Where is the main panel located? Basement?
If the walls are not structural in any way, remove a stud on one side and move it over.
Typically plenty of knockouts on the sides of those residential panels. Pull the front cover of the panel and check this before making any changes and check your local code.
If you are using hard conduit all the way to the panel, I would suggest a pull box instead of the pull LB that you have on the end. Easier to pull you wire (Rawknees should be commenting shortly) through the box and you can leave a bit extra looped in the box in case of any changes down the road. YMMV.
edit;
Empty flex is fine here for that last run into the panel.
The two hole straps you are using for the emt would not pass inspection here unless both sides were fastened to a 2x4 or some backer.