It makes you wonder how many installs are working but not working well. Owners don't know they just think it's a bit more expensive and less efficient than they had expected....
Bingo! At this point I'm somewhat happy to say the AC contractor now agrees something odd is happening. Now we can cut the bravo sierra and start diagnosing the issue.
Sold: 1989 3.2 coupe, 112k miles
Old 10-12-2023, 04:20 AM
Mighty Meatlocker Turbo
Rawknees'Turbo's Avatar
There is a good chance that they either did not get all of the air and moisture out of the system after all (possibly due to an unfound leak, as indicated by one of your vacuum charts), or did not add the proper amount of refrigerant (too much or too little), given the strange rise in evaporator temps even when the compressor is running.
Mini-splits come with the compressor pre-loaded with refrigerant that is sufficient for whatever length of piping the install manual specifies (more must be added if that length is exceeded); with your complex system (multiple evaporators/head units), I'm betting the installers did not correctly calculate how much additional refrigerant to add.
When set up correctly, those Mitsubishi's are capable of bone chilling cooling, way beyond what a normal person (me being abnormal! ) would ever want.
Old 10-12-2023, 05:41 PM
Good thinking.
1 - They/we did many evacuation runs with the last couple under 500 (~420) microns. From all my reading under 500 is good. However 420 is certainly nothing to write home about. I think the system is dry enough to operate to spec.
2 - They were aware that a calculated amount of R410A needed to be added - two people checked the calculation. Of course they could have still put in not enough.
3- Your last point is the best - When properly installed and setup I should get "beer" cold air.
He now admits something is off.
Old 10-13-2023, 05:22 AM
I think I'm finally getting somewhere on this. What do we know now:
1 - The one GL wall unit appears to be somewhat okay running by itself. The controls work and it tries to heat and cool.
2 - The GL unit doesn't, at this point, have the capacity to cool the big room enough.
3 - When two or more of the smaller bedroom units are turned on the "big" GL unit all but stops cooling.
This brings to mind a question. When the GL (24,000 Btu) unit is running alone is it cooling near its capacity? How would we test this? Fortunately the CFM for the 5 different fan speeds are in the service manual. I should have thought of this before... it is easy to calculate the cooling provided (Btu/Hr.) using the very common equation Q=1.08*dtF*CFM. So I tested the unit while on full cooling (min. set point of 61F) at the 5 different fan speeds and this is what I got.
What do you think now?
Old 10-15-2023, 09:37 AM
rfuerst911sc's Avatar
Just for a data point my man cave garage is 24x26x12 foot high ceiling . Has 2x6 walls with R19 fiberglass insulation . The ceiling is also R19 . Two garage doors are insulated . So overall a fairly tight building .
The Mitsubishi 24k mini split can get the interior to meat locker quickly . I have never timed it but my guess is less than an hour after turn on . Likewise in heat mode it heats quickly . Just a single head unit .
Past experience with a 3 bay garage in my previous house again with a 24k Mitsubishi was similar . I guess in both cases my installer did a great job . When installed properly the performance is excellent in my opinion .
Old 10-15-2023, 09:58 AM
Good data point. Thanks. Your MC is very similar size to our family room. We have a vaulted ceiling with good insulation. However, we have two large windows that get sun until about 2PM or so and part of the room is open to the kitchen.
The contractor is being a bit quiet right now. At some point I might need an independent evaluation and see if the system is capable or has an issue.
If you have a way to measure air temperature and don't mind checking - maybe you can measure the coil input and exhaust temps for me to compare. I've seen a few measurements in the high 40sF but those don't last long. Probably will require a ladder to get to the top of the coil. The controls work by looking at the set point and air temp. going in the coil. That's what "people" are saying.
Thanks in any case.
Old 10-15-2023, 11:01 AM
@rfuerst, If you want to do some measurements I suggest.....
Fan speed 3, vanes down 3 "notches", setpoint 61F. I assume you have a GL24 unit but if different please send out the model #.
Thanks.
Old 10-15-2023, 12:12 PM
hcoles, those head units have three temperature sensors - one on the evaporator's in pipe, one on out pipe, and a room sensor that is beneath the cover, to the side of the LED display/sensor for remote control (there are a couple of small slits on the side of the cover and the room sensor is there - it basically looks like a short, thin black wire . . . can't see it without removing the cover/case however). I know this because I had to make mods to those when installing my aftermarket controller.
With my fan speed on the second from highest setting (not the "powerful" setting), and the remote control temp set at 61 (my aftermarket controller not operating at the time), the air exiting the evaporator is consistently in the 45-48 degree range (with aftermarket controller running the exit air temp gets much lower).
My model is GL24 (a/c version only - no heat pump function).
Based on what you've described above, it sure seems like there has been an error made in the amount of refrigerant added. Unfortunately, your best option at this point is probably going to be getting someone else to look at/test the system, as long as you can find a tech that you are confident he/she knows what they are doing (based on your remark about installer business going quiet).
Old 10-15-2023, 02:26 PM
Good info. Thanks. At this point I think you might be right re. getting someone to look at the system. My contractor gave me a sheet from Diamond System Builder. I have seen 48-50F discharge temps. from my GL24 but not for very long. Maybe as you say the system is low on 410A. But there are no codes flashing from the LEV sensor indicating low charge.
Old 10-16-2023, 06:09 AM
Okay people, the saga continues.
During hot days the large family room unit goes to a high (+65F) discharge temp. when it should keep supplying cold air. The contractor agrees something is not right.
I've been watching them closely e.g. during the pressure and vacuum processes because I found the brazing "issue" and ground wires placed in the panel on the wrong bus. Then the vacuum process had poor performance due to worn out equipment/etc. Anyway - I'm watching them like a hawk.
Now the GM and lead tech. wants to come and work on the system - AND - doesn't want me to be near where they are working. I suspect many reasons but of course not sure why he would all of a sudden change how we are working. My main concern is he will again not do a good job during the vacuum process and doesn't want me to see him do that.
Am I being unreasonable to want to know exactly what they are doing?
Old 11-12-2023, 05:28 AM
Put the shoe on the other foot. When you are working on something and it isn’t going well, do you want someone right there watching, asking questions and making comments? I say, let them have a go at it while you are away and see if that makes a difference.
Rutager West
Old 11-12-2023, 05:50 AM
A couple simple things to check with the contractor. Is the vacuum pump a minimum 3-5 CFM capacity? Is pump oil clean, should be changed after each use as contaminates, moisture are captured in the oil. Does pump pull below 500 microns when “blocked” off? Does the tech know triple sweep, double evacuation procedure? Did they purge the line set with nitrogen before brazing to prevent oxidation? Looks like they used foscopper brazing solder on the lines, not silver solder or silfos or stabrite. You should talk to the tech intelligently before he starts to work as rwest suggests, so he knows you’re pretty well versed as to what’s happening with the system. Good luck, hopefully the problem will be resolved.
Old 11-12-2023, 08:26 AM
Bob, thanks for the interest and comments.
FYI - When the system was first installed they pressure tested with nitrogen and vacuumed the system. This is where we hit a snag. I read the Mitsubishi manual that describes the vacuum process and specs. Their equipment initially was not capable because it was worn out and needed maintenance. I figured all this out and they finally showed up with much better equipment and pulled an "okay" vacuum.
So, I feel justified in being skeptical and wanting to watch closely to what they might do. I understand it is not comfortable to have someone watching over you when working. The bottom line is at this point - when someone makes a big change (very open to don't be near us) without explanation - it makes me feel they are untrustworthy.
Old 11-12-2023, 08:48 AM
Zeke's Avatar
I've always maintained that if you want to watch (not under all circumstances, depends on what tools are being used) go ahead because I know what I'm doing and it doesn't make any difference.
But stay quiet.
Comment below and don't forget to like and subscribe.
Old 11-12-2023, 09:29 AM
Like Zeke says, stay quiet but keep your eyes open. You’ve been armed with plenty of info from the board to have a pretty good idea of what’s going on. I wonder if the techs are NATE certified? Years ago, I had my techs attend Carrier and Trane tech schools to learn how their equipment should be serviced including understanding a psychometric chart to properly charge a system. At least the hvac owner is standing by his installation and hopefully the issues will be resolved. Best of luck….
Old 11-12-2023, 09:44 AM
The contractor is part of the Mitsubishi Diamond Contractor program. This is supposed to mean at least one employee has been to Mitsubishi for training. I think there are also some on-going training requirements.
Re. psychometric chart - as I understand mini-split systems don't "use" the chart in the same way as standard AC. E.g. there appears to be only one tap (on the pressure side).
My contractor has one person and that person lives ~2000 miles away, TX vs CA.
Old 11-13-2023, 05:54 AM
Minor update. The head guy from the contractor called and we discussed why sometimes people don't like to be watched/etc. So I guess all is going okay - I can still watch what they are doing bit I guess be careful what I say. I don't know - positive progress I guess.
Old 11-13-2023, 05:53 PM
FUSHIGI
Taking over 2 months to correct their usual and customary installation strongly suggests nobody has taken them to the mat on their crappy work before.
Cults require delusions.
Old 11-13-2023, 06:33 PM
I've been reading about mini-splits and watching YouTube, there is a lot of info. out there. What I'm getting is... Mini-splits are a different animal compared to what installers worked on 20-30 years ago. They are less forgiving of poor installation practices that worked okay in the past. One guy on the HVACtalk forum, said residential work doesn't pay enough for us to do good work. My feeling is that someone that knows what they are doing can do correct work without too much more time/materials being used. For me, I'm willing to pay the additional amount but many probably go for the lowest bid. The issue is you don't know all this until you have selected your contractor and watched what they do.
Old 11-14-2023, 06:41 AM
I think some of you here are HVAC technicians or very interested so here is an update.
Their best technician came Friday Nov 17 to find out what is going on. Most if not all of the LED flashing codes indicated a low refrigerant level. So they decided to pull the charge and weigh it. It weighed 3.5lbs instead of 9,8lbs. So they (tech. phoned manager) concluded there is a leak. Pressurized with nitrogen to 600psig in attempt to find the leak(s). Hooked up a digital pressure gauge set Testo 550s. The pressure was dropping. Found a leaking flare fitting right at the outside unit. Checked all the coils and flare fittings at the inside units, using a sonic sniffer, and didn't find any leaks. Closed the isolation valves and hooked one tap on the Testo on the "machine" side and the other on the "house" side. This was a way to isolate where a leak might be if there is one remaining. Initially the machine side was dropping but we were in the afternoon and things were getting colder so not sure what is happening.
I'll attach graphs for comment.
Thanks.
Old 11-22-2023, 06:32 AM