Are you comfortable measuring AC volts in the panel?
If so, next time you have a problem, measure:
1) 2 lugs near top of panel, where the 2 heave black wires connect. If you get 220-240, then lines coming in are ok,
2) Output (2 screws) on the main 50 amp breaker. If #1 is ok, but these are less than 220-240, then the main breaker is bad.
However, if it was me, I'd probably turn off the A/C, eat out (don't use range/oven) trying not to 'draw heavy current' until your electrician checks it out......