canna change law physics
 
red-beard's Avatar
 
Join Date: Jul 2000
Location: Houston, Tejas
Posts: 43,366
Garage
The advantage of recycling the air is that you will remove the moisture in the air, dehumidifying as well as cooling. Constantly running "new" air will add moisture to the system, and if humid enough, may lead to freeze up of the coils.

You're pretty close to the water there (what? 2 miles?) so you may be getting more moisture than you think. A cheap bulk polymer humidity sensor would tell you for sure.

His hot air thing sounds like hot air to me. Cost shouldn't be any different. You are cooling office air, and running that into the shop. So you are pulling fresh air into the offices. I think with the recycle, you'll be more efficient, lower cost.

Cooling air is 1/3 the cost of removing moisture. The heat of vapoization of water is high! Look of the low pressure charts on the steam tables.

__________________
James
The pessimist complains about the wind; the optimist expects it to change; the engineer adjusts the sails.- William Arthur Ward (1921-1994)
Red-beard for President, 2020

Last edited by red-beard; 06-18-2009 at 08:40 PM..
Old 06-18-2009, 08:37 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #1 (permalink)
Registered
 
Eric Coffey's Avatar
 
Join Date: Nov 2000
Location: AZ
Posts: 8,414
Certainly no expert, but I think a closed-loop system would be more efficient. Also, aren't most A/C systems designed to function best with certain warm/cold "split" temps? Maybe he's saying instead of having an exhause fan, that it should be a (filtered) air-return? I'd certainly get a second opinion.
Old 06-18-2009, 08:40 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #2 (permalink)
Run smooth, run fast
 
Heel n Toe's Avatar
 
Join Date: Aug 2008
Location: South Carolina
Posts: 13,447
Wayne, as you know, everything about the way these systems are set up with where the returns and the vents are and how big they are is critical to operating efficiency and performance.

Would it be possible to get a second opinion from another company, or are you on contract with this guy? Or would he be offended?

A second set of eyes might be your answer.

And if you think your guy might be offended if he knew you got another guy to look at it, just request that #2 guy come by after hours in an unmarked vehicle/his own car and do a walk through.
__________________
- John
"We had a band powerful enough to turn goat piss into gasoline."
Old 06-18-2009, 08:50 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #3 (permalink)
Registered
 
chapo's Avatar
 
Join Date: Aug 2003
Posts: 1,401
The only way it will freeze up is if it runs all the time, or for very long times. Compressors freeze up all the time in Lake Havasu at 110 degrees because they always run.
__________________
Patrick
Old 06-18-2009, 09:00 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #4 (permalink)
Registered
 
Join Date: May 2002
Location: St Louis
Posts: 4,211
So your AC guy is saying that continuously cooling the dry, 65 degree air allows the evaporator to drop below freezing?
__________________
Rick
88 Cab
Old 06-18-2009, 09:35 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #5 (permalink)
Run smooth, run fast
 
Heel n Toe's Avatar
 
Join Date: Aug 2008
Location: South Carolina
Posts: 13,447
Quote:
Originally Posted by Wayne at Pelican Parts View Post
It picks up the supply air on the other side of the building, cools it, and then deposits it into the server room. Then, the warm air is sucked out of the room using a ceiling exhaust fan. This air goes into the warehouse.
Quote:
Originally Posted by Wayne at Pelican Parts View Post
If the air in the warehouse (where the A/C unit is sucking in air) is very cool (say 60 degrees or so)
In the first paragraph above, you seem to be saying that the warm air in the server room is sent to the warehouse...

...then you seem to be saying that the return for the server room's A/C is also in the warehouse... but after having read everything you've said, it's from a cool area in the warehouse. The same warehouse, right?

At any rate, this is definitely beyond my abilities, but I know you need for the system to cause the humidity in that server room to be as low as possible... or perhaps within certain limits.

So, I recommend the second opinion approach. You're gonna want someone who is not only knowledgeable, but who doesn't mind answering all your questions. Get a recommendation from another businessman you know in the area who has a similar setup... at least an office area and a warehouse area in the same building... sounds like that's what you have.
__________________
- John
"We had a band powerful enough to turn goat piss into gasoline."

Last edited by Heel n Toe; 06-18-2009 at 09:43 PM..
Old 06-18-2009, 09:40 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #6 (permalink)
 
Registered
 
Join Date: Oct 2000
Location: Nearby
Posts: 79,768
Garage
Send a message via AIM to fintstone
They will freeze up when they run constantly and if/when there is insufficient air flow based on the size of inlet or outlet (including a fouled or too restrictive filter). The really thick or dense filters will almost aways cause this...and changing to a less efficient one will often be enough to fix the problem.
__________________
74 Targa 3.0, 89 Carrera, 04 Cayenne Turbo
http://www.pelicanparts.com/gallery/fintstone/
"The problem with socialism is that you eventually run out of other people's money"
Some are born free. Some have freedom thrust upon them. Others simply surrender

Last edited by fintstone; 06-18-2009 at 09:59 PM..
Old 06-18-2009, 09:50 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #7 (permalink)
Registered
 
Eric Coffey's Avatar
 
Join Date: Nov 2000
Location: AZ
Posts: 8,414
Quote:
Originally Posted by Wayne at Pelican Parts View Post
I think that would be the case if there wasn't significant heat generation going on. I think that's what he thinks too, but the role of the servers (there are about 18 computers in there) change the whole equation. In his recommendation, I'd be pulling out 80-degree air. In my setup, we're pulling air that is about 65 degrees.

-Wayne
Yeah, I'm thinking closed-loop as in: the air in the room IS the air you are pulling back in and re-cooling (just have a filter somewhere in the loop). Just like the forced-air (closed-loop) system you would have in your house.
Old 06-18-2009, 09:58 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #8 (permalink)
Cogito Ergo Sum
 
Join Date: Jul 2007
Posts: 29,791
Garage
I would think the closed loop would be cleaner. Even with a good filter some dust could be getting by. Isn't dust the enemy for computers ?
Old 06-18-2009, 10:35 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #9 (permalink)
Information Junky
 
island911's Avatar
 
Join Date: Mar 2001
Location: an island, upper left coast, USA
Posts: 73,189
Quote:
Originally Posted by fintstone View Post
They will freeze up when they run constantly and if/when there is insufficient air flow based on the size of inlet or outlet (including a fouled or too restrictive filter). The really thick or dense filters will almost always cause this...and changing to a less efficient one will often be enough to fix the problem.
Yeah, I was going to suggest an array o' cool collar, but I suppose a K&N filter ought to do just as well.

Seriously, I've got to agree with finstone; increasing the airflow will transfer more heat to the coils. (stop the freeze)
__________________
Everyone you meet knows something you don't. - - - and a whole bunch of crap that is wrong.
Disclaimer: the above was 2¢ worth.
More information is available as my professional opinion, which is provided for an exorbitant fee.
Old 06-18-2009, 11:05 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #10 (permalink)
Information Junky
 
island911's Avatar
 
Join Date: Mar 2001
Location: an island, upper left coast, USA
Posts: 73,189
I'll just add that your guy is right, that feeding the cold side warmer air will help stop the freezing, but you are certainly right that there is a more efficient solution.
__________________
Everyone you meet knows something you don't. - - - and a whole bunch of crap that is wrong.
Disclaimer: the above was 2¢ worth.
More information is available as my professional opinion, which is provided for an exorbitant fee.
Old 06-18-2009, 11:17 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #11 (permalink)
Detached Member
 
Hugh R's Avatar
 
Join Date: May 2003
Location: southern California
Posts: 26,964
Wayne, certainly no expert here, but if your pulling already cooled air in, you compressor works less. Icing up is on the evaporator occurs from a less than 32 degree temp at the evaporator. Cooler air has less moisture than warm air. So less moisture from cooled air = less icing. One of the ways A/C works best is to recirculate already cooled air. The question is "Is the air from the server room warmer than the air outside?" Given where you are located, you should have a "smart" system that will pull makeup air from the coolest place. Winter outdoors, summer maybe from the server room.
__________________
Hugh

Last edited by Hugh R; 06-18-2009 at 11:44 PM..
Old 06-18-2009, 11:25 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #12 (permalink)
 
Information Junky
 
island911's Avatar
 
Join Date: Mar 2001
Location: an island, upper left coast, USA
Posts: 73,189
Quote:
Originally Posted by Hugh R View Post
. So less moisture from cooled air = less icing. ...
That part isn't quite right. (tho it may seem intuitive)

When air has more moisture it carries more heat-energy, and will take more energy to freeze. (Latent heat and all) Think of it this way; let's say there is ice already on the coils ... what will break the ice faster, room-temp super dry air, or room temp garden hose water?

So, with wet air, condensation may build faster but all that moisture imparts a lot of heat to the cold coils. That is, wet air will take longer to freeze than drier air. (...for a given air flow you'll have more mass flow & latent heat with additional water in the mix)
__________________
Everyone you meet knows something you don't. - - - and a whole bunch of crap that is wrong.
Disclaimer: the above was 2¢ worth.
More information is available as my professional opinion, which is provided for an exorbitant fee.

Last edited by island911; 06-18-2009 at 11:56 PM..
Old 06-18-2009, 11:46 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #13 (permalink)
Unconstitutional Patriot
 
turbo6bar's Avatar
 
Join Date: Apr 2000
Location: volunteer state
Posts: 5,620
Based on your last post describing a system that has worked well for several years, I'd say you may have an undercharged system or dirty evaporator coil reducing airflow. What type of filtration are you using? Are the filters changed regularly?
jurgen
Old 06-19-2009, 03:42 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #14 (permalink)
Registered
 
Join Date: Apr 2005
Location: outta here
Posts: 53,066
I can't diagnose this system from across the country but I agree with turbo6bar, in that your current problem is most likely not due to the design.

However, depending upon where your thermostat is located, and given a higher than normal supply air temperature, it might be possible that the compressor may run a long time. I'd suggest having a mechanical engineer (as opposed to a contractor) take a look at how your system is installed, to see if there might be a better way to do it. I have installed a bunch of systems in server rooms and telephone switches and we never use outside air, primarily as we are also needing to control the humidity within a narrrow range.

JR
Old 06-19-2009, 04:46 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #15 (permalink)
Registered
 
Join Date: Oct 2006
Location: So-Cal
Posts: 428
In my experience freezing up is caused by not enough air flow (ie:dirty filter, not enough incoming air flow) if it used to work, that is my guess. The air in and out to the warehouse I don't think it maters on the freezing . It is probably more efficient to run closed loop because you are trying to cool the already pre or cooled air, it would take less energy to cool the already cooled air plus you get the benefit of removing the humidity and not introducing more moisture.
__________________
1987 Carrera
Old 06-19-2009, 05:02 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #16 (permalink)
Unoffended by naked girls
 
dhoward's Avatar
 
Join Date: Sep 2002
Location: St. Charles, MO
Posts: 5,894
Garage
Send a message via AIM to dhoward
If it worked for several years before. It's not a design issue.
That's the lazy way out.
Low airflow or undercharge.
__________________
Dan
1969 911T (sold)
2008 FXDL
www.labreaprecision.com
www.concealedcarrymidwest.com
Old 06-19-2009, 07:13 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #17 (permalink)
Registered
 
pete3799's Avatar
 
Join Date: Nov 2008
Location: Vermont
Posts: 7,431
Garage
No expert here but seems like your compresor would run less if you recuirculate the air inside the room (draw already cooled air) than drawing outside air.
__________________
Pete
79 911SC RoW
"Tornadoes come out of frikkin nowhere. One minute everything is all sunshine and puppies the next thing you know you've got flying cows".- Stomachmonkey
Old 06-19-2009, 07:42 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #18 (permalink)
Unconstitutional Patriot
 
turbo6bar's Avatar
 
Join Date: Apr 2000
Location: volunteer state
Posts: 5,620
Quote:
Originally Posted by pete3799 View Post
No expert here but seems like your compresor would run less if you recuirculate the air inside the room (draw already cooled air) than drawing outside air.
That would depend on the sensible and, to some extent, latent head loads. Without knowing the conditions of the server room AND warehouse space, it's pure wild-ass guessing. You could be entirely correct, though.
Old 06-19-2009, 08:37 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #19 (permalink)
Registered
 
T77911S's Avatar
 
Join Date: Oct 2006
Location: MYR S.C.
Posts: 17,321
if you are pulling air from another room, you are putting a vacuum on that room, i bet the doors dont need closers. so, you are putting a load on that system. it is trying to draw air into it, and it is providing air to another room.

the server room. this unit is icing because it has cool air going into the evap. the system is deigned to remove heat from the air, so if air going into the system is ALREADY cool, there is effectively no heat load on that system even though the room is getting warm. with the unit running and no heat load, it will/may ice up.

you may connsider just running another supply and return from where you are getting the cold air now to cool the server room and use the server unit as a backup. set the T stat to auto and about 5 degrees higher than what you want and as needed, itwill come on.
i dont know what type your big system is, but you could even put a damper controlled by a Tstat in the server room to keep it cool. keeping the server ac sys off would save the system and money.

__________________
86 930 94kmiles [__] RUNNING:[__] NOT RUNNING: ____77 911S widebody: SOLD
88 BMW 325is 200K+ SOLD
03 BMW 330CI 220K:: [__] RUNNING: [__] NOT RUNNING:
01 suburban 330K:: [__] RUNNING: [__] NOT RUNNING:
RACE CAR:: sold
Old 06-19-2009, 09:11 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #20 (permalink)
Reply


 


All times are GMT -8. The time now is 11:36 PM.


 
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2025, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2025 Pelican Parts, LLC - Posts may be archived for display on the Pelican Parts Website -    DMCA Registered Agent Contact Page
 

DTO Garage Plus vBulletin Plugins by Drive Thru Online, Inc.