I'm not an electrician by trade, but your #6-3 would be rated for max 60A breaker at main panel, if running through attic you would derate that wire a little depending on attic temp. As Zeke mentioned you should run the AC direct to main panel or you could run new #3 wire and install 100A subpanel in your laundry room.