Quote:
Originally Posted by dad911 View Post
Not Correct, Often use (multiple) 15A receptacles on a 20A circuit, done in Kitchens, Dining Rooms, etc. See NEC code section 210.21 (B), and Table 210.21(B)(3)

A 15amp receptacle on a 20 amp circuit will not overload the circuit. You will only be allowed to plug in 15a devices. 20 Amp receptacles/plugs have a 'T' configuration.
That would never fly in NY, and I would never install it. The 15amp device/receptacle could melt down before the breaker ever tripped. Especially with an extension cord.