.......This is not a work shop . Outlets will be used for a battery charger for tractor or anything with minimal draw . I was thinking I might be able to get away with # 10 wire ? And maybe use a 20 or 25 amp double pole breaker ? Fire away gentleman 
|
Only 2 circuits, outlets and lights? Chargers and lights(LED) are very low current.
I'd skip the subpanel and pull 2 blacks, 2 whites, 2 grounds, all #12, and split the lights and outlets between these 2 circuits..... and I'd probably pull 3 of each so there is a spare.
1" sched80 pvc capacity is 20 wires, so you are not even close.
I usually lay out the wire next to the trench, slide pipe over it and glue as you go. Much easier than pulling, imho. Add a pull string for the future, if you need to pull more conductors later.