Quote:
We have 3-phase 220/380V 50Hz lead our house main fuse board. It is rather convenient gauge-wise. Main phase fuses are currently 20A but I gather we could go down to 16A as I never busted main fuses despite welders, geothermal heat pump etc. (part of subscription price is based on fuse size). Those US wire gauges look gigantic to me.
__________________
Thank you for your time, |
||
|
|
|
|
Puny Bird
Join Date: Nov 2002
Location: Port Hope (near Toronto) On, Canada
Posts: 4,566
|
Quote:
I bet that will make your service meter spin.
__________________
'74 Porsche 914, 3.0/6 '72 Porsche 914, 1.7, wife's summer DD '67 Bug, 2600cc T4,'67 Bus, 2.0 T1 Not putting miles on your car is like not having sex with your girlfriend, so she'll be more desirable to her next boyfriend. |
||
|
|
|
|
Puny Bird
Join Date: Nov 2002
Location: Port Hope (near Toronto) On, Canada
Posts: 4,566
|
Quote:
As said 3 phase is mostly commercial only and then you have a transformer to run any single phase equipment and lighting. You can find really cheap used car lifts here, but they're no good to the hobbyist because they're 3-phase.
__________________
'74 Porsche 914, 3.0/6 '72 Porsche 914, 1.7, wife's summer DD '67 Bug, 2600cc T4,'67 Bus, 2.0 T1 Not putting miles on your car is like not having sex with your girlfriend, so she'll be more desirable to her next boyfriend. Last edited by Mark Henry; 02-17-2017 at 03:53 AM.. |
||
|
|
|
|
Platinum Member
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 21,118
|
With 100 amps and #4, you can make it a subpanel. Wire is all there, neutral, Ground, and 2 hot legs.
Then branch off to oven and have room for a few expansion. How much current will the oven draw max? |
||
|
|
|
|
Registered
Join Date: Jun 2001
Location: Sweden
Posts: 5,911
|
Quote:
Not here. All houses are fed by 3-phase. But light loads (TV, fridge lights etc.) are all single phase. You can easily get single phase from 3-phase by connecting the load between one of the phases and NULL. There is no transformer involved. So you basically connect three groups of single phase 220V loads (which you try to spread evenly across the phases) or you can connect one 3-phase load (in either Y or D-connection).
__________________
Thank you for your time, |
||
|
|
|
|
Puny Bird
Join Date: Nov 2002
Location: Port Hope (near Toronto) On, Canada
Posts: 4,566
|
Quote:
As said we never see 3-phase in residential unless it's something like a big farm. Our residential service has two single phase 120V legs, we get 220/240V by using the two legs in tandem.
__________________
'74 Porsche 914, 3.0/6 '72 Porsche 914, 1.7, wife's summer DD '67 Bug, 2600cc T4,'67 Bus, 2.0 T1 Not putting miles on your car is like not having sex with your girlfriend, so she'll be more desirable to her next boyfriend. Last edited by Mark Henry; 02-17-2017 at 04:24 AM.. |
||
|
|
|
|
|
Registered
Join Date: Jun 2001
Location: Sweden
Posts: 5,911
|
Quote:
Here, the phases are 120 degree apart. So tapping one leg towards NULL gives you 220V. Connecting a load between two phases (without involving NULL) gives you 380V. Makes mixing 3-phase and 1-phase loads rather easy... Of course, touching two phases will give you rather good jolt, compared to 110V-
__________________
Thank you for your time, |
||
|
|
|
|
Registered
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,461
|
Quote:
No idea on how much current. There are 3 mercury switches inside, presumably 1 for each heating element in the original dryer. I am only using 2 of the elements. Says 120V with a 35 amp draw. Running the dryer back in the day, all day, the 100 amp breaker never tripped. Until I needed to replace the breaker on the outside of the building anyway. But internal never did. I was planning on making an extension cord with this wire I've had laying around. Need about 20 feet, 30 at the most. It's solid core but should be easy to just leave in the room when not in use. It's 4 wires: R, B, W and copper ground.
__________________
Tru6 Restoration & Design |
||
|
|
|
|
Registered
|
First off I always recommend using a licensed electrician for commercial work. There are National Code and also Town Codes that need to be met. Ugly's Electrical Reference is a very handy book for quick reference to code requirements. There are rules that need to be met for hook ups, wet or dry locations, disconnect means, etc.
Most wiring is done with stranded wire, and above certain gauge all wire is stranded. 100 amp circuit should have #2 awg. #4 awg is too small for that breaker. You don't seem sure what amperage you need. The 30 amp outlet shown in post 8 should not be used if 35 amps is required, plus it should not be connected to a 100 amp breaker, breaker needs to be downsized at the least due to wire gauge. Outlet used must match breaker and wire size. 30 ft extension cord would not be legal to hook up equipment. I would recommend checking the plate on the equipment you are hooking up to see what the rated power requirements are. It will list voltage and amperage minimum requirements. Just hooking up to an existing circuit without knowing your actual need is not a good idea. For those that desire it in a residential single phase home, 3 phase equipment can be used with a convertor. I have hooked up rotary convertor in a friends house so he could run a 3 phase milling machine in his garage. As to the sub panel, another panel can be fed from the main panel to allow additional breakers for more branch circuits if needed, but must also be hooked up according to local Code.
__________________
Ed 1973.5 T |
||
|
|
|
|
Puny Bird
Join Date: Nov 2002
Location: Port Hope (near Toronto) On, Canada
Posts: 4,566
|
I agree, is there not a label on the machine telling you the requirements?
12/ wire is a bad idea as it's is only good to 20amps and that wire would be totally illegal as an extension cord. I also wondered about the #4 wire on 100 amps, I believe code here is 3/ IIRC If you want 40amp on an extension cord you'll need 8/4 SOOW wire with the correct connectors (50amp). Even then I'd run conduit to an overhead box and using a strain relief (Kellem grip) hang it over the approximate location of the oven. This way the extension cord is never laying on the floor. This is how I did my TIG welder except it's 50amp with 6/4 wire But as always I'm not an electrician, so I recommend you seek the advice of a pro.
__________________
'74 Porsche 914, 3.0/6 '72 Porsche 914, 1.7, wife's summer DD '67 Bug, 2600cc T4,'67 Bus, 2.0 T1 Not putting miles on your car is like not having sex with your girlfriend, so she'll be more desirable to her next boyfriend. |
||
|
|
|
|
Registered
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,461
|
Hi Ed,
The #4 was installed by a licensed electrician 10 years ago. Cost about $1500 to run wire from the breaker to the box shown and then #4 was spliced from the box to the control box of the dryer. I can run the same #4 or #2 if required, to a similar box in the oven room. In post 28, there are 3 of those contactors in the control box, one for each heating element. I seem to recall the electrician said they added up to 105 but the 100 amp breaker was fine. Like I said, it never tripped running all three heating elements all day long. I am only running 2 heating elements so I can put in a 70 amp breaker if that will work. There is no plate on the equipment unfortunately. here is a pic of what the dryer looked like. Heating elements above the conveyor belt. Control box mounted to frame, you can see the curved conduit that held the 4 #4 wires. Quote:
__________________
Tru6 Restoration & Design |
||
|
|
|
|
Registered
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,461
|
Good to know. There are generator extension cords I can look into as well.
Quote:
__________________
Tru6 Restoration & Design |
||
|
|
|
|
Puny Bird
Join Date: Nov 2002
Location: Port Hope (near Toronto) On, Canada
Posts: 4,566
|
Because you don't know the true requirements of this unit, I strongly suggest you talk to a licenced electrician.
Sucks, but it's not worth burning your house down.
__________________
'74 Porsche 914, 3.0/6 '72 Porsche 914, 1.7, wife's summer DD '67 Bug, 2600cc T4,'67 Bus, 2.0 T1 Not putting miles on your car is like not having sex with your girlfriend, so she'll be more desirable to her next boyfriend. |
||
|
|
|
|
Registered
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,461
|
well a licensed electrician installed this 10 years ago. easy to duplicate 20 feet away.
__________________
Tru6 Restoration & Design |
||
|
|
|
|
Registered
|
I gotta go with Sully...
This whole project begins with known current draw for each piece of equipment and putting each on it's own circuit. If we don't know this, please back away from wiring anything. 100A and #4 wire are a clue that this stuff draws a LOT of juice and you want it done exactly right. Not a good DIY money saving project IMO because you will let the smoke out of #12 wire in short order.
__________________
2009 Cayman PDK With a few tweaks 2021 Cayman GTS 4.0L 2021 Macan (dog hauler) Last edited by Cajundaddy; 02-17-2017 at 09:38 AM.. |
||
|
|
|
|
Registered
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,461
|
May I direct you the thread title.
__________________
Tru6 Restoration & Design |
||
|
|
|
|
Registered
|
Yep, I saw it and it frightens me a bit. I love stranded wire. I've done a lot of electrical work and job #1 is matching wire size to the max current draw of the machinery. Don't know that for certain? Stop all work and find out.
This also frightens me a bit: "I was planning on making an extension cord with this wire I've had laying around. Need about 20 feet, 30 at the most. It's solid core but should be easy to just leave in the room when not in use. It's 4 wires: R, B, W and copper ground." ... with a pic of 12/3 Romex. If you wire that machinery up be sure to have hot dogs and marshmellows handy. It is going to get very exciting for a while.
__________________
2009 Cayman PDK With a few tweaks 2021 Cayman GTS 4.0L 2021 Macan (dog hauler) Last edited by Cajundaddy; 02-17-2017 at 09:53 AM.. |
||
|
|
|
|
Registered
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,461
|
That's why I post here! With the help of everyone here I wired in a buck-boost transformer a year and a half ago for my compressor and no fires yet.
My protocol is to post here and get great information, help and support. I also google a lot. So by time I actually do something, I'm an expert with 30 years experience.
__________________
Tru6 Restoration & Design |
||
|
|
|
|
|
Platinum Member
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 21,118
|
I'm a little confused. I assumed you are decommissioning the silkscreen oven and installing the powdercoat oven?
|
||
|
|
|
|
Registered
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,461
|
Sorry, that pic is 8 years old. Yes, the silk screen dryer is no more. The heating elements and controller have been repurposed into the powder coat oven.
The pic with the temp gun below, I just connected the element terminals to a 110V outlet. ![]() ![]() ![]() ![]() ![]()