Originally Posted by legion View Post
So far, this is what I have learned:

-Separate circuits for lights vs. outlets
-Conduit and GFCIs on outlets on walls against concrete
-No more 13 outlets per circuit

Remaining questions:
-It is my understanding that code requires an outlet every 6 feet, is this correct?
-What gauge wire should I use for outlets?
-What amperage breaker should I use for outlets?
-At what height should I mount outlets at?
You can use Romex if you staple to a stud of the the framed walls in basement, not foundation wall.

14 gauge, 15 amp. Outlets within 6 feet from an opening (doorway, etc) then less than 12' apart.

They can be at std heights, and don't need to be GFI, unless there is a chance of getting wet/flood zone.