Quote:
Originally Posted by Jim Richards
dad, that's only for receptacles. Wiring will need to be at least #12 is the breaker is rated at 20A. So, it's a system...breaker, wiring, and receptacles.
|
That's right. Breakers match branch wire.
You covered that in the first post. The posts on receptacles were unclear, so I clipped the table from the code.