Location: Sioux Falls, SD is what the reg says on the bus.
Posts: 1,867
Hugh;

I just changed everything in the house over to CFL's. Did not change the dimmables, but I see now that there even models for that.

I discovered two 'surprises'. The lumens on the 100 and 120 watt comparable ones are probably brighter than described. The lower lumens are close to, or even 'conservative' on brightness.

Second discovery. When cold, they start after a 2 second or so delay, and come on very dim, rising to full luminescence after a minute or so.

The only other consideration would be waterproofing; they are not rated 'outdoor' unless specifically stated. Some of the larger flood-looking ones have base up or down restrictions, and some seem to run fairly warm, not the bulb part, but the transformer / starter part. Check bulb dimensions carefully if going into an enclosure. The CFL's are sometimes longer, especially the larger 'flood' types.

My electrical consumption is noticibly down. PG&E paid a fair share of the changeover costs, I'd say 15% or so.

Last edited by fingpilot; 01-01-2009 at 08:33 PM..
Old 01-01-2009, 08:30 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #5 (permalink)
Detached Member
 
Hugh R's Avatar
 
Join Date: May 2003
Location: southern California
Posts: 26,964
Cool, thanks guys.
__________________
Hugh
Old 01-02-2009, 08:24 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #6 (permalink)
 
Registered
 
competentone's Avatar
 
Join Date: Mar 2004
Location: Summerville, SC
Posts: 2,057
Quote:
Originally Posted by Hugh R View Post
Currently, I have a dedicated 15 amp breaker going to ten lights around the pool with 60 watt incandescent bulbs which is 600 watts, or about 5 amps, excluding line losses. They are all in a loop meaning the wires go from one light to the next. . I want to tap into one existing light in the middle of the loop and run outdoor-rated flex out and branch out to about 8 CFL outdoor fixtures.

The CFL's that are equivalent to a regular 75 watt incandescent are 18 watts, so 8 x 18 = 144 watts, if I convert the existing ten 60 watt bulbs to CFL's as well then I'm looking at 140 watts (they're 14 watt CFLs), and thus about 284 watts total, or around 2-1/4 amps, plus voltage drop on about 300 feet of outdoor wiring. It looks like I'll be well under the load rating of the 15 amp breaker. Any thoughts? Are my assumptions correct?
I'm no electrician, but are the new fixtures designed to only accept the CFLs?

If you are using standard flood light fixtures that can support standard flood bulbs is it acceptable (code), or advisable to have a circuit that could be overloaded by someone simply swapping the CFL bulb (18 of them, if I'm understanding your description) with larger (100+ watt) bulbs?
Old 01-02-2009, 04:08 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #7 (permalink)
Detached Member
 
Hugh R's Avatar
 
Join Date: May 2003
Location: southern California
Posts: 26,964
Good point compentenone, I'll check my calcs, but I'm pretty sure that I'd still be way under. The new lights can only take the CFL bulbs, and if someone load up the other ten with 60 watters, I'd still be under. The turning point for me doing this now, not ten years ago was the advent of inexpensive CFL. I wouldn't have the load capacity running a bunch more 60 or 100 watt floodlights out there.

__________________
Hugh
Old 01-02-2009, 04:47 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #8 (permalink)
Reply


 


All times are GMT -8. The time now is 11:11 AM.


 
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2025, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2025 Pelican Parts, LLC - Posts may be archived for display on the Pelican Parts Website -    DMCA Registered Agent Contact Page
 

DTO Garage Plus vBulletin Plugins by Drive Thru Online, Inc.