Look at section A8. What does the elevation cert state for enclosure size (a)? How about the amount of venting (b)? The venting needs to equal or exceed the enclosure size.

The hot water heater being below base flood is at least part of the problem. Do you have room to raise it up? The bottom needs to be at least equal to the base flood. The last pic looks like the vents are closed?