If you have 230 volts you only need one neutral. If you have two 115 volt circuits you need two neutrals.
That is not true. With a split phase system, like here in the US, you only need one if the legs of the 115 are on different phases


EDIT: This is the only requirement which no one seems to follow:

Quote:
(B) Dwelling Units. In dwelling units, a multiwire branch
circuit supplying more than one device or equipment on the
same yoke shall be provided with a means to disconnect
simultaneously all ungrounded conductors at the panelboard
where the branch circuit originated.
and no I am not an electrician.