Measuring using a Fluke multimeter across common black to common white.
Redid my tests this morning, and I realized that I did not use the common neutral when testing the switches in the on position, I used the ground.
I get 120V with the switch in the off position using hot inlet and common neutral.
I get 120V withe the switch in the on position using hot outlet and ground.
However, I do not get 120V with the switch in the on position using hot outlet and common neutral.
So on my way to the panel to inspect the neutral connection on the bus bar.
Maybe a loose connection that gives 120V at low amps, but not 120V at full load amps.
We will see!