GFCI failure -- mystery...?
So I'm putting in a bathroom, and I installed a single outlet with a GFCI breaker for protection.
All is well for months. I use the outlet while I'm putting in studwalls. The drywall guys use the outlet for their tools. No problems. A few weeks later, after we've painted the rest of the floor, done some plumbing, and a few other things, the outlet is dead. Some research shows that the breaker won't reset. Right. First question: Where's the water? So I trace out the portion of the wire that I can still see (most of it is in the wall now), and it's all good. The outlet seems fine, but just to make sure, I pull it completely out of the circuit. So the next test is: Will the breaker reset with just the wire, no breaker. Answer: No. So I changed out the breaker, and the new breaker worked fine. I shrugged and said, "That's $60 lesson in breaker selection. Odd, but I'm sure it's not unheard of." That was two weeks ago. I've used the outlet half a dozen times since then. I checked it tonight and it was dead. Breaker tripped and won't reset. My thoughts? Maybe it's bad wiring? Or maybe I've installed the breaker wrong? ... That would be strange, because they're not that hard to install. The outlet could be bad? Except that swapping in a different outlet or trying it with no outlet doesn't fix the problem. Wiring? ... Or maybe wiring? (sigh) Never seen this before, and google turned up a lot of results that say "Check for water or something plugged in that's bad." Any thoughts? I'm at wits end here. Thanks, Dan
__________________
'86 911 (RIP March '05) '17 Subaru CrossTrek '99 911 (Adopt an unloved 996 from your local shelter today!) |
||
![]() |
|
Slackerous Maximus
Join Date: Apr 2005
Location: Columbus, OH
Posts: 18,150
|
I feel for you man. The new GFCI outlets are SO freaking sensitive. I had the same thing happen to me . Never did get to the bottom of it because I had electricians redo the whole house.
__________________
2022 Royal Enfield Interceptor. 2012 Harley Davidson Road King 2014 Triumph Bonneville T100. 2014 Cayman S, PDK. Mercedes E350 family truckster. |
||
![]() |
|
Did you get the memo?
Join Date: Mar 2003
Location: Wichita, KS
Posts: 32,111
|
Nicked wire leading to an intermittent short? It's not uncommon to have wires hit by errant drywall screws.
__________________
‘07 Mazda RX8-8 Past: 911T, 911SC, Carrera, 951s, 955, 996s, 987s, 986s, 997s, BMW 5x, C36, C63, XJR, S8, Maserati Coupe, GT500, etc |
||
![]() |
|
Registered
Join Date: Mar 2004
Location: Los Angeles
Posts: 17,295
|
Try a regular outlet for a few weeks and see if that trips the breaker. What did we do 20-30 years ago without them to protect us? I lived through it as a kid, and so did many of us. Yes, the GFIs do just go bad and are just too sensitive. Now they have those goddam lock out things that make it almost impossible to plug anything into it without using all my strength and scratching up all the new outlet with only using it a few times. I hate plugging a tool into a new outlet when the place is done. it always scratch the new outlets when the home owners come home. We jsut run a cord now. its better and cheaper then having to replace it with new.
Oh, you might have a cut wire on the clamp when the electrical guys pull the wire too hard. I don't think its your wires. |
||
![]() |
|
Registered
Join Date: Nov 2003
Location: West of Seattle
Posts: 4,718
|
Quote:
![]() I may try running a normal breaker for a while. Or maybe a normal breaker with a gfci outlet? I don't know, I just really don't feel like re-running wires from a basement breaker panel to a second floor freshly-renovated bathroom. ![]() Any other ideas? Thanks, Dan |
||
![]() |
|
Did you get the memo?
Join Date: Mar 2003
Location: Wichita, KS
Posts: 32,111
|
I would try the regular outlet. You still have the breaker to protect the circuit.
__________________
‘07 Mazda RX8-8 Past: 911T, 911SC, Carrera, 951s, 955, 996s, 987s, 986s, 997s, BMW 5x, C36, C63, XJR, S8, Maserati Coupe, GT500, etc |
||
![]() |
|
![]() |
Registered
Join Date: Jun 2002
Location: Winnipeg, MB, Canada
Posts: 3,963
|
Did you buy both breakers that went bad from the same place? If so, it could be that they got a bad batch of breakers.
Try a normal breaker with a GFI outlet at the end. The GFI outlet would be cheaper.
__________________
Bunch of old cars ![]() |
||
![]() |
|
Registered
|
I have a question, as I'm not sure what's going on.
Do you have a circuit with one plain outlet and a GFCI breaker, or a circuit with a standard breaker and a GFCI outlet? Is this outlet the only one on the circuit?
__________________
. |
||
![]() |
|
Registered
|
Assuming you are referring to a GFCI outlet on a standard breaker I have had the same problem.
Installed a new GFCI outlet for my sump pump, and everytime I would check on it, it would be tripped. Eventually it would not reset just like you describe. Replaced it with another brand and all has been well for about 6 months. Try a different brand. Apparently some products made in China are not up to spec, or so I have heard.
__________________
Randy '87 911 Targa '17 Macan GTS |
||
![]() |
|
Registered
Join Date: Nov 2003
Location: West of Seattle
Posts: 4,718
|
Quote:
That's the baffling part: It's literally just breaker-wire-outlet, with nothing else there to interfere. If it isn't the outlet (I've tried other outlets already), then it's either two bad breakers (possibly the same bad batch from the same Lowe's, purchased several months apart?) or something wrong with the interconnecting wiring. Some other ideas that I'll try tomorrow morning: 1 - Pull the receptacle out of the circuit, remove the breaker, and check for even minute grounds between branches. 2 - Swap this GFCI breaker with another one of the GFCI breakers in the same panel. See if the problem follows the breaker or the circuit. 3 - Try a normal breaker (I do have spare 20A breakers) with a GFCI outlet (I'd have to go buy one). Or just a normal breaker with a normal outlet, for temporary.
__________________
'86 911 (RIP March '05) '17 Subaru CrossTrek '99 911 (Adopt an unloved 996 from your local shelter today!) |
||
![]() |
|
Registered
|
If it rains hard here in Florida and the humidity goes up all our GFI's go off line. I guess they're going their job but it is inconvenient.
|
||
![]() |
|
Registered
|
That would be my next step. Cheap, easy, definitive.
__________________
. |
||
![]() |
|
Registered
|
My first thought was also a short somewhere along the circuit. Or possibly interference from a more powerful circuit it's running near? Dunno what your interior wiring situation looks like...
__________________
Guy '87 944 (first porsche/project car) |
||
![]() |
|
závodník 'X'
|
Never had an issue with a GFCI but wait until your local code requires AFCI (arc fault receptacles).... ridiculous. Recent basement rehab and it was required. Total waste, PITA picky little bastards.
__________________
“When these fine people came to me with an offer to make four movies for them, I immediately said ‘yes’ for one reason and one reason only… Netflix rhymes with ‘wet chicks,'” Sandler said in a prepared statement. “Let the streaming begin!” - Adam Sandler |
||
![]() |
|
Registered
Join Date: Apr 2005
Location: outta here
Posts: 52,927
|
Install a regular breaker and a GFCI outlet? Cheaper?
JR |
||
![]() |
|
Control Group
|
Those things go bad, and are sometimes bad out of the box, in my experience.
__________________
She was the kindest person I ever met |
||
![]() |
|
Registered
Join Date: Mar 2004
Location: Los Angeles
Posts: 17,295
|
After reading through some of the stuff here, I was going to type the same thing.
I always fail to understand why people get so up tight about GFIs, now arc fault ? They are such PITA and sometimes is completely unnecessary. |
||
![]() |
|
Registered
Join Date: Jun 2001
Location: Sweden
Posts: 5,910
|
I also had those experiences, and found out that GFCI was NEVER the fault.
They fill a function and are not "overly sensitive". Here in 230V/50Hz land GFCI is required to trip at 30mA earth current in order to be classed as "personal protection". Choosing the higher current rating will certainly make it less sensitive but also worthless as protection device as more than 30mA through body will likely kill you. It's quite easy to troubleshoot. Break the circuit, remove the breaker and measure leads going FROM GFCI with ohm-meter. Resistance between earth, phase and null should be very high, almost infinite. If resistance in-between any of those leads is less than that, you either have a short (>10 Ohm) or a sneaky-leaker (10 - 100kOhm) due to water, a nail that went through the wire or something like that. First one is easy to fix, sneaky-leaker is dangerous one. Common fault scenario is short between earth and null (or whatever you call it in 110V-istan) in outlet itself. It will not burn the fuse (as earth and null are shorted in the fuse box anyway) but it will trip the GFCI. Next most common scenario is "in between, not-quite the short" (the dangerous one), as it might electrocute you or start to burn without burning out the fuse. And this scenario is the one GFCI is there to protect you from.
__________________
Thank you for your time, Last edited by beepbeep; 03-01-2013 at 01:24 PM.. |
||
![]() |
|
![]() |
Evil Genius
|
GFI's suck.
end of message. But then again, seem pretty robust under testing here. GFCI test - YouTube
__________________
Life is a big ocean to swim in. Wag more, bark less. ![]() |
||
![]() |
|
Registered
Join Date: Mar 2004
Location: Los Angeles
Posts: 17,295
|
Quote:
|
||
![]() |
|
![]() |