Help me with my breaker box
OK, the new house I'm renting (and going to buy, which is why I'm doing this myself) has a blown breaker. I know the previous renters, and it blew maybe 3 months ago, they just ignored it.
30 amp breaker in an ancient box which is on the outside (exposed, but in a "rainproof" box) wall of the house, circa late 50s to early 60s. Breaker is blown, I can reset it and it makes a humming sound and trips within a second, over and over again. I know which boxes are on this breaker from experimentation, all are along the outside wall. 2 are GFCI outlets in the kitchen, 3 are normal outlets in the living room, and 2 are outdoor, old fashioned "weatherproof" spring loaded steel door types on the outside brickwork. NOTHING is currently plugged into any of these (new rental). Now, I basically know how to replace the breaker itself. I know how to check an outlet when there's power going to it, but I don't know how to check which of these 7 boxes is the bad one. Safe bet it's one of the outside boxes, but it also could be one of the inside GFCI boxes, which had a microwave and coffee maker and who knows what other kind of temporary but high amp equipment. So, how do I go about this? Go buy a 30 amp breaker, replace it and risk turning it on? Nothing is plugged in right now. Replace the 2 outside outlets wholesale just because there's a good chance they're buggered anyways? Then what? Replace one or both GFCI outlets because they're the most complex thing on the circuit and therefore most likely to be going haywire? Replace everything and hope it's not wires in the wall? Is there any sane method for checking the status of the wires and/or outlets without any power to them? I an presuming that if I just put a new breaker in that it will trip immediately, which makes testing everything else pretty hard. ![]() ![]()
__________________
Mike Bradshaw 1980 911SC sunroof coupe, silver/black Putting the sick back into sycophant! |
||
![]() |
|
Non Compos Mentis
Join Date: May 2001
Location: Off the grid- Almost
Posts: 10,594
|
Bad news.
Federal Pacific breaker panels are no good. Most lenders will not fund a mortgage until a FP panel is replaced. If you get a home inspection, they will definitely insist the box must be changed. |
||
![]() |
|
Registered
|
Open the boxes up, pull out the devices, and look at them.
__________________
. |
||
![]() |
|
Registered
Join Date: Jun 2007
Location: Lake Oswego, OR
Posts: 6,061
|
^^^sorta maybe. Insurance is the key. Mortgage not an issue. I have a crap apartment with them. We did find insurance and the mortgage didn't care.
There are fixes and work arounds. Dantilla is right though. You need to figure out which solution is acceptable before you move forward. We were given a $25k bid to redo to boxes for 12 units. Ugg. |
||
![]() |
|
Platinum Member
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 20,956
|
Quote:
Quote:
I suspect more is going on. Landlord should fix. Edit: Is it possible/have you checked for Aluminum wires?
__________________
The truth is that while those on the left - particularly the far left - claim to be tolerant and welcoming of diversity, in reality many are quite intolerant of anyone not embracing their radical views. - Charlie Kirk Last edited by dad911; 07-17-2019 at 04:26 AM.. |
||
![]() |
|
Non Compos Mentis
Join Date: May 2001
Location: Off the grid- Almost
Posts: 10,594
|
Makes sense. A friend is a building inspector. Says if he reports an FP breaker panel, it usually halts a sale until resolved.
Also- Pull an outlet or light fixture or two and see if the wire is copper or aluminum. If copper, replace the Federal Pacific breaker panel and live happily ever after. If aluminum, I would definitely NOT buy the house, unless the budget is large enough to re-wire the entire place. I looked at a fixer-upper a few years ago. Had a brand new Square D panel, with neat, tidy wiring at the breakers. Noticed most of the home runs went into a large J box several feet away. Pulled the cover and found a rats nest of new copper romex coming from the breakers wire nutted to aluminum wire that ran through the house. Yikes! Dodged bullet on that one. |
||
![]() |
|
![]() |
Brew Master
|
IF as you mention there's nothing plugged in, the breaker is bad. It happens. I'd kill the power and check all outlets and lights to make sure you don't have an issue in the circuit.
As dad911 points out, I'd be a bit concerned that there's a 30 amp breaker on a circuit that would typically be 20 amp.
__________________
Nick |
||
![]() |
|
Non Compos Mentis
Join Date: May 2001
Location: Off the grid- Almost
Posts: 10,594
|
Looks like dad911 beat me to it about the possibility of aluminum.
|
||
![]() |
|
Registered
Join Date: Jun 2007
Location: Lake Oswego, OR
Posts: 6,061
|
^^^aluminum wire can be used. There are special wire nuts for aluminum to copper. I forget if it is expansion or corrosion st is the problem. This is an easy thing to fix. I had it done for a client. Full insurance company buy in. Also, there are three fixes or so. Make sure you do the one your carrier approves!!!
|
||
![]() |
|
Registered
Join Date: Apr 2008
Location: Houston TX
Posts: 8,704
|
Ugh.
Well, the house was opened up to the studs after Hurricane Harvey, it's *possible* that someone at some point would have examined it for aluminum wires at that time, but I cannot be sure. The inspector is a friend of ours, as is the mortgage broker, and we have a good relationship with the owner (we've been renting the second house on the property for 9 years) and his realtor (who is his rental manager, so we've meet him several times). Maybe we'll all just make this go away... ![]() I'll have to put some time in this weekend. I plan on tossing a new breaker in one way or the other, I'll examine for aluminum wire. The house has very little value compared to the land, so it probably does not deserve a rewire if needed. Can I ask how one knows that it should be 20 instead of 30 amps, since it has as many as 6 boxes/12 outlets connected to it? Seems like it should be bigger than 30 amps for that, but I'm thinking in common sense guy think, not residential code think.
__________________
Mike Bradshaw 1980 911SC sunroof coupe, silver/black Putting the sick back into sycophant! |
||
![]() |
|
Non Compos Mentis
Join Date: May 2001
Location: Off the grid- Almost
Posts: 10,594
|
The circuit breaker is to protect the wire from overheating. Unless the wire to every outlet is heavy enough to handle 30 amps (extremely doubtful) a 30 amp breaker will not trip when the smaller wires overheat.
|
||
![]() |
|
Registered
Join Date: Apr 2008
Location: Houston TX
Posts: 8,704
|
Quote:
I understand what you're saying, and I'll downsize the breaker to 20amp, but it just means that *I* need to be aware of the limitations of that particular circuit from now on, right? Hell, I used to run the electric lawnmower on that circuit, now I know that if I do that, I can't have the microwave on at the same time, or the livingroom A/V system running. I probably did damage to it by mowing the damned lawn...
__________________
Mike Bradshaw 1980 911SC sunroof coupe, silver/black Putting the sick back into sycophant! |
||
![]() |
|
UnRegistered User
|
Quote:
Your example is exactly why all conductors/plugs etc need to be rated for the amperage of the breaker. Overheating/burning = Unhappy Homeowner. I would second the opinion of the Federal Pacific panel should go away. Not that big of a job if the circuits within the home are OK.
__________________
Bill K. "I started out with nothin and I still got most of it left...." 83 911 SC Guards Red (now gone) And I sold a bunch of parts I hadn't installed yet. |
||
![]() |
|
Band.
|
I'm with WD,
I'd probably pull the outlet covers off and just see that nothing is touching the wrong stuff, especially if you have metal boxes. I'd probably start with the outdoors ones, same as you. You'll be able to find out what kind of wiring you have when you do it.
__________________
1983 SC Coupe 1963 BMW R60/2 1972 Triumph Tiger 1995 Triumph Daytona SuperIII |
||
![]() |
|
Platinum Member
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 20,956
|
Quote:
Quote:
You also have 2 double pole 40s, and a double pole 30. I assume they are for cooking, AC, and water heater. If not, perhaps some more investigation is in order.
__________________
The truth is that while those on the left - particularly the far left - claim to be tolerant and welcoming of diversity, in reality many are quite intolerant of anyone not embracing their radical views. - Charlie Kirk |
||
![]() |
|
Registered
Join Date: Dec 1969
Location: chula vista ca usa
Posts: 5,697
|
When we had solar installed several years ago we needed a new and "modern" breaker box installed as ours (like yours) was installed when the house was made in 1960. I had labeled all the original breakers many years ago and did it by plugging in a lamp to every outlet in the house. I would open a breaker and my wife would call down to tell me what light went out. I know that is not a very technical method, but it worked well. The price for the breaker swap was $3,000 if I remember correctly and took a couple hours since the hole in the garage wall had to be cut larger. If it were me, I would replace the whole box so any chance of an electrical fire is eliminated.
|
||
![]() |
|
Registered
Join Date: Jan 2002
Location: Long Beach CA, the sewer by the sea.
Posts: 37,700
|
Let's start with the basics. A hum and an subsequent trip suggests first and foremost a direct short. This is not likely in one of the GFIC receptacles.
What I want to know is why there are so many 30 A breakers in there. Checking wire size as mentioned by others is paramount. And me thinks at least 2 of those 30A should be tied as evidenced by the hole that spans nos. 6 & 7. Get a real electrician out there. Seriously. |
||
![]() |
|
Registered
Join Date: Sep 2009
Location: North of You
Posts: 9,160
|
Find the bad breaker, remove it and trace the wires. Black should not be grounded.
https://www.amazon.com/Amprobe-BT-120-Circuit-Breaker-Tracer/dp/B005G7SC0M/ref=sr_1_1_sspa?crid=22HCUAD2N6I6U&keywords=wire+tracer+%26+circuit+tester&qid=1563376201&s=gateway&sprefix=wire+tracer%2Caps%2C167&sr=8-1-spons&psc=1
__________________
"A machine you build yourself is a vote for a different way of life. There are things you have to earn with your hands." Last edited by 1990C4S; 07-17-2019 at 07:10 AM.. |
||
![]() |
|
![]() |
Registered
Join Date: Apr 2008
Location: Houston TX
Posts: 8,704
|
I talked with my inspector, and he agreed that the box needs to go before he bothers with anything else.
So, looks like I'll be bugging the landlord to fix all of this before the inspection. Too bad for him!
__________________
Mike Bradshaw 1980 911SC sunroof coupe, silver/black Putting the sick back into sycophant! |
||
![]() |
|
canna change law physics
|
Quote:
I know several electricians that can replace the electrical panel with a modern one. If you are inside City Limits, it will take an electrical permit
__________________
James The pessimist complains about the wind; the optimist expects it to change; the engineer adjusts the sails.- William Arthur Ward (1921-1994) Red-beard for President, 2020 Last edited by red-beard; 07-17-2019 at 09:54 AM.. |
||
![]() |
|