Replacing outside breaker
The breaker on the outside of my building is tripping when my silk screen dryer and flash dryer are on. Never used to.
Anyone ever change the breaker on a main box? Do I have the e- company turn off power to it? http://forums.pelicanparts.com/uploa...1390146050.jpg http://forums.pelicanparts.com/uploa...1390146065.jpg http://forums.pelicanparts.com/uploa...1390146097.jpg |
i don't think they are a big deal to replace, but someone with more knowledge can confirm. i think just make sure that everything they feed is off and replace. But don't take my word for it, wait for an expert.
|
Is there a main breaker upline from that 3 pole 100 amp?
|
Craig, I think this is the main breaker. Wires go from the pole to a huge steel conduit at the top of the building, that runs down to the box and meter.
|
If that's the one that's tripping I'd call a professional, that's a lot of juice to get hit with!
|
I'd have the e-company pull the meter, you may just need to take a stiff wire brush to the buss bars.
|
Thanks. E-company will only turn off juice. I don't think they will do it if I call and tell them too. Will call tomorrow and see.
|
E-company turns off juice, its dead, you take wire brush to the buss bars, and inspect/replace the breakers. Price out those breakers first, they could be no longer available. They look old and breakers, especially, old ones ,are known to fail just from taking them out and futzing with them.
|
100 amp!! That will kill you if you don't know what you're doing. Please hire a professional.
IMO the breakers get old and trigger all the time when the load is close to limit. |
Great information, thanks. I'm hoping the E-company will turn off the e- with only my call.
this one looks similar Siemens Q3100 100-Amp 3 Pole 240-Volt 10-Kaic Circuit Breaker - Amazon.com |
My house is 100 amp, its no big deal to add a new breaker with power on. They clip in and out, about as dangerous as flicking a light switch.
BUT......the breaker may just be doing its job!!!! It is important to call someone in to insure that you do not have an electrical issue down the line that is causing the breaker to pop. This happened everytime I turned on the toaster at home.... Then the toaster tried to electrocute me!!!! The issue was the worn out toaster not the breaker. |
OK, Mike, I'm taking you out of my will. :D
|
call an electrician, will your insurance company cover you if you do it incorrectly?
|
Shaun, being an electrician, the best advice I can give you is to have an electrician look at it. The breaker is tripping for a reason.
|
Last time I screwed with the main breakers I wound up replacing the service panel and it took a day. Twas shot.
|
Are your dryers 3 phase? I am just curious how they balance the loads.
|
What Vin said. Replacing a breaker, even a 3 pole is easy. Done it many times. You need to now WHY it's tripping. Better to have a pro verify the load. Be safe.
|
Quote:
|
Quote:
Quote:
I'm going to take the box cover off tomorrow and see what's in there. Can't hurt. |
Shuan,
I don't think its the Breakers, but I have been known to be dead wrong. It might be something else that's tripping it. Cheap enough to change out the breakers and see if its still doing it. Hire someone to change out the breakers because it should be cheap enough to do if you feel uncomfortable doing it yourself. Its a 5 minute job. |
Hey Shaun I am also an electrician. I think you are right that it is the outside breaker it is showing rust. That outside breaker is your main feed being fed from your meter pan. It's live until your power company kills it which unfortunately for you means they have to shut it off for it to be replaced.
If you want to check your amperage use you will need an amp probe. Open up the panel in the house and with the dryer and the other device on put the amp probe on each of the main feed wires. Each one will give you a reading of the amperage in use. If one is a lot higher than the others shut off that 2nd device on the 30amp breaker. See if the amperage goes down if it does move that 30 amp breaker to one of the other 2 feeders(the one with the least amperage) and that should solve your problem. Again I think it's the outside breaker. |
100 Amps is no more dangerous then .5 amps
each WILL kill you just as fast 110v v.s. 277v that is a whole different thing- |
Thanks 86, I'll do some testing tomorrow.
here's the dryer. not a home, light industrial. it cures freshly silk screened t-shirts running on the conveyor belt. http://forums.pelicanparts.com/uploa...1390171029.jpg |
Borrow a clamp on ammeter or buy one.
See what the machine is really drawing. My guess is the breaker is not working properly. I would change it live, but I'm a professional (and an idiot). |
I was told by a city inspector that a single-throw switch is required after the utility meter, within a certain distance (3-5ft?), and before any breaker box.
Such would allow safe conditions when working on sub-boxes. Residential house. (However your city code might not require this.) I've been told breakers can get soft and trip easy, but wholly second the advice of testing amp draw first and using an electrician for an hour. The wiring could be undersized, breaker bad, or machine drawing too much juice. You don't have time for a house fire..... |
Quote:
|
I would imagine that each of the loads are protected by fusing or a distribution panel for the space. If those are not tripping then the main could be suspect or perhaps something that was once cute and fuzzy was chewing on some wires...
The 100 amp main for the house (the house is a sub panel, main is in the garage) went bad at Christmas a couple of years ago. The main would trip while nothing else would.... They are not a big deal to change out. |
Quote:
You may have an intermittent ground fault. |
Quote:
I'm no electrician, but the clamp on attachment for using a Fluke isn't the same thing. Where you going to hook the Sears clamp on meter, you have to put it on an electrical leg inside the box where the 100A juice is open and exposed. Or you can open the box at the dryer and clamp each leg of wire to see the draw. My vote again is aging breakers with corrosion and corroded buss bars. |
Shaun - If you're not 100% comfy working on this, hire it out. You've already used up too many of your 9 lives.
|
Hugh's wisdom still reigns supreme.
Me in your shoes: I pull with a replacement on hand, look it over - if it looks corroded or crushed up, replace it. See what happens. If it still blows trips, call the electrician and get be true load checked out. Could be something stupid pushing it close to load rating and with a fatigued breaker, that would do it. Plugged in a new coffee pot or toaster lately? Sometimes...ya never know. |
That dryer should be on its own dedicated circuit.
|
Quote:
I never have the dryer and exposure unit on at the same time. Mostly because you never have to, but the electrician said it would trip the main breaker. These breakers, inside, never trip. I always have them off when not using the equipment too. http://forums.pelicanparts.com/uploa...1390221932.jpg |
Breakers. I wouldn't hire an electrician, do it live. If you don't there will be five bills to pay. One to shut it down, one to take out the screws, one to pull the breaker, one to install the breaker, and one to watch the others do the work. Unions...
|
You can get the correct clamp on attacment for your Fluke. They automatically scale down the reading to the 10 amp scale you should have on the Fluke. It's not a direct current to meter configuration...
Having said that and looking at the downstream breakers I've got two suggestions... One, you should probably be on a 200 amp service or more. Can't believe a licensed electrician would put that kind of load on the secondary panel. Also, I do suggest measuring your current draw but, like others, I suspect either your main breaker has gotten weak from age or you have a corrosion issue. |
Hey Shaun the 100 amp breaker is to the left of your panel? If so shut it off open the metal enclosure check wires coming off breaker make sure they are dead. Remove wires and replace breaker. Go inside run all your devices see if it trips. If all is well it was the breaker. If not it is something else in the house. I don't have that type of a system with the main outside the house in my house you have to pull the meter to kill the power at the main.
|
Pelican David Goodman sent me an email this morning and left his clamp adapter on his back porch for me. I'm going out now to take some measurements.
here are some pics of the box. 86, this is a light industrial building. http://forums.pelicanparts.com/uploa...1390242362.jpg http://forums.pelicanparts.com/uploa...1390242374.jpg http://forums.pelicanparts.com/uploa...1390242382.jpg http://forums.pelicanparts.com/uploa...1390242393.jpg |
My advice is if you feel comfortable changing that yourself, then save a couple hundred bucks and see if it trips again with new breakers. This will rule out the breaker issue. Somethings are just worth paying for. This maybe one one them.
|
here are the readings I got.
First set are with only the dryer on. Second set is with the dryer and the flash dryer on. I wonder if I screwed something up given the first set readings on the 3rd wire over. I took pics of a few of the outputs, it was jumping around. With both on, the 3rd acted like the first two. Note that with the dryer and flash both on, the breakers were buzzing a little and were hot. It typically takes 20 minutes for this to flip with both on. Only Dryer On http://forums.pelicanparts.com/uploa...1390244230.jpg http://forums.pelicanparts.com/uploa...1390244246.jpg http://forums.pelicanparts.com/uploa...1390244317.jpg http://forums.pelicanparts.com/uploa...1390244333.jpg http://forums.pelicanparts.com/uploa...1390244349.jpg Dryer and Flash Unit On http://forums.pelicanparts.com/uploa...1390244379.jpg http://forums.pelicanparts.com/uploa...1390244396.jpg http://forums.pelicanparts.com/uploa...1390244410.jpg |
Quote:
|