Sean, you are running an undersized transformer for a single phase motor on a three phase system.

Perhaps this has been contributing to your problems all along.

You are running an unbalanced load for extended periods with an undersized transformer and undersized wires.

Please bring someone in there and don't get offended at what they say/do.