Quote:
Originally Posted by 1990C4S View Post
That thing looks to be toast. You have so much corrosion that you lost your contact force. Which leads to heat, arcing, and then more corrosion.

Measure the breaker voltage drop for each phase at full load....(input side of the breaker to the output side).

Short term I would clean it and add a copper shim with Noalox. Long term I would plan to replace it the breaker AND the box. Or make new lugs.
It is toast! Call a professional.

__________________
Jim

1983 944n/a
2003 Mercedes CLK 500 - totaled. Sanwiched on the Kennedy Expressway
Old 09-05-2017, 04:39 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #21 (permalink)
Registered
 
Shaun @ Tru6's Avatar
 
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,264
Quote:
Originally Posted by wdfifteen View Post
This seems so out of character for you. You are so meticulous about Porsche stuff, but seem to be vacillating on doing this very important job properly.
Haha, not at all!

Look at what I wrote, I'm calling the electric company about turning off service at which time I can replace the rails and whatever else is necessary in the box. This is an outside box connected to the meter. I have to look at it and take pics tomorrow but it seems to be just a few rails running into the box from the meter that the breaker rails bolt to. My sense is I need a new system that bolts to the rails and which the breaker attaches to. More pics tomorrow to clarify.

This is why I'm a horrible manager, I am the exact opposite of a micro-manager and think everyone should just "get it" when in reality I don't explain enough. Though I am supportive and nurturing so I have that going for me.

But as to leaving it to a professional, I don't trust anyone to do half as good of a job as I can. I've done significantly better plumbing than the people who put the water into this building and the electrical in the ceiling is a mess like I've never seen. This is to say nothing of the professional electrician I hired to wire in the silk screen dryer and I have to wonder if he did anything to create this situation.

I did wire in a buck-boost transformer to go from 208V to 230V for my compressor and I expect this job to be a lot simpler.

And per my usual way of doing things, will be done meticulously.

All that said, it does seem to be working nicely just with the cleaning and Noalox but clearly needs to be replaced. I think when you are Dremeling bars leading directly to the meter so you can get the breaker back on, it's time to replace the unit.

What I really want to know more than anything else is how this happened in the first place. Replacing the breaker rails is just mechanical. Troubleshooting the problem is the interesting part.

But really, I was hoping to use these chemically cut copper T-Rex foils that were supposed to go on boy's t-shirts (if you hit them with a mapp torch first they become crazy cool) but market testing found that mom's were concerned about the real foil. You can scrunch up the shirt and then flatten but they retain all the scrunching like Al foil. Very sad, they would have been super cool.

__________________
Tru6 Restoration & Design

Last edited by Shaun @ Tru6; 09-05-2017 at 04:56 PM..
Old 09-05-2017, 04:53 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #22 (permalink)
Registered
 
Join Date: May 2006
Location: Upstate New York
Posts: 1,446
Garage
Shaun,
Could be voltage or current unbalance between the legs. Anything more than 2% is unacceptable. I presume you have commercial power (3ph) going into your building. The unbalance could be from the power being supplied from the utility company or unbalanced loads in your building. A qualified electrician can install a line recorder on your power panel and it records electrical faults and load inbalance at the panel. Not a pretty sight from your posted pics.
Old 09-05-2017, 05:00 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #23 (permalink)
Registered
 
Shaun @ Tru6's Avatar
 
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,264
Hey Bob! Maybe because this building is in a residential neighborhood (no idea how it got zoned) but I called the e- company years ago and they said this building is single phase 208V.

Each of the three main lines are 120V and run into the breaker panel in the building and are then divided up between the breakers in the panel. So only lights in 3 rooms and one row of outlets gets effected when the center rail goes down.

I wish I knew and electrician I could trust.
__________________
Tru6 Restoration & Design
Old 09-05-2017, 05:05 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #24 (permalink)
Brew Master
 
cabmandone's Avatar
 
Join Date: Jul 2013
Location: Delphos OH
Posts: 32,062
Garage
FWIW that looks like arcing more so than corrosion bases on what I'm seeing in the pics. it doesn't appear to me that the breaker tabs are making correct contact with the lugs.
Old 09-05-2017, 05:05 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #25 (permalink)
Make Bruins Great Again
 
Por_sha911's Avatar
 
Join Date: Dec 2003
Location: TN
Posts: 20,819
Garage
I'm sure you'll be getting new breakers when you get the buss bar. Is it that much more money to get a whole new box?
__________________
--------------------------------------
Joe
See Porsche run. Run, Porsche, Run: `87 911 Carrera
Old 09-05-2017, 05:07 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #26 (permalink)
 
Registered
 
greglepore's Avatar
 
Join Date: Mar 2003
Location: Charlottesville Va
Posts: 5,754
Quote:
Originally Posted by cabmando View Post
FWIW that looks like arcing more so than corrosion bases on what I'm seeing in the pics. it doesn't appear to me that the breaker tabs are making correct contact with the lugs.
This. Arcing could be caused by corrosion, but it'd have to be pretty bad. In any case, I'd get to the root before it arcs and lights something up.
__________________
Greg Lepore
85 Targa
05 Ducati 749s (wrecked, stupidly)
2000 K1200rs (gone, due to above)
05 ST3s (unfinished business)
Old 09-05-2017, 05:12 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #27 (permalink)
UnRegistered User
 
billybek's Avatar
 
Join Date: Dec 2007
Location: Calgary
Posts: 8,016
Garage
That T-Rex shirt was one of my sons favorite, Shaun! Thanks for the nice memory....

On the box, I would replace it. As mentioned, checking voltage drop while under load is important but check from the bus bar to the terminal end or from the wiring terminals entering the panel to the terminals leaving the breaker while under load.

If you can get parts for the original box and replace the bus bars and breaker that would be OK but a new panel weatherproof from Home Depot is like $77 in three phase. Add on the cost of the breaker and misc hardware. The only problem with replacement is there may be some screwing around to make it work but it would probably be worth it.

The old breaker and bus bars really look as though someone in the past had pulled that breaker under load and not corrosion but I cannot imagine anyone doing that.

Cheers,
__________________
Bill K.
"I started out with nothin and I still got most of it left...."
83 911 SC Guards Red (now gone)
And I sold a bunch of parts I hadn't installed yet.
Old 09-05-2017, 05:43 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #28 (permalink)
Registered
 
Shaun @ Tru6's Avatar
 
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,264
Hey Bill,

Fond memories of days gone by but better ones are always ahead.

What may complicate getting a whole new box is this one houses my floor and the one below me. 2 different meters running independently into the same box with independent main breakers. I have a single 3 pole 100A breaker and so does the other meter. And they are oriented vertically so it would be a lot of work to add a whole new box.

More tomorrow.
__________________
Tru6 Restoration & Design
Old 09-05-2017, 05:56 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #29 (permalink)
Registered
 
86 ssinit's Avatar
 
Join Date: Oct 2011
Location: Massapequa Park
Posts: 839
Garage
Ok so we agree it's arcing now why? Again check amperage. Also for voltage go phase to phase aacross all three phases. If one set read nothing across 2 phases than it is single phase 208. If it reads 208-220 across all three sets it's 3 phase.
__________________
1986 Porsche 911 Targa
1983 911 sc
2015 WRX
Old 09-05-2017, 06:56 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #30 (permalink)
Brew Master
 
cabmandone's Avatar
 
Join Date: Jul 2013
Location: Delphos OH
Posts: 32,062
Garage
Quote:
Originally Posted by 86 ssinit View Post
Ok so we agree it's arcing now why? Again check amperage. Also for voltage go phase to phase aacross all three phases. If one set read nothing across 2 phases than it is single phase 208. If it reads 208-220 across all three sets it's 3 phase.
Personally from looking at the pictures it doesn't look like the center leg is making good contact. It appears burn low on the post whereas the left and right have markings that are about center on lug.
Old 09-06-2017, 03:44 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #31 (permalink)
Registered
 
Shaun @ Tru6's Avatar
 
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,264
Some quick pics of the box. I'll have to look closely for a manufacturer. As as long the power is turned off, it looks like a 10 minute job to swap in a new a bar system and that's while having a beer and some hot wings. I think my biggest concern will be the bees. Saw a wasp and a few yellow jackets yesterday too.













__________________
Tru6 Restoration & Design
Old 09-06-2017, 04:27 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #32 (permalink)
 
Control Group
 
Tobra's Avatar
 
Join Date: Aug 2005
Location: Carmichael, CA
Posts: 53,469
Garage
Look how clean that one below looks. Maybe you are just over taxing yours. It sounds like you are using a residential hookup for semi industrial purposes.
__________________
She was the kindest person I ever met
Old 09-06-2017, 05:52 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #33 (permalink)
Still Doin Time
 
asphaltgambler's Avatar
 
Join Date: Nov 2004
Location: Nokesville, Va.
Posts: 8,225
Definitely the 'environment' causing this. Possibly seal the box with weather stripping on the lid, caulk any opening or hole inside the box as well.
__________________
'15 Dodge - 'Dango R/T Hauls groceries and Kinda Hauls *ss
'07 Jeep SRT-8 - Hauls groceries and Hauls *ss Sold
'85 Guards Red Targa - Almost finished after 17 years
'95 Road King w/117ci - No time to ride, see above
'77 Sportster Pro-Street Drag Bike w/93ci - Sold
Old 09-06-2017, 06:23 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #34 (permalink)
Registered
 
Shaun @ Tru6's Avatar
 
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,264
Quick note, busy day, raining on and off so no outside measurements. Center line has been fine all day so that's good. Just measured voltage at inside box:

122.1
122.2
121.6

Going to HD tonight and will get a clamp on amp meter.
__________________
Tru6 Restoration & Design
Old 09-06-2017, 09:47 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #35 (permalink)
Registered
 
86 ssinit's Avatar
 
Join Date: Oct 2011
Location: Massapequa Park
Posts: 839
Garage
Ok new pictures do make it 3 phase unless something funny is going on in that junction box. Again if you read phase to phase you should get 220. Yes your feeders are shot and I'm not sure if you can buy that part. Usually you would replace the whole thing. Can you get a picture of the wires street side going to the feeder pipe. Just curious are you the owner or a renter/lease holder
__________________
1986 Porsche 911 Targa
1983 911 sc
2015 WRX
Old 09-06-2017, 10:04 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #36 (permalink)
Registered
 
Join Date: May 2002
Location: St Louis
Posts: 4,211
So the lines from the pole go into the left box, through the center box to the meters in another box and back to the main breakers?
Success of this will depend on whether you can source that buss bar assembly separately.

Quote:
Originally Posted by Shaun @ Tru6 View Post
Some quick pics of the box. I'll have to look closely for a manufacturer.


Quote:
Originally Posted by Tobra View Post
Look how clean that one below looks. Maybe you are just over taxing yours. It sounds like you are using a residential hookup for semi industrial purposes.
Although it would be great, not many residences around here have 3 phase power going to them.
__________________
Rick
88 Cab
Old 09-06-2017, 10:10 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #37 (permalink)
Registered
 
Shaun @ Tru6's Avatar
 
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,264
Quote:
Originally Posted by 86 ssinit View Post
Ok new pictures do make it 3 phase unless something funny is going on in that junction box. Again if you read phase to phase you should get 220. Yes your feeders are shot and I'm not sure if you can buy that part. Usually you would replace the whole thing. Can you get a picture of the wires street side going to the feeder pipe. Just curious are you the owner or a renter/lease holder
phase to phase is 211V. When I called Nstar a few years ago they were very clear that I had single phase 208V.

I wish it were easier to turn the e- off, I could probably make new feeders.

More pics tomorrow.
__________________
Tru6 Restoration & Design
Old 09-06-2017, 10:22 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #38 (permalink)
Registered
 
Join Date: Sep 2009
Location: North of You
Posts: 9,160
Measure these voltages:

__________________
"A machine you build yourself is a vote for a different way of life. There are things you have to earn with your hands."
Old 09-06-2017, 10:40 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #39 (permalink)
Registered
 
wdfifteen's Avatar
 
Join Date: Mar 2008
Location: SW Ohio
Posts: 29,254
Garage
I see why you don't want to simply change out the whole box. What a monstrosity.

__________________
.
Old 09-06-2017, 10:46 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #40 (permalink)
Reply


 