On some Rheem units, check the fiberglass insulation pads on the sides of the blower housing. After a few years the contact cement holding these pads can fail, and they get sucked up against the blower inlet blocking off the airflow. With insufficient airflow the evaporator freezes-up. Since the insulation falls back into its normal position with the blower off this is an easy thing to miss during inspection.