Confused about an NEC standard
All the single breakers in the electrical panel in our new house are 20 amp. ALL of them. This panel is basically a sub-panel, though it is as big as the main (200 amps). It feeds primarily to bedrooms and bathrooms. I'm sure the outlets, ceiling fans, etc are rated for 15 amps. I thought every device on a 20 amp circuit had to be rated for 20 amps, but trying to read the Code it seems to say something along the lines of, "mmmm, not really." It's either ambiguous or so precise I get confused in the verbiage.
So what does the PPOT brain trust have to say about it?
__________________
. |
||
![]() |
|
Bandwidth AbUser
Join Date: Nov 2001
Location: SoCal
Posts: 29,522
|
The breakers should be the amp rating as the wires for each of your circuits. #12 wiring should have 20A breakers, #14 wiring should have 15A breakers, etc. Are all of your circuits fed by this panel lighting or outlets? Are you positive your outlets are 15A? For example, our kitchen and garage have 20A outlets.
__________________
Jim R. |
||
![]() |
|
Registered
Join Date: Mar 2004
Location: Los Angeles
Posts: 17,408
|
They better be, Jim. How's that garage/shop coming along?
WD15, Outlets should be rated 20 amps in your situation. Here's the deal, how often are gouging to draw 20 amps out of one single outlet in that kitchen unless one circuit is feeding lots of outlets and that are all being used at the same time. I see people put those cheap 15amp outlets hooked up to 20 amp outlets all the time only because they are much cheaper and the inspector never checks them |
||
![]() |
|
I see you
Join Date: Nov 2002
Location: NJ
Posts: 29,921
|
Seems to me that if the breaker is rated higher than the device then the circuit isn't really protected. But I'm not an electrician.
__________________
Si non potes inimicum tuum vincere, habeas eum amicum and ride a big blue trike. "'Bipartisan' usually means that a larger-than-usual deception is being carried out." |
||
![]() |
|
Registered
Join Date: Oct 2006
Location: MYR S.C.
Posts: 17,321
|
you can put 15amp outlets on a 20amp circuit, just not the other way around.
i prefer the overprotection,. not an electrician either. just because you have 15amp outlets on a 20amp service does not mean you still cant trip a 20amp brkr. as jim said the breaker protects the WIRES. as gogar said, you protect the smallest ga wire. i ran a dedicated service to my music room for the band. i ran 10g to the first box, then 12g to all outlets and put in a 20a brkr and 20amp outlets. the service split down 2 walls where the 10g tied in.
__________________
86 930 94kmiles [_ ![]() 88 BMW 325is 200K+ SOLD 03 BMW 330CI 220K:: [_ ![]() 01 suburban 330K:: [_ ![]() RACE CAR:: sold Last edited by T77911S; 01-09-2018 at 08:29 AM.. |
||
![]() |
|
Registered
Join Date: Jul 2001
Location: Lawrenceville GA 30045
Posts: 7,379
|
Exactly - the device (switch/outlet) or the wire.
__________________
Mark '83 SC Targa - since 5/5/2001 '06 911 S Aerokit - from 5/2/2016 to 11/14/2018 '11 911 S w/PDK - from 7/2/2021 to ??? |
||
![]() |
|
![]() |
Bandwidth AbUser
Join Date: Nov 2001
Location: SoCal
Posts: 29,522
|
Quote:
My son is selling his house and had the buyer's home inspector point out that his subpanel had a breaker that was too large for the wiring it had connected to it. Sure enough, the wiring was correct for the load it was carrying but the breaker should have had a smaller amperage rating. It had probably been like that since the place was built. ![]()
__________________
Jim R. |
||
![]() |
|
Registered
Join Date: Mar 2004
Location: Los Angeles
Posts: 17,408
|
Easy fix for him. Did he buy another place nearby. That's a great neighborhood
|
||
![]() |
|
Platinum Member
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 21,002
|
It's OK. Common practice.
This is from NEC code: ![]()
__________________
The truth is that while those on the left - particularly the far left - claim to be tolerant and welcoming of diversity, in reality many are quite intolerant of anyone not embracing their radical views. - Charlie Kirk |
||
![]() |
|
Bandwidth AbUser
Join Date: Nov 2001
Location: SoCal
Posts: 29,522
|
dad, that's only for receptacles. Wiring will need to be at least #12 is the breaker is rated at 20A. So, it's a system...breaker, wiring, and receptacles.
__________________
Jim R. |
||
![]() |
|
Registered
|
Thanks for the input. I'm not going to worry about it. The installing electrician's sticker is on the box. I don't think he'd be advertising if he'd screwed the job up this badly. Wire ARE 12 ga. so they are not an issue. I was concerned about overheating a 15 amp receptacle by plugging in multiple devices.
__________________
. |
||
![]() |
|
Platinum Member
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 21,002
|
Quote:
You covered that in the first post. The posts on receptacles were unclear, so I clipped the table from the code.
__________________
The truth is that while those on the left - particularly the far left - claim to be tolerant and welcoming of diversity, in reality many are quite intolerant of anyone not embracing their radical views. - Charlie Kirk |
||
![]() |
|
![]() |
Band.
|
Not really germane, but Just for info, I'm pretty sure that
Any device designed to fit into a 15A receptacle must pull less than 15A. A device designed to pull more than 15A has a perpendicular prong. That's why "20A" receptacles have the combo parallel/perpendicular socket. ![]()
__________________
1983 SC Coupe 1963 BMW R60/2 1972 Triumph Tiger 1995 Triumph Daytona SuperIII |
||
![]() |
|
Registered
Join Date: Jul 2001
Location: Lawrenceville GA 30045
Posts: 7,379
|
Quote:
__________________
Mark '83 SC Targa - since 5/5/2001 '06 911 S Aerokit - from 5/2/2016 to 11/14/2018 '11 911 S w/PDK - from 7/2/2021 to ??? |
||
![]() |
|
Registered
|
Loads only use what they are designed for , 1500 watts divided by 120 volts equals 12.5 amps. On a 15 amp breaker , this is fine. On a 20 amp breaker this is fine. You will not be able to plug into a 30 amp circuit or higher due to plug configuration. As previously stated , the breakers protect the conductors. you can have 12 receptacles to a circuit. you can plug 24 appliances into this circuit but it will throw the breaker instantly when you turn them on, thus protecting the conductors and building they are in. Breakers are rated for 10000 amps symmetrically and work best when the rise of amperage is FAST. Adding more grounds or a heavier ground to a service only slows down the rise of a fault because the fault current has more paths to travel thus limiting the fault current to rise symmetrically. all services are protected by number 6 copper now so in a large fault condition, it burns through and allows the fault current to travel on the neutral back to the distribution cutout or main , depending on where the fault is. On a side note, I have often wondered about the cold flow properties of aluminum when used in cases of porsche motors, but that is another topic entirely. hope this helped.
Dan. Last edited by bickyd; 01-10-2018 at 06:41 AM.. |
||
![]() |
|
Registered
|
Quote:
|
||
![]() |
|
Platinum Member
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 21,002
|
Quote:
"A single receptacle installed on an individual branch circuit must have an ampere rating not less than that of the branch circuit. For example, a single receptacle on a 20- ampere individual branch circuit must be rated at 20 amperes; however, two or more 15-ampere receptacles or duplex receptacles are permitted on a 20-ampere general purpose branch circuit. ....... 15 amp duplex receptacles are rated at 20 amps pass through in the UL listings. And each 1/2 of the duplex is rated at 15 amps. So they can handle a 15 and 5 or 10 and 10 amp loads for example." The standard 15A GFCI receptacles are rated for 20 amp feed thru. It's the plug configuration, not the device. As gogar points out, 2 vertical prongs are 15a plugs. That is why kitchens & dining rooms are 12 gauge, 20 amp breaker, with the common 15a receptacles. It's common to use 14 gauge 15 amp for lighting other general outlets.
__________________
The truth is that while those on the left - particularly the far left - claim to be tolerant and welcoming of diversity, in reality many are quite intolerant of anyone not embracing their radical views. - Charlie Kirk |
||
![]() |
|
Registered
|
dad911 ^^^^ is TOTALLY CORRECT (Elec inspector here btw)
ALso a note regarding home inspectors finding oversized breakers at inspection. Take note of typically they find breakers "oversized to wiresize" on A/C units. The NEC specifically notes exception for wire size vs breaker on these. Go to the name plate of the device for minimum wire size/maximum breaker. |
||
![]() |
|