Compare the number tags to t he wiring diagram. This is not a wye delta motor. It is a wye wound motor and the star point is not accessible. High voltage config places two (correct) windings in series for each of the three phases. Low voltage is like two wye wound motors connected in parallel.
Is the coil voltage 120? If you bring in a neutral leg any one of your three phases will suffice as a control voltage. Make sure that all the components are grounded properly.
Forgot you were on a single phase service. Ymmv.
|