Originally Posted by Tidybuoy View Post
I'd like to be as close to code as possible but my house is 72 years old so not everything can be accomplished (easily). That said,......
By National Electric Code, kitchens are supposed to have 2 -20 Amp GFI circuits feeding the countertop receptacles. That's 12 gauge wire. Spacing is 4' or less, and less than 2' from each end of the counter. So a 4' counter needs at least 1 centered receptacle, a 5' counter would need 2 receptacles spaced less than 4' apart. In theory, an appliance with a 24" cord should not need an extension.

NEC 210.52 https://up.codes/viewer/new_jersey/nfpa-70-2017/chapter/2/wiring-and-protection#210