Quote:
Originally Posted by greglepore View Post
What do you see at the 30 amp breaker FEEDING the sub panel. You should see 220v across the two breaker terminals, and 110v from each to the respective leg of the buss bar.
123V from the individual legs to the bus bar, 246V across the breaker terminals.

_

__________________
When in doubt, use overwhelming force.
Old 05-03-2024, 09:34 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #21 (permalink)
Preferred pronoun:Maestro
 
Norm K's Avatar
 
Join Date: Sep 2012
Location: Group W Bench
Posts: 11,355
Quote:
Originally Posted by greglepore View Post
The other thing is, from the photo of the subpanel, I only see one leg on the buss bar. Normal 220 practice is red and black wires are the two phases and white is neutral. All I see is a black wire on the buss bar. Not saying the other phase isn't there but I don't see it.

There's no red wire in the sub-panel. So I have a 240V breaker at the main panel that appears to be doing what it's supposed to do, but only 120V at the sub.

The system has worked as-is for several years, then after it suddenly self-energizes, won't function properly after being turned off, then on, then some new parts, more ons and offs, rinse and repeat, all to no avail (except for two normal surges of water that both ceased once a zone was selected).

I'm about to call a professional but I'm so GD cheap in retirement that I really don't want to.

_
__________________
When in doubt, use overwhelming force.
Old 05-03-2024, 09:42 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #22 (permalink)
Registered
 
Join Date: Sep 2009
Location: North of You
Posts: 9,160
Quote:
Originally Posted by Norm K View Post
123V from the individual legs to the bus bar, 246V across the breaker terminals.

_
You show A-B as 120VAC in an earlier post. Is it actually 230V?

You breaker box does not look like it has 230VAC, but I can't see the whole box...

Is it possible your motor is wired for 120VAC?
__________________
"A machine you build yourself is a vote for a different way of life. There are things you have to earn with your hands."
Old 05-03-2024, 09:43 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #23 (permalink)
Registered
 
Zeke's Avatar
 
Join Date: Jan 2002
Location: Long Beach CA, the sewer by the sea.
Posts: 38,266
Quote:
Originally Posted by greglepore View Post
The other thing is, from the photo of the subpanel, I only see one leg on the buss bar. Normal 220 practice is red and black wires are the two phases and white is neutral. All I see is a black wire on the buss bar. Not saying the other phase isn't there but I don't see it.
I think the black is running behind the bus. BTW, it's not buss.

So the 120v circuit powers the zone controller, right? I do believe that needs to be checked if all else is correct and it sounds like it is.
Old 05-03-2024, 10:03 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #24 (permalink)
Preferred pronoun:Maestro
 
Norm K's Avatar
 
Join Date: Sep 2012
Location: Group W Bench
Posts: 11,355
Quote:
Originally Posted by 1990C4S View Post
You show A-B as 120VAC in an earlier post. Is it actually 230V? No, it's 120V.

You breaker box does not look like it has 230VAC, but I can't see the whole box...

Is it possible your motor is wired for 120VAC? It's certainly possible, but I don't understand why I have e a 240V circuit in the main panel but only 120V at the sub.
__
__________________
When in doubt, use overwhelming force.
Old 05-03-2024, 10:58 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #25 (permalink)
Registered
 
Join Date: Sep 2009
Location: North of You
Posts: 9,160
Turn the two breakers on. Measure A-B voltage.

Measure L2-L3 voltage on the relay.

Measure T2-T3 voltage on the relay when the pump is running.

They should all be 220 VAC...

__________________
"A machine you build yourself is a vote for a different way of life. There are things you have to earn with your hands."

Last edited by 1990C4S; 05-03-2024 at 04:01 PM..
Old 05-03-2024, 03:56 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #26 (permalink)
 
Reply


 


All times are GMT -8. The time now is 02:15 PM.


 
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2026, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2025 Pelican Parts, LLC - Posts may be archived for display on the Pelican Parts Website -    DMCA Registered Agent Contact Page
 

DTO Garage Plus vBulletin Plugins by Drive Thru Online, Inc.