Question for the hydrodynamic gurus
I'm trying to measure water flow thru my pool pump system. I've got 2-1/2" SCH 40 pipes running water around, but a flow sensor for pipe that big is pretty spendy. It occurred to me I could break out a smaller parallel path that would fit a smaller, cheaper flow sensor.
My question is, what is the relationship of the flow thru the smaller pipe to the bigger pipe? Would there be water flow? Would the elbows reduce the flow thru the smaller pipe ? ![]() |
||
![]() |
|
Registered
Join Date: Sep 2009
Location: North of You
Posts: 9,160
|
What flow sensors are you proposing?
__________________
"A machine you build yourself is a vote for a different way of life. There are things you have to earn with your hands." |
||
![]() |
|
Takin' hard left turns
Join Date: Dec 2004
Location: So Cal
Posts: 1,412
|
I was thinking something along the lines of this
|
||
![]() |
|
Banned
Join Date: Jul 2011
Location: St Paul MN
Posts: 19,431
|
there will likely be some relationship in flows, but it will not linear, and without a larger sensor to first calibrate it, it will be pretty tough to predict with any reasonable accuracy.
|
||
![]() |
|
Home of the Whopper
|
Do you have pressure gauges before and after the pump?
Most pumps have a pump curve that you can determine flow by the dp across the pump.
__________________
1968 912 coupe 1971 911E Targa rustbucket 1972 914 1.7 1987 924S |
||
![]() |
|
Registered
Join Date: Sep 2009
Location: North of You
Posts: 9,160
|
Quote:
__________________
"A machine you build yourself is a vote for a different way of life. There are things you have to earn with your hands." |
||
![]() |
|
![]() |
Registered
Join Date: May 2003
Location: Woodlands TX
Posts: 3,941
|
I predict a highly nonlinear relationship between the two flows as well.
I think measuring differential pressure across a restriction (or from the pump as BK suggests) would be preferable. Depending on your accuracy requirements you need some sort of calibration method for anything resembling quantitative results IMO, can you do a time to fill calculation or similar Surely others have tried similar things so the all knowing google probably has a solution
__________________
84 930 07 Exige S |
||
![]() |
|
Registered
Join Date: Dec 1969
Location: chula vista ca usa
Posts: 5,696
|
I would suggest measuring how much power the motor driving the pump is using and that will equate to how much water is being pumped. Having the small line off the side of the main line will never give a reading relating to the actual flow. You would need some restriction in the main line to force the water through the small line and then it would not match actual flow.
I would suggest installing a tee and short section of the 2 1/2 pipe and a valve that opens with no restriction down stream of the filters, etc. A valve in the main line would also be needed so you could shut off main flow and open the test line to see how long it takes to fill a 5 gallon container. This would be pretty close to actual flow rate. |
||
![]() |
|
Unregistered
Join Date: Aug 2000
Location: a wretched hive of scum and villainy
Posts: 55,652
|
Here's how I would do it:
Forget the small pipe. Build as flange into the larger pipe and install an orifice plate in that flange, small enough to restrict the flow slightly and cause a pressure drop across it. then drill and tap the pipe on either side of the orifice and plumb up a delta P gauge (differential pressure gauge). Use the gauge to measure the pressure drop across the orifice, which should be reasonably linear until it starts cavitating. You may have to play with the size of the orifice and range of the gauge until you can get both to work together, and you'll have to do some calcumalations to determine calibration, but it will be reliable, cheap, accurate, and kind of fun to do. Last edited by sammyg2; 04-13-2016 at 11:22 AM.. |
||
![]() |
|
Unregistered
Join Date: Aug 2000
Location: a wretched hive of scum and villainy
Posts: 55,652
|
Or you could go the easy route and get a copy of the centrifugal pump curve, and measure the amps the motor is pulling.
Convert the amps to HP, and along with the delta P across the pump (discharge minus suction pressure) converted to head feet and voila! Plot it on the curve and you have your flow. After several measurements you could use as a graph to indicate flow at various discharge pressures, assuming the suction pressure is constant. ![]() |
||
![]() |
|
Home of the Whopper
|
I didn't recommend the orifice because it will reduce flow and a 2.5" one won't be cheap.
Couple of taps on either side of the pump, Couple of ball valves and a pressure gauge and BAM! Done. Deadhead the pump and read pressure. That will put you on the right pump curve. Then use dP and that will give you flow. Couple of bucks and less than a 6 pack in labor.
__________________
1968 912 coupe 1971 911E Targa rustbucket 1972 914 1.7 1987 924S |
||
![]() |
|
Home of the Whopper
|
I didn't recommend the orifice because it will reduce flow and a 2.5" one won't be cheap.
Couple of taps on either side of the pump, Couple of ball valves and a pressure gauge and BAM! Done. Deadhead the pump and read pressure. That will put you on the right pump curve. Then use dP and that will give you flow. Couple of bucks and less than a 6 pack in labor.
__________________
1968 912 coupe 1971 911E Targa rustbucket 1972 914 1.7 1987 924S |
||
![]() |
|
Detached Member
Join Date: May 2003
Location: southern California
Posts: 26,964
|
get some more pipe and elbows and time how long it takes to fill a container of a known volume like your trash can you drag to the curb once a week.
If you have a DE filter with a backwash valve, get a slack hose from the pool supply place and put it on backwash and fill the large container as you time it. That way, you account for DE filter pressure and flow drop. Last edited by Hugh R; 04-13-2016 at 12:28 PM.. |
||
![]() |
|
Registered
|
Flow varies a great deal over a seasonal filter cycle. If accuracy is important, plumb this in:
https://www.poolsupplyunlimited.com/h2flow-fv-c-flowvis%EF%BF%BD%EF%BF%BD-flow-meter-check-valve-with-valve-body/142242p1
__________________
2009 Cayman PDK With a few tweaks 2021 Cayman GTS 4.0L 2021 Macan (dog hauler) |
||
![]() |
|
Registered
Join Date: Jan 2001
Location: So. Cal.
Posts: 9,104
|
I was going to suggest something along the lines of what Hugh said. If you are OK with plumbing in an alternate path to measure flow through a cheaper & smaller type of meter, you can put in a valve on your main line and put in a T before it with another valve for a shut off. Then just close the main flow, open the alternate flow, and do a timed measurement into a container. Cheaper & easier than more valves & plumbing, plus it might serve some purpose later on.
__________________
Marv Evans '69 911E |
||
![]() |
|
Registered
|
Timing a 50 gallon drum fill is certainly the cheapest way to go but accuracy will be about +/- 25%.
Remember that by diverting flow from the filter you have eliminated all the head loss between filter and pool return, including heater, return valves, check valves, and any 90 ells. Typically greater than 1/2 of your head loss is in the return side. If a really rough estimate is all you need this will get you there. Calculating head loss: http://blog.poolproducts.com/swimming-pool-feet-of-head-calculations/
__________________
2009 Cayman PDK With a few tweaks 2021 Cayman GTS 4.0L 2021 Macan (dog hauler) Last edited by Cajundaddy; 04-13-2016 at 01:39 PM.. |
||
![]() |
|
Takin' hard left turns
Join Date: Dec 2004
Location: So Cal
Posts: 1,412
|
Thank you all for your replies. I’ve been out of the office for a few hours, so just getting back to this now.
Quote:
Quote:
Well, the assumption is you can deduce the water velocity from the pulse rate. Given the pipe ID you should be able to convert that to flow in GPM. Quote:
Quote:
Quote:
Quote:
Quote:
Quote:
Quote:
Quote:
Again, thanks for your suggestions. If I’m wrong about the impeller and secondary strainer condition affecting flow rate calculations, please tell me. This is a fun exercise, and I’m looking forward to coming up with a good solution! Last edited by Amail; 04-13-2016 at 02:18 PM.. |
||||||||||
![]() |
|
....
Join Date: Feb 2008
Posts: 18,665
|
Quote:
visual
__________________
dolor et pavor Copyright |
||
![]() |
|
![]() |
Takin' hard left turns
Join Date: Dec 2004
Location: So Cal
Posts: 1,412
|
Thanks for the video. In there he shows pressure sensors on both the suction and discharge side of the pump. If you close off the pipe on the discharge side, I see how you get pressure (thanks, pump!). How do you get any pressure on the inlet side though? For instance, my pool water level is about a foot above the inlet of the pump, so I could see measuring a foot of head on the inlet side. But my friend's pool has the pump higher than the water level, so wouldn't it measure suction?
![]() |
||
![]() |
|
....