Replace cloth-wrapped wiring in conduit?

I've replaced the outdoor electrical service for my house.

My next electrical task -may be- to replace the old waxy-cloth covered wiring inside the house.

All the wiring inside the house is (i'm guessing) a mid-20th century upgrade. All conduit, all the time. Inside the conduit are said waxy-cloth wires.

So . . . . What say you? Do I need to replace this wiring if it's not 'broken?"

If so, can I just remove it and shove some romex through the conduit? (if it will fit)

I like the conduit, actually. The walls are plaster and lathe, so just shoving new wiring through the conduit is a quick and easy idea, if that's acceptable.

thanks

__________________
1983 SC Coupe
1963 BMW R60/2
1972 Triumph Tiger
1995 Triumph Daytona SuperIII
Old 11-22-2013, 09:33 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #1 (permalink)
Registered
 
porwolf's Avatar
 
Join Date: May 2011
Posts: 7,245
Why not pull single wires through the conduit? Smaller diameter, less friction.
__________________
79 SC Targa
72 T Targa Sold
68 T Coupe Sold
65 912 Coupe Sold
62 356B Coupe Sold
Old 11-22-2013, 09:39 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #2 (permalink)
Registered
 
Bill Douglas's Avatar
 
Join Date: Jun 2000
Location: bottom left corner of the world
Posts: 22,699
OH sh it. Excuse me. Whatever you do, you have to replace that stuff.
Old 11-22-2013, 10:42 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #3 (permalink)
Cogito Ergo Sum
 
Join Date: Jul 2007
Posts: 29,791
Garage
Yes replace, but pull three singles through, no Romex. The first curve you get to you wil HATE pulling the Romex!

Cheaper too!

Your best bet to pull will be to make a hook in the end of the existing and tie a loop in some string. Then tape the loop closed with a little taper up the wire to make it easy. Pull the string through, then pull the string through with the new wire done the same way.


I'll let someone more experienced recommend the wire, we tend to run everything in 10 or 12ga THHN stranded since that's what we have to use to run up sign poles.

Last edited by porsche4life; 11-22-2013 at 11:02 PM..
Old 11-22-2013, 10:53 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #4 (permalink)
Hell Belcho
 
Nostril Cheese's Avatar
 
Join Date: Sep 2006
Location: Oz
Posts: 9,249
Quote:
Originally Posted by porsche4life View Post
Yes replace, but pull three singles through, no Romex. The first curve you get to you wil HATE pulling the Romex!

Cheaper too!
This man speaks the truth.
__________________
Saved by the buoyancy of citrus.
Old 11-22-2013, 11:03 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #5 (permalink)
Registered
 
Join Date: Mar 2004
Location: Los Angeles
Posts: 17,317
Absolutely not Romex through conduits.

Use fish tape, hook wire to it and pull through. Having Conduits are much better then Romex. Why do you think you need to replace the cloth wiring? If you have conduit, then it isn't knob and tube (1920s). your existing wires inside the conduit should not heve cloth sheathing on it. Take a pic of it for us will ya? Maybe its that way in Colorado back then. My building restoration experience is limited to so cal.
Old 11-23-2013, 01:08 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #6 (permalink)
 
Used Up User
 
imcarthur's Avatar
 
Join Date: Jun 2003
Location: Toronto
Posts: 8,311
Garage
Quote:
Originally Posted by porsche4life View Post
Your best bet to pull will be to make a hook in the end of the existing and tie a loop in some string. Then tape the loop closed with a little taper up the wire to make it easy. Pull the string through, then pull the string through with the new wire done the same way.


I'll let someone more experienced recommend the wire, we tend to run everything in 10 or 12ga THHN stranded since that's what we have to use to run up sign poles.
This is the 'correct' method. 14 ag THHN/THWN would be sufficient for 15A circuits although 12 ga would give you extra amperage. Pull 3 wires - black/white/green representing hot/neutral/ground. The conduit is often used as a ground but that relies on metal to metal contacts which may or may not be there hidden in the wall. The old thick cloth/paper insulation was wrapped around a rubber core of insulation on the wire so it is safe as long as it is terminated properly.

Ian
__________________
'87 Carrera Cab

----- “Only two things are infinite, the universe and human stupidity, and I'm not sure about the former.” A. Einstein -----

Last edited by imcarthur; 11-23-2013 at 04:56 AM..
Old 11-23-2013, 04:48 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #7 (permalink)
Parrothead member
 
VINMAN's Avatar
 
Join Date: Jul 2003
Location: Monmouth county, NJ USA
Posts: 13,820
No romex through conduit! Also conduit is not legal to use as a ground conductor. You have to run a separate ground.
__________________
Vinny
Red '86 944, 05 Ford Super Duty Dually '02 Ram 3500 Diesel 4x4 Dually, '07Jeep Wrangler '62 Mercury Meteor '90 Harley 1200 XL
"Live your Life in such a way that the Westboro Baptist Church will want to picket your funeral."
Old 11-23-2013, 05:02 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #8 (permalink)
Registered
 
peppy's Avatar
 
Join Date: Aug 2007
Location: Kenbridge VA
Posts: 4,267
Is this what you have?



If the wires are not damaged then they do not need to be replaced, they should be solid copper.

In our home the only wires that I have trouble with are ones in the ceilings. The heat from the lights breaks down the rubber insulation. I would concentrate more on running new circuits to places that you need more power, like bathrooms and kitchens.

Pulling wires through bx can be done but 3/12awg wires is a tight fit, and all bx ends need bushings in them.

This is all based on you having bx. If you have normal conduit it's a lot easier.
__________________
Peppy
2011 BMW 335d
1988 Targa 3.4
2001 Jetta TDI dead
1982 Chevette Diesel SOLD
Old 11-23-2013, 05:42 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #9 (permalink)
Registered
 
Join Date: Jul 2001
Location: St. Louis, MO
Posts: 3,092
Garage
Quote:
Originally Posted by Gogar View Post
The walls are plaster and lathe, so just shoving new wiring through the conduit is a quick and easy idea
This is my favorite part of your question.

Quick and easy, as a part of home remodeling, is a surprise event - not a planned one. I've been rehabbing on and off for 25 years. I can count the quick and easy projects on my fingers. They usually cost twice as much and take 4 times as long.

Of course I am figuring in the many trips to the hardware store. Its tough to get everything in one trip. Every trip to HD usually starts with a stop at the return counter because you always buy more than you need in an attempt to eliminate another visit. Seldom works for me.
__________________
Randy
'87 911 Targa
'17 Macan GTS
Old 11-23-2013, 06:08 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #10 (permalink)
Band.
 
Join Date: Dec 2003
Location: Denver, CO
Posts: 13,312
Send a message via AIM to Gogar
Thanks, Dudes! Single wires it is!

Quote:
Originally Posted by look 171 View Post
Having Conduits are much better then Romex. Why do you think you need to replace the cloth wiring? If you have conduit, then it isn't knob and tube (1920s). your existing wires inside the conduit should not heve cloth sheathing on it. Take a pic of it for us will ya? Maybe its that way in Colorado back then. My building restoration experience is limited to so cal.
Quote:
Originally Posted by peppy View Post
Is this what you have?



If the wires are not damaged then they do not need to be replaced, they should be solid copper.
Nope, it's not the that it's the other stuff.



This house had knob and tube and got 'updated' to the nice, big, non-flexible conduit sometime.

The wiring seems 'fine', except like Peppy here and there in overhead boxes where the heat has broken down the cloth.


Quote:
Originally Posted by VINMAN View Post
No romex through conduit! Also conduit is not legal to use as a ground conductor. You have to run a separate ground.
The conduit serves as the ground right now.
Do I leave it or should I pull a green wire because I'm in there?

Thanks!
__________________
1983 SC Coupe
1963 BMW R60/2
1972 Triumph Tiger
1995 Triumph Daytona SuperIII
Old 11-23-2013, 06:12 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #11 (permalink)
Registered
 
craigster59's Avatar
 
Join Date: Aug 2004
Location: Gilbert, Az
Posts: 21,655
Garage
Pull 3 wires, 12g preferred. If the existing wire is copper, you might just want to leave it. If it's aluminum, it definitely needs replacing. Just put a grounding rod near the panel for your ground.
__________________
---------------------------------------------------------------------------

"There is nothing to be learned from the second kick of a mule" - Mark Twain

Last edited by craigster59; 11-23-2013 at 06:15 AM..
Old 11-23-2013, 06:13 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #12 (permalink)
Registered
 
Join Date: May 2002
Location: St Louis
Posts: 4,211
If it that BX armored cable like peppy showed there is no way you are going to get just the wires out of there. I would guess that wiring dates to the 30's or 40's.

If the rubber is not deteriorated why not just leave it and make sure you have the right ground fittings on the jacket?

Quote:
Originally Posted by Gogar View Post
I like the conduit, actually. The walls are plaster and lathe, so just shoving new wiring through the conduit is a quick and easy idea, if that's acceptable.
__________________
Rick
88 Cab
Old 11-23-2013, 06:14 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #13 (permalink)
Registered
 
911_Dude's Avatar
 
Join Date: Dec 2001
Location: Ky, USA
Posts: 1,127
Quote:
Originally Posted by gr8fl4porsche View Post

Quick and easy, as a part of home remodeling, is a surprise event - not a planned one. I've been rehabbing on and off for 25 years. I can count the quick and easy projects on my fingers. They usually cost twice as much and take 4 times as long.

Of course I am figuring in the many trips to the hardware store. Its tough to get everything in one trip. Every trip to HD usually starts with a stop at the return counter because you always buy more than you need in an attempt to eliminate another visit. Seldom works for me.
So true. I now pick my rehabs/flips that are relatively close to a HD or Lowes. Each project takes at least 2-3 trips.
Old 11-23-2013, 06:14 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #14 (permalink)
Band.
 
Join Date: Dec 2003
Location: Denver, CO
Posts: 13,312
Send a message via AIM to Gogar
Quote:
Originally Posted by gr8fl4porsche View Post
This is my favorite part of your question.

Quick and easy, as a part of home remodeling, is a surprise event - not a planned one.
I hear you, I think I meant "quick and easy" compared to having to bust open some walls to get a look at stuff. I'm approaching the end of my rope with plaster and lathe, so fishing some wire actually sounds. . . easy and . . . not dusty.
__________________
1983 SC Coupe
1963 BMW R60/2
1972 Triumph Tiger
1995 Triumph Daytona SuperIII
Old 11-23-2013, 06:15 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #15 (permalink)
Band.
 
Join Date: Dec 2003
Location: Denver, CO
Posts: 13,312
Send a message via AIM to Gogar
Quote:
Originally Posted by craigster59 View Post
Pull 3 wires, 12g preferred. If the existing wire is copper, you might just want to leave it. If it's aluminum, it definitely needs replacing. Just put a grounding rod near the panel for your ground.
It's copper. When I had my outside service done he did proper ground rods etc. so I'm getting closer to being correct.
__________________
1983 SC Coupe
1963 BMW R60/2
1972 Triumph Tiger
1995 Triumph Daytona SuperIII
Old 11-23-2013, 06:17 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #16 (permalink)
Driver
 
Noah930's Avatar
 
Join Date: May 2005
Location: gone
Posts: 17,429
Garage
We had the same issue in our 60 year-old house last year. A couple light switches started shorting out, prompting our "update." We had a handyman/electrician replace our wiring via the above sting-and-new wire technique. The insulation was intact, except for the ends (where connected to electrical switches) as that's where heat had broken down the insulating cloth over the years. The existing conduit made the job much easier (only 1 hole had to be made/patched).
__________________
1987 Venetian Blue (looks like grey) 930 Coupe
1990 Black 964 C2 Targa
Old 11-23-2013, 06:28 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #17 (permalink)
Senior Member
 
Join Date: Jun 2000
Location: N. Phoenix AZ USA
Posts: 28,943
And if you have room, go with the thicker gauge wiring. Its nice to have more capacity in the wiring than you have to have. Running a space heater at the end of a run can over task some smaller stranded wiring, so good to go up one size...
__________________
2013 Jag XF, 2002 Dodge Ram 2500 Cummins (the workhorse), 1992 Jaguar XJ S-3 V-12 VDP (one of only 100 examples made), 1969 Jaguar XJ (been in the family since new), 1985 911 Targa backdated to 1973 RS specs with a 3.6 shoehorned in the back, 1959 Austin Healey Sprite (former SCCA H-Prod), 1995 BMW R1100RSL, 1971 & '72 BMW R75/5 "Toaster," Ural Tourist w/sidecar, 1949 Aeronca Sedan / QB
Old 11-23-2013, 06:34 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #18 (permalink)
 
Used Up User
 
imcarthur's Avatar
 
Join Date: Jun 2003
Location: Toronto
Posts: 8,311
Garage
No doubt about it, it will be a big job. You would have to map the wiring to locate the hidden junction boxes that may be lurking in the basement & attic or in closets etc. Buy 4 rolls of wire (add red for the 2nd hot lines as shown in the junction box you posted) & buy or make a cradle to feed them smoothly. A local electrical distributor would be a good source for supplies.

Ian
__________________
'87 Carrera Cab

----- “Only two things are infinite, the universe and human stupidity, and I'm not sure about the former.” A. Einstein -----
Old 11-23-2013, 06:47 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #19 (permalink)
Band.
 
Join Date: Dec 2003
Location: Denver, CO
Posts: 13,312
Send a message via AIM to Gogar
Can I crimp the new wires to the old and use the old as my 'fish' line?

thanks everybody.

__________________
1983 SC Coupe
1963 BMW R60/2
1972 Triumph Tiger
1995 Triumph Daytona SuperIII
Old 11-23-2013, 06:55 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #20 (permalink)
Reply


 


All times are GMT -8. The time now is 05:47 PM.


 
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2025, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2025 Pelican Parts, LLC - Posts may be archived for display on the Pelican Parts Website -    DMCA Registered Agent Contact Page
 

DTO Garage Plus vBulletin Plugins by Drive Thru Online, Inc.