mikehinton 02-11-2013 02:34 PM

Electrical Help Needed
 
About 7 years ago, I installed a new wiring system for my shop, barn, and a couple of other outbuildings. All 4 of the circuits are serviced by a sub-panel, which was installed by our electrician. I did all of the other wiring myself (I've done similar projects several times over the last 20+ years). The circuits are all very simple - just a bunch of outlets with a few switched outlets for fluorescent lighting. There are no 3-way switches anywhere.

Everything worked fine upon installation, and continued to work fine until a couple of weeks ago. I went out to the barn to plug in a battery charger, and no power. Went to the box and found that the circuit breaker had tripped. That seemed odd, but I just reset it and continued on. A couple of days later, I went to turn on overhead lights, and same circuit was tripped. Strange. Reset it and continued. Last week, I encountered the same thing. This time, when I reset the circuit, I heard a "pop" coming from the barn, and the breaker tripped again. As far as I can tell, there was no load on the circuit when the breaker tripped.

So, I'm figuring that there must be a short somewhere in that circuit. A couple of questions: 1. Why would a short suddenly manifest itself after 7+ years? 2. Is there a way to track down the source without disconnecting everything? The "pop" I heard was coming from a junction box in the barn. When I removed the cover, the large wire nut (joining 6 neutral wires) was burnt to a crisp.

Any advice appreciated! Thanks for reading!

Mike

Bill Verburg 02-11-2013 02:45 PM

Quote:

Originally Posted by mikehinton (Post 7267567)
About 7 years ago, I installed a new wiring system for my shop, barn, and a couple of other outbuildings. All 4 of the circuits are serviced by a sub-panel, which was installed by our electrician. I did all of the other wiring myself (I've done similar projects several times over the last 20+ years). The circuits are all very simple - just a bunch of outlets with a few switched outlets for fluorescent lighting. There are no 3-way switches anywhere.

Everything worked fine upon installation, and continued to work fine until a couple of weeks ago. I went out to the barn to plug in a battery charger, and no power. Went to the box and found that the circuit breaker had tripped. That seemed odd, but I just reset it and continued on. A couple of days later, I went to turn on overhead lights, and same circuit was tripped. Strange. Reset it and continued. Last week, I encountered the same thing. This time, when I reset the circuit, I heard a "pop" coming from the barn, and the breaker tripped again. As far as I can tell, there was no load on the circuit when the breaker tripped.

So, I'm figuring that there must be a short somewhere in that circuit. A couple of questions: 1. Why would a short suddenly manifest itself after 7+ years? 2. Is there a way to track down the source without disconnecting everything? The "pop" I heard was coming from a junction box in the barn. When I removed the cover, the large wire nut (joining 6 neutral wires) was burnt to a crisp.

Any advice appreciated! Thanks for reading!

Mike

Is any of the wire separate tnn wire in conduit? I had a similar occurrence after 10 yrs in service except the breakers and GFI didn't trip, there was just no power in one leg. The wire had apparently been nicked when pulled and it took all those years of arcing to ground to finally erode the wire to the point that it would no longer conduct. The funny thing was that per code all the conduit was plastic except where the nick was, under a paved drive. At that point code called for metal conduit which facilitated the arc.

rick-l 02-11-2013 02:51 PM

Are those Ground fault interrupters in the sub panel?

krystar 02-11-2013 02:58 PM

1) bad flourescent ballast
1b) condensation water+rust bubble?
1c) rodents?

guessing the real fault is somewhere downstream of that wire nut. wire nut just acted as a slow burn fuse.

mikehinton 02-11-2013 03:24 PM

All wire in the circuits is 12/2 Romex, so no separate TNN wires. All conduit is EMT above ground and PVC below. No GFI outlets anywhere in the system.

Is there a way to test for a short?

Red88Carrera 02-11-2013 03:27 PM

Quote:

Originally Posted by mikehinton (Post 7267567)
When I removed the cover, the large wire nut (joining 6 neutral wires) was burnt to a crisp.

I think you already found the problem. Most likely came loose and burned up over time, causing the symptoms you had.

mikehinton 02-11-2013 03:31 PM

I did replace the fried wire nut, but that didn't solve the problem...

john70t 02-11-2013 03:54 PM

Quote:

Originally Posted by Red88Carrera (Post 7267684)
I think you already found the problem.

Not an electrician but..
There shouldn't be any junction boxes. Definitely not on a main leg.

The wiring from the house to garage sub panel should be continuous and oversized for total load.
That includes lights, compressor, and welder being used at the same time.
Feed wire and breaker should be same stats, or breaker should trip early. That's the safety link.

Then, each leg in garage should be connected individually to bus and breaker.

Red88Carrera 02-11-2013 04:15 PM

If it's NM/B romex it can't be used underground, even in conduit. That's considered a wet location. Romex is not rated for wet locations.

mikehinton 02-11-2013 04:28 PM

I guess I should have added that the main supply lines to the various buildings are either 6 gauge or 8 gauge individual wires running in PVC conduit. I'm fairly certain that that is the case also for the wires going from the main service entrance panel on the house to the sub panel. I didn't actually witness that installation, but it was done by a well-known electrical contractor here in the Napa Valley.

I don't think there is actually any Romex underground, but if there is, it's the gray stuff that's rated for damp locations.

The junction box I'm referring to takes the feed from the main wires, and distributes it to the outlets and light fixtures in the barn.

Red88Carrera 02-11-2013 04:33 PM

Good to hear that. So if I understand correctly, you're saying that the breaker tripped even with everything unplugged and switches turned off? You're absolutely sure of it?

74-911 02-11-2013 05:01 PM

Bad breaker ??

mikehinton 02-11-2013 05:02 PM

I'm pretty sure that's correct. I still need to unplug the overhead fluorescent lights, but they are controlled by a switch. I'll check tonight and see if anything else is plugged in down the line. If there's nothing plugged in, it would have to be a short somewhere, correct?

Bill Verburg 02-11-2013 05:03 PM

Quote:

Originally Posted by Red88Carrera (Post 7267684)
I think you already found the problem. Most likely came loose and burned up over time, causing the symptoms you had.

I didn't see that on first read, I agree that's the problem.

why are 6 whites bonded the only place that many whites should come together is at a sub-panel where they are individually bonded to the bus. Wire nutting that many 12-2 wires is asking for trouble.

mikehinton 02-11-2013 05:03 PM

I already replaced the breaker too :(

Red88Carrera 02-11-2013 05:09 PM

Quote:

Originally Posted by Bill Verburg (Post 7267872)
I didn't see that on first read, I agree that's the problem.

why are 6 whites bonded the only place that many whites should come together is at a sub-panel where they are individually bonded to the bus. Wire nutting that many 12-2 wires is asking for trouble.

I agree that it's not a good practice, but if there is nothing turned on or plugged in, it wouldn't cause the breaker to trip.

Red88Carrera 02-11-2013 05:11 PM

Quote:

Originally Posted by mikehinton (Post 7267869)
I'm pretty sure that's correct. I still need to unplug the overhead fluorescent lights, but they are controlled by a switch. I'll check tonight and see if anything else is plugged in down the line. If there's nothing plugged in, it would have to be a short somewhere, correct?

I would agree with that. If you find other devices plugged in, check to see what the voltage is on that circuit.

look 171 02-11-2013 05:16 PM

Look at the connector or clamp. Sometimes they over tighten it or pull on it with the clamp tight and cut the wires. Rodens, or ....

I must run, but I will try to read through the posts and see if I can help you solve it later tonight. It sounds like an easy issue to isolate.

mikehinton 02-11-2013 07:39 PM

OK. Got home tonight and made sure everything was unplugged. Circuit still trips after about 60 seconds. I guess the next step is to start disconnecting things at the junction box in order to isolate the "bad" circuit...

look 171 02-11-2013 07:58 PM

Quote:

Originally Posted by mikehinton (Post 7267800)
I guess I should have added that the main supply lines to the various buildings are either 6 gauge or 8 gauge individual wires running in PVC conduit. I'm fairly certain that that is the case also for the wires going from the main service entrance panel on the house to the sub panel. I didn't actually witness that installation, but it was done by a well-known electrical contractor here in the Napa Valley.

I don't think there is actually any Romex underground, but if there is, it's the gray stuff that's rated for damp locations.

The junction box I'm referring to takes the feed from the main wires, and distributes it to the outlets and light fixtures in the barn.

I don't know about that gray stuff. We would never use it and some inspectors will not pass it. I actually don't think its code.

look 171 02-11-2013 08:04 PM

I can't see what's going on there. Which one of the circuit is tripping, outlets or lighting? Go as far back as you can and disconnect that section at the J box and see if that trips the breaker. If it does not, then you know its downstream. If it still does, then its up stream. It can be several things like a nail through the Romex, roden, or a cut on the wire at the metal connectors. Did you use metal boxes?

mikehinton 02-11-2013 08:22 PM

There are mostly outlets on the circuit. There is one switched overhead lighting fixture. The "gray stuff" I was referring to earlier is the direct burial style of Romex. It's in PVC conduit. I don't think it could be nail damage, since all exposed Romex is in EMT conduit, and there haven't been any construction projects near the circuitry. There is one branch of the circuit that was added later that services a couple of outlets, but that circuit has worked fine for a couple of years. I think I'll disconnect that one first and see what happens. A project for daylight tomorrow...

mikehinton 02-11-2013 08:23 PM

Oh, and metal boxes were used indoors; weatherproof PVC outdoors.

Jim Sims 02-11-2013 09:17 PM

It would appear this installation is below code requirements - beginning with the lack of GFI equipment. The wire nutting of a bunch of neutrals together should also likely result in red tagging. However the correct installation and isolation of the neutral and grounding bus bars for subpanels is often missed by professional electricians. See: http://www.creia.org/images/stories/sub-panel-grounding.pdf

Sounds like it's time for a rework by someone who is up to speed on the code.

look 171 02-11-2013 10:21 PM

Check those Romex connectors in the first picture on the second page in Jim's link above. Sometimes they are cut there because of over tightening. I think something might have come part in one of the J boxes.

nowaydude 02-12-2013 04:53 AM

Shut the light off and turn on the breaker see if it still trips.if it doesn't its the light circuit.If it does leave someone in the room in the dark turn on the breaker and see if there is an arc when it trips they will see where it's general location is ,maybe hear it too. Start pulling out the outlets see if you see any burn marks ( power off ) generally hot wire wire hitting metal box some where.

mikehinton 02-12-2013 08:19 AM

Thanks for the suggestions. I'll check the j boxes when I get home tonight. I can hear the arcing in my barn, and I have an idea about where it is. I'll disconnect that branch line tonight and see if it solves the problem.

1990C4S 02-12-2013 10:32 AM

You could have a bad circuit breaker. Borrow a clamp-on ammeter and measure the current.

I don't believe the burned common is the problem, that should not cause your circuit breaker to trip unless it is causing a heavy starting load to cycle repeatedly (like an air compressor or a fridge).

If there is no visual damage then you need a megger to do an insulation test.

mikehinton 02-12-2013 11:37 AM

A bad circuit breaker was my first thought, since the breaker was tripping with zero or minimal load on the circuit. I've already replaced the breaker, with no effect on the problem. The entire circuit is generally subjected to minimal loads - a couple of fluorescent lights (corded, that are plugged into outlets), and battery chargers. There is an air compressor that is used occasionally, but it's never tripped the breaker. Last night, after I unplugged all loads from the circuit, and reset the breaker, it tripped after 60-90 seconds. Very strange...

There are three other breakers in the sub panel. None of those has ever tripped.

1990C4S 02-12-2013 02:31 PM

You need to start disconnecting loads/lines from the circuit until it doesn't trip. Start at the circuit breaker itself, and then work towards the end.

Are you sure this is just a circuit breaker, not an arc fault or ground fault breaker?

look 171 02-12-2013 02:45 PM

You must have a cut wire somewhere that grounding itself. Now its just a process of elimination.

mikehinton 02-12-2013 04:35 PM

Pretty sure it's just a circuit breaker, as only one is affected in the sub panel. I agree that the process is to start disconnecting the branches on the circuit one by one until it stops misbehaving. That process will begin tonight... ;)

johnsjmc 02-12-2013 05:07 PM

Quote:

Originally Posted by mikehinton (Post 7270164)
Pretty sure it's just a circuit breaker, as only one is affected in the sub panel. I agree that the process is to start disconnecting the branches on the circuit one by one until it stops misbehaving. That process will begin tonight... ;)

If you can "hear" arcing noise from somewhere in your shop I doubt it is a bad breaker, Substitute a known good breaker (of same amp rating) from another circuit and see if the problem moves with the breaker.
I had a similar situation develop with a circ running my compressor It would spark once in a while and pop a breaker. Turned out to be a piched wire behind it which only shorted to the compressor when running (and vibrating)

look 171 02-12-2013 06:23 PM

Quote:

Originally Posted by mikehinton (Post 7270164)
Pretty sure it's just a circuit breaker, as only one is affected in the sub panel. I agree that the process is to start disconnecting the branches on the circuit one by one until it stops misbehaving. That process will begin tonight... ;)

I wish it was that easy, I really don't think its a bad breaker. LIke John said, swap another one in there and see. Simple and easy if you have no testing tools.

nowaydude 02-13-2013 05:44 AM

Turn it on and listen for the hissing,general area and start there.Look in the dark for arching,Like looking for bad spark plug wires at night. Start there. Sounds like a wire is grounding but not a dead ground.look for burnt wires. Look ,listen,smell. LOL!

mikehinton 02-13-2013 09:27 AM

Sorry. Last night I meant to say that I was pretty sure it was NOT a bad circuit breaker, as I've already replaced the offending one with a new one. I disconnected the "prime suspect" branch last night, but that wasn't the problem. I'll start on the others tonight. If that doesn't cure the problem, then I'm guessing that the issue would have to be in the 6-gauge wires that bring the power from the sub panel to the various buildings. We do have gophers, but have they been known to chew through underground PVC conduit?

johnsjmc 02-13-2013 10:13 AM

Problem cant be in your 6 g supply wires. The circuits should be set up with a breaker protecting the 6 g wires at the supply panel (60A). You should have 20 or 15 A breakers protecting your branch circuits (depending on wire size either 12g or 14g. Breakers protect the wire downstream not upstream at the supply.
When you say you disconnected the branch but it wasn,t the problem .How did you determine that? With no load connected the breaker wont trip.
I would look for the source of your crack /snap sound in the other room and start there.

mikehinton 02-13-2013 11:01 AM

I disconnected the branch circuit at its junction box, then reset the breaker to "on." It tripped within about 60 seconds. I could hear the noise in the barn (where a couple of the junction boxes are), but didn't see any visible arcing (it was pitch black in there). When I was speculating about the supply lines, maybe I should have said that the 6 (or 8) gauge wires take the power from the 20 amp breaker in the sub panel to three separate outbuildings via underground PVC conduit. If those supply wires became compromised (e.g. if a gopher chewed through the PVC and wire insulation), that would also trip the breaker, wouldn't it? I'm hoping I don't have to dig up 150 feet of conduit to find the problem :D

johnsjmc 02-13-2013 11:20 AM

Quote:

Originally Posted by mikehinton (Post 7271527)
I disconnected the branch circuit at its junction box, then reset the breaker to "on." It tripped within about 60 seconds. I could hear the noise in the barn (where a couple of the junction boxes are), but didn't see any visible arcing (it was pitch black in there). When I was speculating about the supply lines, maybe I should have said that the 6 (or 8) gauge wires take the power from the 20 amp breaker in the sub panel to three separate outbuildings via underground PVC conduit. If those supply wires became compromised (e.g. if a gopher chewed through the PVC and wire insulation), that would also trip the breaker, wouldn't it? I'm hoping I don't have to dig up 150 feet of conduit to find the problem :D

I don,t understand how you can disconnect the breaker from its branch and still have it connected to something in another room? I mean actually disconnect the wire at the breaker NOT just turn something off.
It,s also rather unusual to have 3 seperate buildings supplied from the same breaker. You would need a splitter somewhere (or the illegal 3 wires under the same screw on a breaker)
If you are concerned about the integrity of the underground run Disconnect the loads at the first junction box in the barn where the wire comes out of the ground downstream from the breaker Then you will ONLY have the undeground wire connected to the breaker . If it then trips the problem is in the ground. You don,t dig you attach a rope to the wire and pull it out of the conduit. Repair or replace and pull it back in with the rope.

Also be sure to do this disconnecting with the power turned OFF to your breaker panel at it,s supply.
If this basic troubleshooting is this confused perhaps you should call a licensed electrician.

mikehinton 02-13-2013 11:43 AM

I'm obviously not communicating what I'm doing properly.

Right now, the breaker is connected to the sub panel, AND the supply lines that feed the individual buildings. In front of each building is a PVC junction box underground. Connected to the main supply lines at each point is 12/2 direct burial Romex (in PVC conduit) that goes into a metal junction box in each building. From that metal box, additional 12/2 Romex goes to the various outlets and light switches.

At this point, I'm testing to see if any of the "branches" from the metal junction box has a short circuit in it that would trip the breaker. I disconnected one of those last night, but the problem remained. I plan to disconnect each additional "branch" one at a time to see if the problem gets resolved.

If disconnecting each "branch" does not solve the problem, then the only remaining possibility is that the short is in the main supply wires.

One of my initial questions was whether or not there was a way to test for a short circuit in one of the branches without disconnecting them one at a time. It seems that there isn't, but no one had addressed that directly.

Hope that clears up the present situation.