Check the neutral line. If one side has a higher load (like 120 A/C & Fridges) and the neutral is bad feeding the house, the other leg will spike. In other words, feed to house is 240ish. If one side goes down to 90v, without a neutral the other will be 150v.
Happened to my son. Burning out light bulbs because of a bad neutral at the pole.