Electrical code for breaker box clearance...

My understanding is there is to be 30" wide clearance in front of the panel, 36" in front of the panel and 6'-6" clearance in height.

Is the 30" centered on the panel or can the panel be somewhere inside that 30" as long as the panel door can open 90*?





Last edited by A930Rocket; 01-18-2018 at 05:13 PM..
Old 01-18-2018, 02:11 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #1 (permalink)
Registered
 
Join Date: Oct 2005
Location: Capistrano Beach, Ca.
Posts: 7,235
My interpretation, from your posted illustrations, is that the panel can be anywhere within that 30" space. The gray 18" rectangles in the top illustration represents the width of the panel relative to a 30" space. The panel can be offset to the left, centered, or offset to the right. The lower part of the top illustration shows how three panels, side by side, can use part of each other's clearances to meet the requirement. Notice how the two outside 18" rectangles are not centered within their respective 30" clearances.

In short, the panel does not have to be centered within the 30" clearance.
__________________
L.J.
Recovering Porsche-holic
Gave up trying to stay clean
Stabilized on a Pelican I.V. drip

Last edited by ossiblue; 01-18-2018 at 05:05 PM..
Old 01-18-2018, 05:02 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #2 (permalink)
Registered
 
John Rogers's Avatar
 
Join Date: Dec 1969
Location: chula vista ca usa
Posts: 5,694
If it were me, I would take pictures and plans and see an electrical contractor. If it costs some $$$$$ you'll be ahead when it has to be inspected. Your city may also provide that service but locations vary.

When we had solar installed we needed a new breaker panel since ours was 1960 vintage and not legal any longer. The electrical contractor knew exactly what to do and how to install the new panel so when the city inspector came around, he barely glanced at it.
Old 01-18-2018, 05:40 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #3 (permalink)
Registered
 
A930Rocket's Avatar
 
Join Date: Oct 2003
Location: Mount Pleasant, South Carolina
Posts: 14,064
Unfortunately, the panels are in place and we are wrapping up the project. I got there well after drywall, so we can’t move anything.

The problem is the electrician installed them in the wrong location after the first three bldgs.

Where we once planned on installing a wire shelf, we can’t because of the 30” rule.

My thinking is that we can locate the wire shelf on the other side of the panel and maximize the width by pushing the 30” to the other side.

This is what it should look like, but the electrician has installed the panels to close to the wire shelf.

The panel should have been installed were the structured wiring panel is.

Old 01-18-2018, 07:04 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #4 (permalink)
Registered
 
Join Date: Oct 2005
Location: Capistrano Beach, Ca.
Posts: 7,235
Could you mount the wire shelf at 6' 6" and move the brace so it supports the shelf from above?
__________________
L.J.
Recovering Porsche-holic
Gave up trying to stay clean
Stabilized on a Pelican I.V. drip
Old 01-18-2018, 07:32 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #5 (permalink)
Registered
 
LakeCleElum's Avatar
 
Join Date: May 2004
Location: Lake Cle Elum - Eastern WA.
Posts: 8,416
32 feet from front of panel to my garage door...........Height, no so much......New code?
__________________
Bob S.
73.5 911T
1969 911T Coo' pay (one owner)
1960 Mercedes 190SL
1962 XKE Roadster (sold) - 13 motorcycles
Old 01-18-2018, 08:30 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #6 (permalink)
 
Registered
 
A930Rocket's Avatar
 
Join Date: Oct 2003
Location: Mount Pleasant, South Carolina
Posts: 14,064
I’ve thought about that, but the bottom of the angled bracket to support the shelf would need to be at 6’-6”. That would raise the shelf 1’. That might be too high. At least that’s what I’m thinking. I’ll check with the county. They might be ok with that.

Quote:
Originally Posted by ossiblue View Post
Could you mount the wire shelf at 6' 6" and move the brace so it supports the shelf from above?

Last edited by A930Rocket; 01-19-2018 at 04:35 AM..
Old 01-19-2018, 04:26 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #7 (permalink)
Platinum Member
 
dad911's Avatar
 
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 20,879
Put the brackets 32" apart, 1 on each side of panel. (you need 30") and set the shelf at 6’-6”
__________________
Politics is in the eye of the beholder - Rodney Dangerfield
Old 01-19-2018, 04:44 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #8 (permalink)
Registered
 
drkshdw's Avatar
 
Join Date: Jun 2017
Location: Michigan
Posts: 781
Code states the panel can't be in a 'clothes closet'. My local inspector won't allow anything that is meant to hang clothes anywhere near the panel or else to him, it's considered a 'clothes closet' (can't even put a panel in a walk-in closet here). May want to check with your inspector to see what makes an area a 'clothes closet' to them.

Also, why is that panel so close to the floor? Code doesn't have a minimum height requirement but putting it at a childs eye level doesn't seem very smart.
Old 01-19-2018, 05:00 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #9 (permalink)
Platinum Member
 
dad911's Avatar
 
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 20,879
I took that as a pantry shelf/utility closet but you might be right, depends if inspector is a d***.

You could use melamine shelving, can't hang clothes from that.
__________________
Politics is in the eye of the beholder - Rodney Dangerfield
Old 01-19-2018, 05:21 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #10 (permalink)
Registered
 
A930Rocket's Avatar
 
Join Date: Oct 2003
Location: Mount Pleasant, South Carolina
Posts: 14,064
All first floor units are set up for ADA.

That means the box is lower.
Old 01-19-2018, 07:38 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #11 (permalink)
Registered
 
A930Rocket's Avatar
 
Join Date: Oct 2003
Location: Mount Pleasant, South Carolina
Posts: 14,064
You can’t have anything in the way like jackets. Should be free and clear.

Quote:
Originally Posted by dad911 View Post
Put the brackets 32" apart, 1 on each side of panel. (you need 30") and set the shelf at 6’-6”
Old 01-19-2018, 07:39 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #12 (permalink)
 
Registered
 
Join Date: Apr 2005
Location: outta here
Posts: 52,927
Quote:
Originally Posted by A930Rocket View Post
All first floor units are set up for ADA.

That means the box is lower.
I've never heard of an electrical panel being subject to ADA regulations. That must be something new, if it exists at all. Going to be hiring handicapped electricians?

Get rid of the shelf and your problems are solved.
Old 01-19-2018, 07:56 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #13 (permalink)
Registered
 
Join Date: Oct 2005
Location: Capistrano Beach, Ca.
Posts: 7,235
Quote:
Originally Posted by javadog View Post
I've never heard of an electrical panel being subject to ADA regulations. That must be something new, if it exists at all. Going to be hiring handicapped electricians?

Get rid of the shelf and your problems are solved.
Are not homeowners expected to reset a breaker without calling an electrician? Not trying to be argumentative, just raising a point as to why the ADA regulation may be correct.
__________________
L.J.
Recovering Porsche-holic
Gave up trying to stay clean
Stabilized on a Pelican I.V. drip
Old 01-19-2018, 08:09 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #14 (permalink)
Registered
 
A930Rocket's Avatar
 
Join Date: Oct 2003
Location: Mount Pleasant, South Carolina
Posts: 14,064
We had an ADA guru check all the plans and he made changes to make sure everything is ADA compliant. I’m not sure if that was one of his items.

The plans are right. It shows a 3’ shelf and a 3’ area for the panel. It’s a ****up by the electrician and wasn’t caught before I got here. Now it’s too late to move the panel and we have to come up with plan B.

Removing the shelf solves the problem, but leaves no place to hang a coat when you enter or leave. It’s an apartment. Gotta put things where you can.

Quote:
Originally Posted by javadog View Post
I've never heard of an electrical panel being subject to ADA regulations. That must be something new, if it exists at all. Going to be hiring handicapped electricians?

Get rid of the shelf and your problems are solved.

Last edited by A930Rocket; 01-19-2018 at 08:15 AM..
Old 01-19-2018, 08:10 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #15 (permalink)
Registered
 
Join Date: Apr 2005
Location: outta here
Posts: 52,927
ADA regulations apply to commercial buildings. When he referenced buildings in his original post, as in more than one of them, I assumed these were commercial structures not residential structures.

You can argue the other point that if the panel needs to be at that height, the shelf is way too high.
Old 01-19-2018, 08:13 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #16 (permalink)
Registered
 
Join Date: Apr 2005
Location: outta here
Posts: 52,927
Buy a bunch of freestanding coat racks?

How did nobody catch this when the panels were first roughed in?

Last edited by javadog; 01-19-2018 at 09:28 AM..
Old 01-19-2018, 08:15 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #17 (permalink)
Registered
 
Join Date: Oct 2005
Location: Capistrano Beach, Ca.
Posts: 7,235
Quote:
Originally Posted by A930Rocket View Post
We had an ADA guru check all the plans and he made changes to make sure everything is ADA compliant. I’m not sure if that was one of his items.

Removing the shelf solves the problem, but leaves no place to hang a coat when you enter or leave. It’s an apartment. Gotta put thingsvwhere you can.
Can you clear up something for me? Please forgive me if I'm completely off the mark.



The picture you posted is of a properly placed panel, correct? The one you have an issue with has the panel (the dark one in the picture) placed closer to the wall where the light switch is located, correct? If my assumptions are correct, why couldn't the shelf be moved further away from the wall, outside the left side limit of the panel clearance, and supported by two angled braces? It would be above the white panel, but is that white panel also under the same clearance requirements?
__________________
L.J.
Recovering Porsche-holic
Gave up trying to stay clean
Stabilized on a Pelican I.V. drip
Old 01-19-2018, 08:18 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #18 (permalink)
Baz Baz is online now
G'day!
 
Baz's Avatar
 
Join Date: Sep 2008
Location: New Smyrna Beach, Florida
Posts: 45,371
Garage
Don't install shelves until after the inspection.
__________________
Old dog....new tricks.....
Old 01-19-2018, 09:01 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #19 (permalink)
Registered
 
A930Rocket's Avatar
 
Join Date: Oct 2003
Location: Mount Pleasant, South Carolina
Posts: 14,064
That’s what my wife said!
The owner is an ass, so I didn’t offer too many solutions.

How was it missed? Lack of supervision by the electrician and former supervisor.

Quote:
Originally Posted by javadog View Post
Buy a bunch of freestanding coat racks?

How did nobody catch this one the panels were first roughed in?

Old 01-19-2018, 09:26 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #20 (permalink)
Reply

Thread Tools
Rate This Thread
Rate This Thread:

 


All times are GMT -8. The time now is 08:52 PM.


 
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2025, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2025 Pelican Parts, LLC - Posts may be archived for display on the Pelican Parts Website -    DMCA Registered Agent Contact Page
 

DTO Garage Plus vBulletin Plugins by Drive Thru Online, Inc.